Questions on Sistering New Rafters/Rafter Ties/ Ridge Board
bobbuilder440
I have 2x4 rafters 24" on center and rafter ties only ever 48" 23 foot span and only 2x4's rafter ties. No collar ties were previously installed. Looks like they used some type of midspan purlin web truss midspan of the rafters that sits on the rafter ties to transfer load of the rafters. However the rafter ties being only 2x4's spanning 22ft or so are obviously now sagging and the roof has sagged you can see from the street. One side of the garage shares a wall with the house and one rafter tie has pulled the stud it was toe nailed into (below the top plate) out of the wall a few inches.
Trying to do some repairs and have a few questions.
With a cracked rafter tie (it is split like down the middle. Is it best to just replace it completely or sistering on new boards acceptable?
What is the best methodology for repairing a cracked / split reidge board (not load bearing but still cracked in multiple spots its like a 1x10 or something.
Also, any ideas on how if I lift the roof and try to pull walls back, on one side I am pulling on a wall that also is butted up to / connected to the house wall. That make it impossible?
I dk if any of that makes sense or if I am wrong about certain things but any help appreciated.
NUTTSGT
Northern Central Ohio
Pictures are going to be very helpful here.
Pics would be very helpful, especially when you mentioned something like this...
"some type of midspan purlin web truss midspan of the rafters"
Also, a location would help, nothing specific but if you are dealing with heavy snow loads or hurricane type weather...some needed information is pertinent to correcting the issue.
firebirdparts
Kingsport, TN
To answer your first question, it's very important to get a good connection directly to the rafter. I would replace.
To answer your second question, it's practically impossible. The best thing to do is to unload it and be sure you're right.
To answer your "any ideas" question, You can push the roof up with very simple framing lumber techniques. Stand up a post on top of a bottle jack and insert prop poles if you get it to move. We have had some guys in this forum pull the walls together using cables, and so you can do that, but it takes much more force to push up a low roof this way. Keep in mind here that attaching the roof to the top of the wall is not that easy to do well. You may break the rafters loose if you just start pulling the walls with a winch.
mike93lx
Richmond, VA
2x4 rafters? I don't think I've ever seen a span table with 2x4 and I wouldn't use them on even a 12' wide shed.
What condition is the roofing material and decking? If it nerds replacing, tearing all of the existing off and properly rebuilding will be a lot faster and easier
PCustoms
VT
I was thinking that, but the mention of a ridge board threw it off.
Pretty much everything in the OP is throwing me off.
The section @NUTTSGT bolded especially, but the span is listed as 22ft and 23ft as well...
I'll just sit back to see if OP comes back
dscheidt
The garage at the house I grew up in was built like that. The house was built in the 20s, the garage was newer and would have comfortably held two full-size 60s station wagons, plus the lawnmower and general stuff. so bigish two car garage, with a single big door. It was spindly as all hell, it was all 2x4s, with a bigger ridge beam. But the roof deck was done with tongue and groove planks on an angle, and it had horizontal wood siding. Lots of stiffness in that skin, and lots of nails to move a bit as loads shift. The dudes that built these things knew what they were doing, and produced pretty good result -- an inexpensive structure as possible given the available materials that last a reasonably long time. It would be insane to build like that now, but 75 years ago?
bobbuilder440
Hey I am back my account got like bot banned so i emailed the site and was like hey wth that *****. and i just checked now because i came to this site on a google search for another topic and what do you know it let me login. So yes I will post some pictures. and no I am probably describing everything wrong and have no idea what I am talking about-- I agree with you.
So yeah any schooling or any fatherly stern talking to is much appreciated before I make a mistake and f it up.
Thanks
Ill put up photos tomorrow
bobbuilder440
roofing material is single layer composite shingles that are probably 10 years old in decent shape. You could probably get away with just shingling the garage with a close matching color but it owuld look weird. I got a quote from a guy doing side work and it was going to be 7000$ he said roughly to reframe it inside without removing the roof. But he didn't really explain anything about what that entailed / lumber sizes / the plan etc. Just kinda said that number.
But that is more than I want to spend. It is junk garbage right now. I figure sistering on some new rafters and two beams running perpendicular to the rafters-- garage door wall top plate to opposite top plate on exterior wall of garage. Throw two posts in the framing stud bay so that the beam can sit on those and be a little shorter to be able to get it into place. Then brace the midspan of the rafters off of that. Only issue is whether my garage door header would support that. I beefed up the jack and king studs near it just slapped some in.
I also am dealing with finding termite damage around and some framing was pretty well and eaten. I would surmise that maybe a few of the rafters have termite damage so that adds to it. Also someone was storing stuff for awhile on the 4ft on center 2x4 rafter ties and that also led to them having a huge dop.
The photos kind of **** its confusing. You have like a hip and a gable meeting. Then you have an addition onto the exterior wall opposite the garage door. that is why it looks like not an exterior wall. Then you had someone built an addition in the garage so that is running directly below a rafter tie and looks intentional but its not.
driftpin
Professional Engineer (P.E.) time! Find an engineer and do it properly.
#1] hire a P.E. to see what you have, and make a determination of the shape it's in. You may still have an active infestation. That needs to be dealt-with. Finding eaten structural pieces, whether or not it's an active colony, could affect your structural integrity, as I'm sure you seem to know. Let's say, no active colonies are located. Do your work, and once it's completed, then have it tented. If you use the Chinese gas instead of USA Vikane, it's less-expensive. I wouldn't want to count on a significantly-damaged rafter or other structural component to 'sister-to' as you could be nailing into something which has no support presently sufficient to bear a load.
