Yes, 240v unitThat seems appropriate based on the ones I've installed and the chart. I assume it's a 240v setup, I guess you could think about going to 10/2 and a 25amp breaker if it's a 120v setup or if you want it to be a little safer. Make sure and install a surge protector at the outside disconnect, the control boards are really sensitive to spikes and will die fast without one.
Despite searching earlier before starting a new thread, I didn't find this until now:For an 18k, i'd do 12/2 and a 20a without another thought.
My cheap 2.5 ton heat pumps are on a 25...no really a wildly efficient 18k mini should need that
That dude is a weirdo. I wouldn't listen to himDespite searching earlier before starting a new thread, I didn't find this until now:
25A breaker with 12/2 NM-B
I think I know the answer already, but asking anyway. House was built in 2003, a/c systems are all original. I had previously noticed that my 1st and 2nd floor a/c systems (identical systems) used 10/2 nm-b and 25 a breakers. It caught my eye as it wasn't a 30a breaker but smaller is ok In...www.garagejournal.com
Unless stated otherwise either fuse or breaker is fine.
Certainly wouldn't surprise me, personally I would just use a fused disconnect anyway.I've got a funny feeling once the unit shows up it's going to say "max fuse 25A" on the unit.
Annoying that the manual and the unit don't match.
The interesting thing is to look at the LRA for the unit, I know on my 12k units the LRA for 240 is something like 8 amps. So why are they specifying such a large wiring/breaker size if the unit can't ever call for or cause more without damage?I couldn't sort out all the information back when I did my first minisplit install. When all was ready and I still did not have a breaker, i put in a 15 amp that I had and it started running OK so I continued to shop for the correct breaker, I think i was shopping for "mythical" 25A but bought a 20 amp just to have something. That was over 5 years ago. The unit has run 24/7 with the 15A breaker through heating and cooling seasons in KY and the 15A breaker has never thrown so it is still there.
A1: Different time curves between fuse and cb. Without spec'ing a fuse style, multiple fuses would fit the amapacity requirement but can vary drastically for the time curve. Any further details on the fuse requirement?Well physical unit arrived and, surprise, is marked differently then the manual online.
Question 1: other then code, what is the purpose of a fuse instead of breaker? Seems to be a lot of thought online this is an unintentional discrepancy with the manual
- new manual calls for 15.5A MCA, MOP 25A
- My plan is still 12/2 on a 25A breaker
- unit is marked Max Fuse 25A
Question 2: is there a minimum height for the exterior disconnect? I'd like to exit the basement in a joist bay, which leaves the disconnect lower then I'd normally mount one. Other option (I see) is a interior junction box, thwn and an LB/conduit up the exterior, which is less then desirable.