Air compressor circuit breaker size?

wazzabie

Well-known member
Joined
May 9, 2010
Messages
424
What size circuit breaker should I use? Also I have a 50amp 25ft extension cord I'm going to use. The electrical panel is in the garage and I can add a double pole. This is a portable compressor.

The motor on the compressor is:
GE MOTORS
Model: 5KCR48SR59GW
PART NO: C-MO-3013
V: 230
A: 13-1
HZ: 60
RPM: 3450 PH1
PC: B1037
 
To avoid these ads, REGISTER NOW!

JohnX14

Well-known member
Joined
Jun 2, 2014
Messages
600
Location
Boston 'burbs
False. This is a motor. Article 430 tells you how to size the wire and the breaker.

I would probably run min #12 and put it on a 30A
I think OP is installing a plug to run a cord to the portable compressor. I wouldn't put a #12 on a 30 in this case. And at 13.1 amps, a 20A 240V receptacle should be fine.
 
OP
W

wazzabie

Well-known member
Joined
May 9, 2010
Messages
424
Breakers are selected based on conductor size, not the equipment being run.

What size wire do you have in the wall between the panel and the outlet?
8 gauge Romex. The main panel box is in the garage and I have the outlet 2 feet from the panel. I can run any circuit breaker up to 50amp.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,030
Location
NJ
At 13.1A, the "5HP" you see somewhere is 5HP SPL as in NOT 5 hp. It's more like 3 hp, maybe less.

You need a minimum conductor ampacity of 1.25 x 13.1 = 16.4A >> 20amps>> #12cu.

What receptacle will you be using? Does the comp have a cord and plug now?

For this motor, on a motor circuit, the max size cb is 2.5 x 13.1 = 32.75amps>>>35a 2 pole cb.

If this circuit will have a standard receptacle, I would look into 20a "high magnetic" cb's. What is the panel mfr?

If larger conductors are used, it will require a higher ampacity recept just to be able to terminate the wires.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,994
Location
Central Iowa
Those are the same spec's as my compressor and pretty much every other 60 gallon with a SPL (3ish HP) motor on the planet. Mine runs on #12's with a 30 amp breaker but I know a few people that have theirs plugged into a 20 amp 240 volt circuit.
 

BurtEggley

Well-known member
Joined
Oct 8, 2024
Messages
887
we are discussing a 240V circuit with an extension cord?

What is the brand and model of the air compressor?
 
OP
W

wazzabie

Well-known member
Joined
May 9, 2010
Messages
424
At 13.1A, the "5HP" you see somewhere is 5HP SPL as in NOT 5 hp. It's more like 3 hp, maybe less.

You need a minimum conductor ampacity of 1.25 x 13.1 = 16.4A >> 20amps>> #12cu.

What receptacle will you be using? Does the comp have a cord and plug now?

For this motor, on a motor circuit, the max size cb is 2.5 x 13.1 = 32.75amps>>>35a 2 pole cb.

If this circuit will have a standard receptacle, I would look into 20a "high magnetic" cb's. What is the panel mfr?

If larger conductors are used, it will require a higher ampacity recept just to be able to terminate the wires.
50amp welder outlet. I need to add a circuit breaker at the panel. Has a run about 2ft away from the main panel.
 

BurtEggley

Well-known member
Joined
Oct 8, 2024
Messages
887
should be a white label on the rail. If it looks like this, here a typical manual on one made by Devilbiss. Open it in a PDF reader, go to the parts about 1/2 the way thru and see if it looks like yours. That said, both craftsman that I have can be wired for 120v or 240v. The breaker specs are in the manual. Breaker and wires should match.
 

Attachments

  • 919195412_owners__manual.pdf
    5.2 MB · Views: 13

lolaetype

Well-known member
Joined
Dec 11, 2019
Messages
2,100
Location
North Western Arkansas
This might be helpful:


And, FWIW AI says:

The GE Motors 5KCR48SR59GW is a 220V/230V motor (often used in 5HP air compressors) that typically requires a 30-amp, double-pole circuit breaker. It should be wired using 10 AWG wire for the load. Ensure the breaker matches your specific service panel brand (e.g., GE, or compatible Eaton CL or ABB breakers).

Key Considerations:
  • Breaker Type: 2-pole (Double-pole) circuit breaker.
  • Amperage: 30 Amp (Standard for 5HP compressor motors, check nameplate for exact full-load amps).
  • Voltage: 220V-240V.
  • Wire Size: 10-gauge wire is generally required.
 
To avoid these ads, REGISTER NOW!

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,610
Location
BC
What size circuit breaker should I use? Also I have a 50amp 25ft extension cord I'm going to use. The electrical panel is in the garage and I can add a double pole. This is a portable compressor.

The motor on the compressor is:
GE MOTORS
Model: 5KCR48SR59GW
PART NO: C-MO-3013
V: 230
A: 13-1
HZ: 60
RPM: 3450 PH1
PC: B1037

My speedaire is similar... 15A/240V rated and has successfully run on #12/20A circuits for 25ish years. The factory cord plug is a 6-20P.
 

beltfeed

Well-known member
Joined
Jan 22, 2006
Messages
226
Location
USA
Sharing a common breaker for two different loads has its short comings (safety issues). Like others have said the load specs for the welder would help.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,590
Location
Fullerton, CA
If you have room in the panel, just install another breaker.
At only 2' from the panel, just ignore (or use) the welder outlet.
Buy a 30A breaker and #10 wire. Install a 6-30 (30A/250V) outlet.
 
