looking for a 3 hp electric Air Compressor motor

1930artdeco

Well-known member
Joined
Dec 28, 2010
Messages
1,109
Location
Lynden, Wa
Ok. My AC motor is just not powerful enough to turn my rebuilt pump. I am looking for something in the 3 HP range, single phase with a CW (looking at the pulley) rotation. Everything I see is either 1Kish, 3 ph or Home deport quality. Any ideas on where to look for a good quality motor? I am currently trying to use this on a 41 Wayne compressor. There are a few 2 HP but not sure if they have the oompf to turn it. How are the H.F. motors (ick I know)?

Mike
 
To avoid these ads, REGISTER NOW!

finn

Well-known member
Joined
Mar 27, 2005
Messages
16,375
Location
The UP, God's country
Industrial Air compressor dealer. Major cities have them. Or any electric supply house as far as that goes.

My local electric shop rebuilds motors or can order whatever I need, and our county population is less than 30000.

There are dozens of compressor houses on the internet that sell quality motors. I found several selling name brand motors last week when looking for a 5hp compressor motor, although the name brands aren’t going to be priced like the no name imports.

Even the name brands are probably going to be imported at the power level you’re looking at, though.
 
Last edited:

micromind

Well-known member
Joined
Sep 24, 2023
Messages
3,106
Location
Fernley, Nevada, about 30 miles east of Reno.
Look for used ones. Usually, used is just fine, sometimes you get a dud though.

In my experience, the best brands are Doerr, Leeson (the sons of Lee Doerr), Baldor (the dor part is Lee Doerr's Father), Emerson (which includes many sub-brands) and others I can't think of at the moment.

There are tons of '3HP' motors out there, usually 'compressor duty' that are not 3HP at all. They are labelled 3HP because that's the absolute maximum the motor can produce but only for a short time. A true 3HP single phase motor will draw between 12 and 16 amps @ 230 volts.

Another thing is RPM. A 3450 RPM (or thereabouts) is generally less $$$ but not as good as a 1725 RPM model.

I don't know anything about the HF ones.
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,581
Location
Northern Virginia
Look for used ones. Usually, used is just fine, sometimes you get a dud though.

In my experience, the best brands are Doerr, Leeson (the sons of Lee Doerr), Baldor (the dor part is Lee Doerr's Father), Emerson (which includes many sub-brands) and others I can't think of at the moment.

There are tons of '3HP' motors out there, usually 'compressor duty' that are not 3HP at all. They are labelled 3HP because that's the absolute maximum the motor can produce but only for a short time. A true 3HP single phase motor will draw between 12 and 16 amps @ 230 volts.

Another thing is RPM. A 3450 RPM (or thereabouts) is generally less $$$ but not as good as a 1725 RPM model.

I don't know anything about the HF ones.
Interesting about the lineage of the various motor firms!
 

johnre

Well-known member
Joined
Dec 1, 2016
Messages
1,059
Location
Portland, OR
Century is another reasonable brand. Dayton is a lot more pricey.

Regarding 3450 vs. 1725 RPM, the task here is to match what it is intended to replace for the HP rating, pulley diameter, and RPM. While a 1725 RPM motor will cost more, all else equal, and might be considered "better", it's really the application that matters the most here.

That being said, the pulley diameter can be a variable that you control in order to make either a 1725 or 3450 RPM motor work in an application where new and old are mismatched.
 
Last edited:
OP
1

1930artdeco

Well-known member
Joined
Dec 28, 2010
Messages
1,109
Location
Lynden, Wa
So I went to the local shop that rebuilds/sells motors. The one they had on the shelf won’t work for my application. He said that it would burn itself up being only a two pole motor vs. a four pole. Essentially just not enough torque.

He recommended and explained a VFD for a three phase motor. So I am now looking to get a 3 phase 3-5 hp motor. It will be less expensive than a single phase motor of equivalent hp. So I will get a motor have them set it all up and call the electricians back out🤬🙄. And who knows maybe next year I will have a functioning air compressor.
 

LopezBart

Well-known member
Joined
Oct 13, 2023
Messages
2,564
Location
Lopez Island, WA
So I went to the local shop that rebuilds/sells motors. The one they had on the shelf won’t work for my application. He said that it would burn itself up being only a two pole motor vs. a four pole. Essentially just not enough torque.

