Liquidtight or Cantex flexible conduit for attic and crawlspace run?

toddt429

Well-known member
Joined
Jan 19, 2024
Messages
90
I need to run 6ga (4wires) thhn from main up to attic and across then down and into a crawlspace then out to a disconnect. I know pvc would probably be a little cheaper, but is it acceptable to use liquidtight or cantex non metalic flexible conduit for the entire run? if so, am I going to kick myself when it comes time to try and fish the wires through it. I will have 4 45 degree bends. According to the conduit fill chart, 3/4" will suffice, but would it be worth it for me to run the 1 inch for ease of getting the wires through? I have to do 4 seperate runs as I will be using 1 spool of wire instead of 4 individual spools. If anyone can offer advice and opinions, I would very much appreciate it. thanks in advance.
todd
 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
8,028
Location
Central Iowa
It's gonna be tough it's as far of a run as it sounds. And, going on the assumption that this is going to be a four wire 120/240 circuit, the neutral is supposed to be white or gray (marking tape isn't code compliant until the size gets to #4), I don't care, I've taped plenty of 8's and 6's, but you're going to get it inspected, the inspector might and the ground wire can be a #10 but it will have to be green.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
I need to run 6ga (4wires) thhn from main up to attic and across then down and into a crawlspace then out to a disconnect. I know pvc would probably be a little cheaper, but is it acceptable to use liquidtight or cantex non metalic flexible conduit for the entire run? if so, am I going to kick myself when it comes time to try and fish the wires through it. I will have 4 45 degree bends. According to the conduit fill chart, 3/4" will suffice, but would it be worth it for me to run the 1 inch for ease of getting the wires through? I have to do 4 seperate runs as I will be using 1 spool of wire instead of 4 individual spools. If anyone can offer advice and opinions, I would very much appreciate it. thanks in advance.
todd
If there is a neutral & grounding conductor in that mix, it will not be code compliant, as phase tape, or paint is not allowed for 6 AWG & smaller neutral & grounding conductors, the insulation must be white or green. Then there is the issue of grounding conductor size, pulling wire in NM liquidtight will be a *****.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,580
Location
VT
4 pulls through flexible conduit?

No thanks.

You didn't say distance, but even pulling all 4 at once is going to ****.

Can you run SEU?
 
OP
T

toddt429

Well-known member
Joined
Jan 19, 2024
Messages
90
It's gonna be tough it's as far of a run as it sounds. And, going on the assumption that this is going to be a four wire 120/240 circuit, the neutral is supposed to be white or gray (marking tape isn't code compliant until the size gets to #4), I don't care, I've taped plenty of 8's and 6's, but you're going to get it inspected, the inspector might and the ground wire can be a #10 but it will have to be green.
Thank you. I had a feeling it was more trouble than it's worth. I appreciate you addressing the non compliance issue as well. I had no Idea that that marking tape wasn't compliant. I've done it before as well, but due to the complexity of this job, I will be pulling permits. I'd rather not embarrass myself to an inspector. Your response was really helpfull and I appreciate it. Thanks.
Todd
 
OP
T

toddt429

Well-known member
Joined
Jan 19, 2024
Messages
90
If there is a neutral & grounding conductor in that mix, it will not be code compliant, as phase tape, or paint is not allowed for 6 AWG & smaller neutral & grounding conductors, the insulation must be white or green. Then there is the issue of grounding conductor size, pulling wire in NM liquidtight will be a *****.
Yup. Thank you for catching that for me, I was unaware.
 
OP
T

toddt429

Well-known member
Joined
Jan 19, 2024
Messages
90
No, I can't use service wire going into the disconnect and I want it to be a home run to the disconnect with no junction or transition. Thank you for helping me make up my mind. I'll stick with pvc conduit.
 
To avoid these ads, REGISTER NOW!
OP
T

toddt429

Well-known member
Joined
Jan 19, 2024
Messages
90
I need to run 6ga (4wires) thhn from main up to attic and across then down and into a crawlspace then out to a disconnect. I know pvc would probably be a little cheaper, but is it acceptable to use liquidtight or cantex non metalic flexible conduit for the entire run? if so, am I going to kick myself when it comes time to try and fish the wires through it. I will have 4 45 degree bends. According to the conduit fill chart, 3/4" will suffice, but would it be worth it for me to run the 1 inch for ease of getting the wires through? I have to do 4 seperate runs as I will be using 1 spool of wire instead of 4 individual spools. If anyone can offer advice and opinions, I would very much appreciate it. thanks in advance.
todd
Thank You all for the help and catching the non compliance issue.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,066
Location
NJ
So why is it that you can't run SEC?

IF SEC is exposed to damage at the disconnect, then sleave it in conduit at that location only.
 
OP
T

toddt429

Well-known member
Joined
Jan 19, 2024
Messages
90
So why is it that you can't run SEC?

IF SEC is exposed to damage at the disconnect, then sleave it in conduit at that location only.
The way I interpreted article 680, it has to be thwn in conduit and I've been reading the histories on other forums and seems that is the common answer. I suppose you now know what the disconnect is for lol. I was reluctant to disclose that.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I'm don't know why SER won't work in your case? What section of 680 are you referring to? Look at 680-25 Feeders (A) (1) Exception for approved cable assembly with insulated equipment ground.
 
Last edited:
OP
T

toddt429

Well-known member
Joined
Jan 19, 2024
Messages
90
I'm don't know why SER won't work in your case? What section of 680 are you referring to? Look at 680-25 Feeders (A) (1) Exception for approved cable assembly with insulated equipment ground.
 
OP
T

toddt429

Well-known member
Joined
Jan 19, 2024
Messages
90
I am having a hard time seeing why I can't use it now that I read through it. I think I'm going to stop into the inspectors office and ask exactly what they expect and prefer. I also have to run a dedicated 110 convenience outlet out there. In which case, the conduit would probably be easier. It is a 70+ foot run up into attic and across then down I to crawlspace. Thank you for poi ting this out. I won't rule it out just yet.
 