OP
W

wazzabie

Well-known member
Joined
May 9, 2010
Messages
424
Update: I found the manual for this air compressor. The manual calls for a min 15 amp circuit and a fusetron type t fuse. From the panel I have this dedicated circuit: 30amp 8/2 Romex, 2 pole type O interrupting rating 10,000 120/240v Siemens L-5538 E82615 circuit breaker. https://www.homedepot.com/p/Siemens-20-Amp-Double-Pole-Type-QP-Circuit-Breaker-Q220U/100074746 I suspect the plug on the air compressor is rated only for 15 amps. If I change out the plug can I use this air compressor on the 30amp circuit? The model number is 919.176951 Do I need to change the circuit breaker to a fusetron type t fuse?

1774126947466.png
 
OP
W

wazzabie

Well-known member
Joined
May 9, 2010
Messages
424
correction 6 gauge wire on a 50 amp outlet.
I have two dedicated circuits from the panel that run about 3 feet in length: 1. 8/2 romex on 240v 30 amp Siemens circuit breaker 2. 6/2 Romex on 240v 50 amp Siemens circuit breaker
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,610
Location
BC
also in the manual:
Screenshot_20260321-143652-478.png

one more time.... wire in a 6-20R on a 20A 2pole breaker with #12 wire. Plug your machine in.
 
OP
W

wazzabie

Well-known member
Joined
May 9, 2010
Messages
424
The extension wire that I would like to use with the air compressor is a Direct Wire 25' 220 Volt 50 Amp Heavy Duty 8/3 Welder Extension Cord MIG TIG. https://ramweldingsupply.com/p/direct-wire-cable-8-3-heavy-duty-welding-machine-extension-cord/

If I change out the cord on the air compressor to fit the end of my welding extension cord and then plug this into the 30amp dedicated 240v circuit would this be ok for the air compressor? I just need to use it temporary for about a week.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
Update: I found the manual for this air compressor. The manual calls for a min 15 amp circuit and a fusetron type t fuse. From the panel I have this dedicated circuit: 30amp 8/2 Romex, 2 pole type O interrupting rating 10,000 120/240v Siemens L-5538 E82615 circuit breaker. https://www.homedepot.com/p/Siemens-20-Amp-Double-Pole-Type-QP-Circuit-Breaker-Q220U/100074746 I suspect the plug on the air compressor is rated only for 15 amps. If I change out the plug can I use this air compressor on the 30amp circuit? The model number is 919.176951 Do I need to change the circuit breaker to a fusetron type t fuse?

1774126947466.png

If that motor is truly rated for 5HP, there is no way it could go on a 15a protected circuit. it would blow the fuse. The FLC chart amperage for 5HP is 28a and typical 5hp motors have an FLA of 20-23a 240v.

post a pic of the motor nameplate. if the HP is listed as SPL or special, and/or the FLA is listed as 15a, then the 5HP rating in the manual is bogus and the motor is closer to 3HP rating....

FYI- the plug would need to be rated for the HP rating of the motor if you change it from factory. There are no standard NEMA plugs and receptacles that are rated for more than about 3hp....
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
also in the manual:
Screenshot_20260321-143652-478.png

one more time.... wire in a 6-20R on a 20A 2pole breaker with #12 wire. Plug your machine in.

not if the motor is rated for 5HP. that would be incorrect. wire for motor circuits is required to be rated 125% of FLC table current. for 5HP that is 25 rated wire.... and a nema 6-20R is not rated for 5HP.... the devil is in the details...
 
OP
W

wazzabie

Well-known member
Joined
May 9, 2010
Messages
424
also in the manual:
Screenshot_20260321-143652-478.png

one more time.... wire in a 6-20R on a 20A 2pole breaker with #12 wire. Plug your machine in.
Ok I'll wire a new circuit. I found a spare 20A 2 pole breaker and 20a-250v outlet. I have some spare 10/3 Romex. Can I use this wire rather then the #12 wire? Also this new outlet will be the 4th dedicated circuit running from the main panel. Is there a limit on how many circuits and outlets I can have next to the main panel? With this new run I will have 30amp 220v, 50amp 220v, 20amp 120v and 20 amp 220v.
 
OP
W

wazzabie

Well-known member
Joined
May 9, 2010
Messages
424
If that motor is truly rated for 5HP, there is no way it could go on a 15a protected circuit. it would blow the fuse. The FLC chart amperage for 5HP is 28a and typical 5hp motors have an FLA of 20-23a 240v.

post a pic of the motor nameplate. if the HP is listed as SPL or special, and/or the FLA is listed as 15a, then the 5HP rating in the manual is bogus and the motor is closer to 3HP rating....

FYI- the plug would need to be rated for the HP rating of the motor if you change it from factory. There are no standard NEMA plugs and receptacles that are rated for more than about 3hp....
1774135002570.png1774135122081.png
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,610
Location
BC
#10 should work fine. In case the receptacle terminals arent rated for #10, pigtail on #12.

Also, the HP on the motor label is blank. The 5HP on the craftsman label is fiction.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,610
Location
BC
not if the motor is rated for 5HP. that would be incorrect. wire for motor circuits is required to be rated 125% of FLC table current. for 5HP that is 25 rated wire.... and a nema 6-20R is not rated for 5HP.... the devil is in the details...

The machine isnt rated for 5hp when it comes with a 15-20A factory cord plug.
 
OP
W

wazzabie

Well-known member
Joined
May 9, 2010
Messages
424
1774137278768.png Actually I may need to get a GFCI. This will be in the garage. The other outlets I wired years ago for welders are not GFCI.
 