Oil Line Between Tank and Boiler Question

Beemer

Well-known member
Joined
Jun 21, 2020
Messages
1,424
Location
Northeast
In the 40 year life of our house we have had to have the copper oil line blown out twice when the boiler wouldn't fire for that reason.
It is less than convenient because it happens in the dead of winter.

My question is can the line be replaced with a larger diameter or do the boiler pumps have a specific size required?
 
To avoid these ads, REGISTER NOW!
OP
B

Beemer

Well-known member
Joined
Jun 21, 2020
Messages
1,424
Location
Northeast
If you're getting sludge clogging the line, a bigger line isn't the solution.
The line is over 40 years is so I can imagine very slow buildup.
When the filter is changed annually there is not much in there to be alarming; definitely slight black on the filter but no globs. Since the first occurrence (perhaps 20 years ago) I started using conditioner every time the delivery comes but the second clog came some time later.
when the line was blown out the second time it didn't look like much other than clean oil.
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
11,014
Location
Rhode Island
I would probably switch to finer filtration at the tank before going through the hassle of trying to upgrade oil line to a larger size. Typical Northeast oil burner supply pipes are already a pretty decent size. I rarely seem or hear of them clogging.

Are you sure it's not just your pump getting weak?
 
OP
B

Beemer

Well-known member
Joined
Jun 21, 2020
Messages
1,424
Location
Northeast
I would probably switch to finer filtration at the tank before going through the hassle of trying to upgrade oil line to a larger size. Typical Northeast oil burner supply pipes are already a pretty decent size. I rarely seem or hear of them clogging.

Are you sure it's not just your pump getting weak?
What is the standard copper line size expected to be seen?

The repairman tested the pump the last time the problem occurred before we blew out the line. I can't saw what the pump condition might be now but it seems to be working.
 
OP
B

Beemer

Well-known member
Joined
Jun 21, 2020
Messages
1,424
Location
Northeast
I have seen where the filter looked like someone put a whole tube of grease in it. Never saw a line plugged up.
Very little settled material in the filter can. The element is changed atleast yearly.
 
OP
B

Beemer

Well-known member
Joined
Jun 21, 2020
Messages
1,424
Location
Northeast
Indoor or outdoor?
Everything inside below ground level where the temperature is pretty stable 60 to 75 degrees. Generally 60 except i winter when the heat runs. Boiler runs all year to maintain hot water storage tank.
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,414
Location
N CA
I’m assuming you have relationship with your oil company and that they are the ones doing the filter change and tune-ups, correct? I also assume you are hearing from the tech on the job. In your position I think I’d stop by the oil company office and have a chat with the Service Manager.What are your options and what are your risks. You do have a 40 yrs old steel tank. Maybe its fine, maybe not. At the least I would replace the line.
 
To avoid these ads, REGISTER NOW!

pcmeiners

Well-known member
Joined
Aug 13, 2009
Messages
7,957
Location
In the only town in Pennsylvania, Bloomsburg.
A new line will do nothing. 3/8" copper could feed multiple oil burners. If you have clogs get a better filter. You could also have the tank cleaned but it will cost you...better off with a new filter. Parents had oil for 60 years, had multiple stoppages was always due to clogging of the oil nozzle or clogging of the filter. Lastly a larger pipe/tub size will cause a lower velocity in the pipe, great for very fine sludge build up.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,453
Location
VT
A new line will do nothing.

Really?

If the line has closed off from sludge twice already, how are they supposed to clean the crud out?

Yes, the filter appears to have issues. But fixing that and expecting an ancient plugged, dented etc like to suddenly work perfectly is unrealistic.

Additionally, depending where the OP lives uncoated lines may no longer be allowed. Around here the oil Co has to check the tank and lines every 3 years, and it now has to be plastic coated.
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,992
Location
Peace Valley,mo
Blowing out either line doesn't make sense. Single stage pump 5-10" of vacuum, 2 stage 10-15" vacuum. Discharge of pump set between 100 - 160 psi. Working pressure of 3/8" tubing is 485 psi. Once I'll call it a mistake twice. Never seen enough dirt to pass by a tank filter and where is it coming from. Rarely have seen a nozzle sinter bronze filter with just a little dirt on them. Failed line at the break looks swollen and split?
 
