Receptacle/Outlet Needed-Can't find at HD...

Model A Fan

Well-known member
Joined
Dec 1, 2011
Messages
1,223
Location
NW Washington
I have an plug I need to find for my welder. I couldn't find a corresponding outlet at Home Depot, so I may need to order online. What type/name do you call this one?

Furthermore, the welder runs off 110/220 using different plugs. The Amp draw on 220v is 23.5A do I use a 20A dual pole breaker or a 30A? I have both types, and I've got 12AWG (12/2) and 10AWG (10/2) Romex. The entire run will be under 15' in length.

Thank you!20250504_153530.jpg20250504_153512.jpg20250504_153516.jpg
 
To avoid these ads, REGISTER NOW!

LellowBabloon

New member
Joined
Apr 20, 2023
Messages
3
I believe a NEMA 6-50R receptacle will fit that, which is available at Home Depot. It is a 50 amp receptacle but you will have 10/2 romex wire run to it and have it attached to a 2 pole 30 amp breaker. Because you are protecting the wire with the properly sized breaker the receptacle being 50 amp doesn't matter because you'll never be able to draw more than 30 amps through it. I am not sure why Miller has it stamped for 20 amps, but that's a question for them.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,899
Location
Richmond, VA
Welder circuits can use lighter gauge wiring based on duty cycle. I believe at 30%, you can use #12 with a 50a breaker and a 6-50R. #10 is absolutely fine to use though, also with a 50a breaker.

30a breaker would work as well
 
OP
M

Model A Fan

Well-known member
Joined
Dec 1, 2011
Messages
1,223
Location
NW Washington
I believe a NEMA 6-50R receptacle will fit that, which is available at Home Depot. It is a 50 amp receptacle but you will have 10/2 romex wire run to it and have it attached to a 2 pole 30 amp breaker. Because you are protecting the wire with the properly sized breaker the receptacle being 50 amp doesn't matter because you'll never be able to draw more than 30 amps through it. I am not sure why Miller has it stamped for 20 amps, but that's a question for them.

Thank you, I was looking for one specifically for 20-30A and not something big like a washer/dryer/stove would use.

Based on the Amp designation on the front, I'll do 30A dual pole and 10/2 for wire.

Welder circuits can use lighter gauge wiring based on duty cycle. I believe at 30%, you can use #12 with a 50a breaker and a 6-50R. #10 is absolutely fine to use though, also with a 50a breaker.

30a breaker would work as well

I'll stick with a 30A 220v breaker and 10/2. I use it so seldomly that I'll never exceed the duty cycle.

Try the manual...

Ice had the welder for...7(?) years and it may have gone MIA when I moved.


Search for 6-50R

Will do, again that you guys foe the excellent assistance.

HD should have it but I'm not sure which store you looked at.Screenshot_20250507_223809_Home Depot.jpgScreenshot_20250507_223800_Home Depot.jpg

My problem may have been not knowing what type/shape to look for and the store electrical section being rather picked over...this was in Bellingham.

Thank you to everyone who helped me with the info, I appreciate it.
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,051
Location
NJ
I believe that’s the output of the welder, not how much power it draws. There should be a data plate where the cord goes into the box, look for “input” on the label. Or read the manual.
No. It's max input to provide a max output of 150A to the work piece.
 

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,328
Location
Alexandria, VA
I have a dual voltage Lincoln 211 MIG welder and IIRC it only requires a 20 amp breaker and 12 gauge wire if you run it on 240. When I run it on 240 volts I have it plugged into a 6-50R receptacle with a 50 amp breaker, so I'm way over the minimum requirement.
 
OP
M

Model A Fan

Well-known member
Joined
Dec 1, 2011
Messages
1,223
Location
NW Washington
Well, I'll stop overthinking this and run 10-2, connect it to a 30A breaker and call it a day. Thank you for the help. Turns out in the few years I've been hoarding electrical stuff for projects, I picked up the proper receptacle somewhere along the way, quite serendipitous. :D
 