I too am failing to see any conductors that would be for ground rods.Is there a metermain or meter and seperate disconnect outside?
Where do the ground rods get connected in?
There are a few things that could potentially be wrong depending on how the panel is fed. Looking at that mess, I wouldn't be referring to the installer as an electrician even if he has a license.Stand alone bldg. There are 2 grounding rods. The inspector and my electrician indicated the bonding was acceptable, this was before power was pulled. I will be contacting my electrician in the morning. Just trying to get some education prior. This is power from electric company service, not from house.
Agreed. Need the full installation details b/c it is either wrong or incomplete.There are a few things that could potentially be wrong depending on how the panel is fed. Looking at that mess, I wouldn't be referring to the installer as an electrician even if he has a license.
Yes, but it's a Siemens & you can't see it in the photo.Doesn't that 100A breaker need a hold down?
You failed to answer if you have an external disconnect switch or breaker at the meter. We need to know that to answer correctly.I had questioned early on about the neutrals and grounds on same bus bar, but the electrician and inspector said this was acceptable
Nope its Eaton BR, your favorite brand.Yes, but it's a Siemens & you can't see it in the photo.

I think you are right, my bad. I've never used BR and didn't realize their main wasn't separateThat is a BR series 20 circuit main breaker panel. Unless I'm missing something.
The lugs on the breaker will always be "hot" (unless the meter is pulled, which requires safety gear/steps/knowledge) so this keeps someone from inadvertently removing the "hot" breaker.What is the purpose of the hold down?
Ah, that's what that black plastic piece is for in the pic I posted with the screw!
Or it getting dislodged from the buss stabs b/c of tension on the conductors.The lugs on the breaker will always be "hot" (unless the meter is pulled, which requires safety gear/steps/knowledge) so this keeps someone from inadvertently removing the "hot" breaker.
then the bare ground wire needs to be removed from the neutral bus on each end as you are creating a parallel pathway.No external dis-connect. Will get photos later this evening or tomorrow, had to go to work. It is Eaton breakers. What is this hold down thing? There was a silver bracket I had to remove from the 100a to turn it on, safety bracket I assume.
It's possible you are picking up capacitively coupled voltage on the "off" conductor. This is common with DMMs due to the high input impedance. There are DMMs that have a LoZ setting to squash this reading. A solenoid tester is another option. Gardner Bender makes this one. Wiggins (now Ideal) is an industry standard but priced higher. A test lamp can also be used.One other issue I noted this morning, I was checking 2 3-way switches with my Fluke voltmeter at the light box. When switched to OFF I get 40Vac, ON I get 120Vac.

It's a very common multi-wire branch circuit (mwbc). Nothing wrong with it. The voltage measured on that neutral at the same point with both cb's on could be the same, lower or higher depending on the current flowing through it.re 40VAC, are any neutrals shared where a neutral could be backfeeding voltage. I have one circuit in this house that was designed that way back in 1979. Essentially in my situation, two circuits each have dedicated hots but share a neutral. When one circuit is off, the resistance back to the box on the neutral causes it to be above ground at a distance from the box. To kill that I have to turn off both breakers. I am told it was common back then. Someday maybe I will have my electrician run a dedicated neutral to the far circuit and separate the two.
Would you just cut it back at the entry point?then the bare ground wire needs to be removed from the neutral bus on each end as you are creating a parallel pathway.
You are right, it's a Zinsco II.Nope its Eaton BR, your favorite brand.
Hold down screw is missing