He recommended and explained a VFD for a three phase motor. So I am now looking to get a 3 phase 3-5 hp motor. It will be less expensive than a single phase motor of equivalent hp. So I will get a motor have them set it all up and call the electricians back out🤬🙄. And who knows maybe next year I will have a functioning air compressor.
The big advantage of the VFD is being able to set a reasonable acceleration ramp; this will greatly reduce inrush current, since you're not applying full power to an essentially locked stator.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,721
Location
Fargo, ND
So I went to the local shop that rebuilds/sells motors. The one they had on the shelf won’t work for my application. He said that it would burn itself up being only a two pole motor vs. a four pole. Essentially just not enough torque.

He recommended and explained a VFD for a three phase motor. So I am now looking to get a 3 phase 3-5 hp motor. It will be less expensive than a single phase motor of equivalent hp. So I will get a motor have them set it all up and call the electricians back out🤬🙄. And who knows maybe next year I will have a functioning air compressor.
That will work, but unless you find a used 3PH motor, I doubt is will be much less money. A 1PH in, 3PH out VFD for 3 or 5 HP won't be cheap either.

I bought a compressor with a 5HP, 3PH motor and ran across a used 1PH. I looked into a VFD and decided it was too much money, and I had the motor already! Of course, unless you are looking at some Amazon Chinese no-name VFDs.
 
Last edited:
OP
1

1930artdeco

Well-known member
Joined
Dec 28, 2010
Messages
1,109
Location
Lynden, Wa
I found a used 3 ph/5 hp Baldor for $400 and I will check it at the shop and if it works I will grab it as there is nothing around in the single phase category. They will set the VFD for me to match the motor. At this point I just want the damn thing running.......
 
OP
1

1930artdeco

Well-known member
Joined
Dec 28, 2010
Messages
1,109
Location
Lynden, Wa
Well, the baldor motor got sold:( but he has a 2 HP 3ph Nord motor with a reduction gear. I will take the reduction gear off because I don't need it. So if it is a 4 pole it should work but I will have it tested in a shop.
 

stonesfan68

Well-known member
Joined
Apr 19, 2012
Messages
2,764
Location
Houston, TX
I'd try Zoro. If you can find a 15-20% off coupon they are generally pretty price competitive especially since they offer free shipping.
 

whateg01

Well-known member
Joined
Mar 13, 2006
Messages
11,533
Location
doo dah, kansas, usa
Well, the baldor motor got sold:( but he has a 2 HP 3ph Nord motor with a reduction gear. I will take the reduction gear off because I don't need it. So if it is a 4 pole it should work but I will have it tested in a shop.
If you were worried that a 2hp motor wasn't going to work before, why is it ok now?
 
To avoid these ads, REGISTER NOW!
OP
1

1930artdeco

Well-known member
Joined
Dec 28, 2010
Messages
1,109
Location
Lynden, Wa
The guys at the shop said that a 2 pole 1.5 hp won't last (it tripped the breaker after 30 sec. of run time). A 4 pole hopefully is a little beefier torque wise and will last. I will ask on Monday and if they say no then I will look again for another one....I am not smart when it comes to electric motors, I am hoping 3 ph is a bit more powerful than single ph.
 
Last edited:

micromind

Well-known member
Joined
Sep 24, 2023
Messages
3,106
Location
Fernley, Nevada, about 30 miles east of Reno.
The guys at the shop said that a 2 pole 1.5 hp won't last (it tripped the breaker after 30 sec. of run time). A 4 pole hopefully is a little beefier torque wise and will last. I will ask on Monday and if they say no then I will look again for another one....I am not smart when it comes to electric motors, I am hoping 3 ph is a bit more powerful than single ph.

Typically, a 3Ø motor with 3Ø utility power will have more starting torque than a single phase one but with a VFD it'll have less.
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,049
Typically, a 3Ø motor with 3Ø utility power will have more starting torque than a single phase one but with a VFD it'll have less.

Oh, ok didn’t know that. Well….rats.
with a properly spec'd "name brand" VFD you'll have 150-200% of running torque for startup with a VFD. either way you need an unloader if you want things to work properly.
 