OP
B

Beemer

Well-known member
Joined
Jun 21, 2020
Messages
1,424
Location
Northeast
Blowing out either line doesn't make sense. Single stage pump 5-10" of vacuum, 2 stage 10-15" vacuum. Discharge of pump set between 100 - 160 psi. Working pressure of 3/8" tubing is 485 psi. Once I'll call it a mistake twice. Never seen enough dirt to pass by a tank filter and where is it coming from. Rarely have seen a nozzle sinter bronze filter with just a little dirt on them. Failed line at the break looks swollen and split?
Not visible. It's mostly covered with cement coating, presumably for protection.
 
OP
B

Beemer

Well-known member
Joined
Jun 21, 2020
Messages
1,424
Location
Northeast
Really?

If the line has closed off from sludge twice already, how are they supposed to clean the crud out?

Yes, the filter appears to have issues. But fixing that and expecting an ancient plugged, dented etc like to suddenly work perfectly is unrealistic.

Additionally, depending where the OP lives uncoated lines may no longer be allowed. Around here the oil Co has to check the tank and lines every 3 years, and it now has to be plastic coated.
Sounds like oil companies did some lobbying up there.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,453
Location
VT
Sounds like oil companies did some lobbying up there.
Doubtful.

It's an environmental thing. I think a licensed plumber, boiler tech etc. Needs to sign off and the oil Co has to verify inspection prior to filling.

Thankfully I burn wood with propane as the "primary" (backup) heat.
 

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,745
Location
AK
I’m assuming you have relationship with your oil company and that they are the ones doing the filter change and tune-ups, correct? I also assume you are hearing from the tech on the job. In your position I think I’d stop by the oil company office and have a chat with the Service Manager.What are your options and what are your risks. You do have a 40 yrs old steel tank. Maybe its fine, maybe not. At the least I would replace the line.
My folks had to replace theirs simply due to age. Insurance mandated it.
 

ratdoggy

Well-known member
Joined
Mar 27, 2009
Messages
11,977
Location
Akron-Canton area OH
I had to blow out the line once in 15 years. If the tank is level the crud will get into the line. My tank was tilted away from the line so any crud would be downhill of the line. Also, I never ran the heat right after a fill-up
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,453
Location
VT
They got by cheap!
It was a conservative guess.

I remember seeing one from a foreclosure rehab years ago where they hauled the tank off on on a lowboy. Never did find out if it was an old dairy or fuel tank. Either way just digging the massive hole and fill wasn't cheap, I'm sure the petroleum testing and possible disposal pushes it waaaaay up.
 
OP
B

Beemer

Well-known member
Joined
Jun 21, 2020
Messages
1,424
Location
Northeast
I had a friend who bought a large historic factory building for a dollar. The catch was that he and the original owner (truly original) shared the cost of ground cleanup.
 

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,948
Location
New England
typical delemma in our area. oil tanks grow sludge animals in the bottom. If you run the tank out or low they get sucked up. Also if the tank is low and you get if filled they will be swirled around. Short term change to a spin on oil filter like this.
Readily availble replacements at home depot. If you have ever changed your car oil you can do this 2x a season while in use. When i switched to this and changed them i never had to have them here to blow out the line again.
A few years ago i changed that metal tank out for the plastic square ones, an overhead line, and a tiger loop. Not one supply problem since.
 

locomotiveman

Member
Joined
Feb 11, 2025
Messages
20
In the 40 year life of our house we have had to have the copper oil line blown out twice when the boiler wouldn't fire for that reason.
It is less than convenient because it happens in the dead of winter.

My question is can the line be replaced with a larger diameter or do the boiler pumps have a specific size required?
Both of my oil-fired Boilers needed cleaning between the line and the nozzle orifice. Same goes for Steam Locomotives.. ask me how I know. 🔥
 