I installed a 100 amp sub panel in my shop (steel building on a concrete slab) that is fed by copper 6 AWG UF from a 60 amp 2 pole breaker in my main panel that is attached to my house.
I mounted the subpanel in the detached steel building to a 3/4" x 4' x 4' plywood board, and screwed the plywood to the steel frame of the building, so the subpanel is not bonded to the steel building at this time. I installed a separate bus bar in the panel for the grounding so that the ground was not bonded to the nuetral in the sub panel. I then hammered an 8' ground rod immediately adjacent to the building and sub panel, and ran a 6 AWG copper cable from a the ground bus bar in the subpanel to the grounding rod.
The steel structure is not attached to the installed grounding rod, and not bonded with the sub panel.
My questions are these:
Since the sub panel has a dedicated 6 AWG cable running from the subpanel to the immediately adjacent grounding rod, can I just run a bonding cable from the steel frame of the building to the sub panel, or do I need to also install a separate cable that runs from the steel frame directly to the grounding rod? Should I do both?
I mounted the subpanel in the detached steel building to a 3/4" x 4' x 4' plywood board, and screwed the plywood to the steel frame of the building, so the subpanel is not bonded to the steel building at this time. I installed a separate bus bar in the panel for the grounding so that the ground was not bonded to the nuetral in the sub panel. I then hammered an 8' ground rod immediately adjacent to the building and sub panel, and ran a 6 AWG copper cable from a the ground bus bar in the subpanel to the grounding rod.
The steel structure is not attached to the installed grounding rod, and not bonded with the sub panel.
My questions are these:
Since the sub panel has a dedicated 6 AWG cable running from the subpanel to the immediately adjacent grounding rod, can I just run a bonding cable from the steel frame of the building to the sub panel, or do I need to also install a separate cable that runs from the steel frame directly to the grounding rod? Should I do both?