N_Jay

Well-known member
Joined
Nov 1, 2016
Messages
1,179
with a properly spec'd "name brand" VFD you'll have 150-200% of running torque for startup with a VFD. either way you need an unloader if you want things to work properly.
A good VFD with a soft start feature will have more torque during start up.
 

whateg01

Well-known member
Joined
Mar 13, 2006
Messages
11,533
Location
doo dah, kansas, usa
The guys at the shop said that a 2 pole 1.5 hp won't last (it tripped the breaker after 30 sec. of run time). A 4 pole hopefully is a little beefier torque wise and will last. I will ask on Monday and if they say no then I will look again for another one....I am not smart when it comes to electric motors, I am hoping 3 ph is a bit more powerful than single ph.
Yes a 4 pole motor has more torque, roughly twice what a 2 pole has. It also spins half the speed so to get the speed back you have to have pulley sizes adjusted. Doing so cuts the torque in half so you're right back where you started. You need to know how fast you want to spin the pump. Then size the motor accordingly.
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,049
A good VFD with a soft start feature will have more torque during start up.
these are the ratings I'm referring to.
Screenshot 2025-12-12 at 19.50.14.png

the only time i've seen a VFD compressor fail to start was when the unloader wasn't operating properly. I've seen big boy DOL compressors start fully loaded. wish I'd thought to throw an amp-clamp set for inrush on that!
 

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,754
Location
AK
Look for used ones. Usually, used is just fine, sometimes you get a dud though.

In my experience, the best brands are Doerr, Leeson (the sons of Lee Doerr), Baldor (the dor part is Lee Doerr's Father), Emerson (which includes many sub-brands) and others I can't think of at the moment.

There are tons of '3HP' motors out there, usually 'compressor duty' that are not 3HP at all. They are labelled 3HP because that's the absolute maximum the motor can produce but only for a short time. A true 3HP single phase motor will draw between 12 and 16 amps @ 230 volts.

Another thing is RPM. A 3450 RPM (or thereabouts) is generally less $$$ but not as good as a 1725 RPM model.

I don't know anything about the HF ones.
That's cool info on Baldor, Lesson and Doer
 

Sumboodie

Well-known member
Joined
Mar 20, 2021
Messages
10,754
Location
AK
Shane you aren't near. I have a 3 phase 5hp I'd give you. It's of no use to me.
 
OP
1

1930artdeco

Well-known member
Joined
Dec 28, 2010
Messages
1,109
Location
Lynden, Wa
Well the 3 HP ran more than 30 sec. and didn't blow the breaker! Next up is to keep the intercooler lines from grinding on the flywheel and then I will let her fill the tank.
 

finn

Well-known member
Joined
Mar 27, 2005
Messages
16,375
Location
The UP, God's country
I don’t see where a 30 second run will tell you much of value. Horsepower requirements are proportional to pump load, ie the tank pressure the pump is working against. At 30 seconds your tank is no where near the cutoff pressure, so there isn’t really much motor horsepower draw.
 
Last edited:

whateg01

Well-known member
Joined
Mar 13, 2006
Messages
11,533
Location
doo dah, kansas, usa
I don’t see where a 30 second run will tell you much of value. Horsepower requirements atr proportional to pum load, ie the tank pressure the pump is working against. At 30 seconds your tank is no where near the cutoff pressure, so there isn’t really much motor horsepower draw.
I wish more people understood this. Or, more broadly, a motor doesn't "put out" HP. A load draws that from the motor and the motor is able to provide what the load requires or it isn't. If the load only needs 1/4 HP, that's all the motor is producing.
 

finn

Well-known member
Joined
Mar 27, 2005
Messages
16,375
Location
The UP, God's country
I wish more people understood this. Or, more broadly, a motor doesn't "put out" HP. A load draws that from the motor and the motor is able to provide what the load requires or it isn't. If the load only needs 1/4 HP, that's all the motor is producing.
Science in general isn’t well understood by the populace.

These are things that are taught in ninth grade, I would think. Instead I keep hearing how we need more wood shop classes.

It’s sort of frustrating sometimes.
 
OP
1

1930artdeco

Well-known member
Joined
Dec 28, 2010
Messages
1,109
Location
Lynden, Wa
You are correct. I was basing my happiness of more than 30 sec. On the previous motor. It would run for 30 sec and trip the breaker. So next weekend I will do a full test run.
 