600SL
Well-known member
Hello Gentlemen
I have two questions regarding SEOOW and SJOOW wire. The application is for a garage lift so the cable will never see the garage floor, as it will be on a twist lock plug on the ceiling.
My first question is that every wire I have ever seen in use is rated at 600V, including 14ga romex to my Plasma cutter with 8/3 using SEOOW cable on a 240V circuit. Therefore is 300V SJOOW acceptable for this application and why is 600V insulation used every where.
Second question, I see that multiple suppliers list the 10/3 SEOOW and SJOOW as good for 30 amps but the 10/4 is only good for 25A. I want to put a convenience 120V receptacle on my lift so the 4 conductor is required. I was hoping to put these on 30A circuits with a 25A/20A CB on the lift itself. Will I need to go to 8/4 to do this? I was wondering if the 25A rating was maybe based on 3 phase which this is not.
I have two questions regarding SEOOW and SJOOW wire. The application is for a garage lift so the cable will never see the garage floor, as it will be on a twist lock plug on the ceiling.
My first question is that every wire I have ever seen in use is rated at 600V, including 14ga romex to my Plasma cutter with 8/3 using SEOOW cable on a 240V circuit. Therefore is 300V SJOOW acceptable for this application and why is 600V insulation used every where.
Second question, I see that multiple suppliers list the 10/3 SEOOW and SJOOW as good for 30 amps but the 10/4 is only good for 25A. I want to put a convenience 120V receptacle on my lift so the 4 conductor is required. I was hoping to put these on 30A circuits with a 25A/20A CB on the lift itself. Will I need to go to 8/4 to do this? I was wondering if the 25A rating was maybe based on 3 phase which this is not.