follow up on my last thread a few weeks ago...
Last year I had HVAC company put in (two) 3tn Trane XR16's and matched TEM6 air handlers. Fast forward a year later, and both units seem to be underperforming. I want to try and see if anybody could look at these pressures and tell me if anything seems off?
Delta T measured at plenum -- 12-14F, never any higher. Outside dry bulb 105F at condenser. Inside is 78F at return, 66F supply.
Our downstairs struggles during the day to get below 77F. I asked it to drop from 79 to 76 4hrs ago and it hasnt got any lower than 78F. Somethings not right. The only strange thing is that BOTH units have poor Delta T...
I have a photo of it outputting 20F delta T a year ago, so it did perform when new.
Any signs here that point to anything?


Last year I had HVAC company put in (two) 3tn Trane XR16's and matched TEM6 air handlers. Fast forward a year later, and both units seem to be underperforming. I want to try and see if anybody could look at these pressures and tell me if anything seems off?
Delta T measured at plenum -- 12-14F, never any higher. Outside dry bulb 105F at condenser. Inside is 78F at return, 66F supply.
Our downstairs struggles during the day to get below 77F. I asked it to drop from 79 to 76 4hrs ago and it hasnt got any lower than 78F. Somethings not right. The only strange thing is that BOTH units have poor Delta T...
I have a photo of it outputting 20F delta T a year ago, so it did perform when new.
Any signs here that point to anything?