Any re-roof, the shingles should be a full removal/tear-off to the decking, and consider re-nailing the sheathing in a pattern concurrent w/the current code.
I got a discount on my house insurance because I used a membrane on the sheathing before the underlayment/shingles.
Bert_
NW Iowa
Really doesn't look that bad. It's a home made truss. Common for the time. If the ridge is sagging, look at where the ties connect to the rafter at the top of the wall.
I see a few joist hangers. If those are on the ties, then whoever put those in didn't have a clue about the forces exerted by a rafter/truss. Those are a potential issue.
bobbuilder440
so ive done a lot of termite work before and ive been treating by drilling holes in anything that looked suspicious but i havent found any new frass. there was subterranean evidence but it is old too. I am trenching for those as well. But ive tested like every board one or two were eaten badly the rest feel really pretty solid. and anywhere i saw any kick out holes i just treated. going to treat my attic with boracare as well
bobbuilder440
Can you just walk me through it. And yeah home made trusses makes sense now. But hte bottom piece of the truss is a 20ft long 2x4 that doesn't really make any sense regardless right? there still has to be force down on the truss? Maybe I am confused on trusses because I thought you would have at truss every junction you would have a typical rafter spacing. I have plenty of 2x4 rafters that are not part of the truss system they are just going from top ridge board (1 x 10) cracked in places down to the top plate.
As far as brackets are concerned just ignore them if they get you distracted. Lots of boards were pulling away from very few nails and any brackets were just put there temporarily to hold stuff al ittle stiffer. I am positive they aren ot hurting anything most of them are only nailed once or twice to not split the wood just add a bit of temporary support.
bobbuilder440
However it is laid out right now is exactly how they built it to code in the 50s. Or someone else came in and did some stuff but all the wood looks the same amount of weathered.
The boards used to build the homemade truss were like 1 x8s or 1x10s. what are you calling the purlin things that are running mid span of the rafters?
bobbuilder440
so far i only found one stud in the kitchen to garage framing that was eaten pretty well through then it stops in both directions. old subterranean evidence. My neighbor had subterranean and treated awhile ago and maybe it killed off my colony as well. I have poked every rafter a million times to find soft spots and used a small drill bit in any i was suspect and then termidor foamed anything I did find. Most of the rafters are strong there may be a few with some rot from old roof leak etc. but they are plenty strong to nail into and transfer roof sheather nails into the new ones in my opinion
Bert_
NW Iowa
A joist hanger is for downward force. A rafter tie does not exert much downward force. A rafter ties main function is to act in tension, keeping the walls from spreading apart. A joist hanger has very little strength in tension.
A rafter tie/bottom cord does not hold anything "up". Get that idea firmly planted in your head and you will be in a lot better place to make any repairs.
bobbuilder440
Well where those joist hangers are where someone had cut the lower rafter tie and toe nailed it into another 2x4 running perpendicular that was then toe nailed again into another rafter tie on one end and the top cord on an exterior wall. So I would imagine there is some weight in the downward vortice where adding a joist hanger isn't going to hurt anything especially since it is two nails holding the board in toe nailed from 1950. And I don't think you are supposed to cut a rafter tie and run a horizontal 2x4 to transfer the load to another undersized rafter tie. I get that rafter ties aren't supposed to have much downward force acting on them. But gravity is always at play and people put storage and other stuff in a garage thinking they are ceiling oists so .
MovingAlong
Looks more like overspan rafters with a purlin in the middle, not trusses. Pics are hard to make sense of, no real "overall" shot from above the ceiling line.
Larry Haun talks about them here:
bobbuilder440
People are telling me these are trusses but I am at a loss. Garage roof California no snow load everything built with 2x4’s and the “trusses” obviously were built in place.
What I was calling rafter ties / may actually be “bottom chords” are over 20ft long 2x4. Ridge board is non structural.
There is also a hip roof? that comes and ties into the same area. Everything is sagging to sh**.
Trying to figure out how to rebuild it or beef it up.
(this was email to Gregvancom on youtube) Ive watched a ton of your videos but nothing quite looks like what I got going on. Seems completely under built. There are two “purlins” what I am calling them that run from garage door mid span wall to the opposite exterior wall top plate. That is built from 2x4’s and then angled 2x4’s inside.
Here are some pics figure could make an interesting video. Watched hours and hours of your stuff and learned a lot.
I filled intros gap at the garage door area to beef it up thinking I may run a beam near there to run new midspan supports for the rafters. But it isn’t really midspan however I think they could be run at a slight angle and still be okay. Otherwise I could put the beam further towards the middle of the rafters (or whatever that board would be called on a truss) which would put the beam over the garage door header which seems strong doesn’t have any termite damage but unknown if I can move the beam in a little ways from the king and jack studs and it would still effectively load transfer easily to those studs. Like is it linear the load transfer for how far away you are from the end of the header the potential for sag in the header. If that makes sense.
Green** That is a 2x4” running 20ft at least with what people are telling me is a “truss” which the diagonal supports are built out of 1x10 or something like that and notched into the top ridge board which is all starting to crack etc.
BLUE line ** The spacing between the bottom chords or rafter ties I dk what to call them from now on I am going to stick with rafter ties is 4ft the rafters are spaced 24” apart and 2x4’s as well.
VIOLET The board running from above the garage header perpendicular to the truss sitting on top of its bottom chord also runs from the top plate header of garage door 20ft back to the top plate of the exterior wall. There is no support for it and all the weight is pushing down then on the truss bottom chord or the rafter tie whichever one is which. Which a guy on the forums is saying those should have no downward force on them at all (the rafter ties / truss bottom chords) but it seems to me if you are supporting mid span down to those then by all definitions they have a downward force on them.
One of two purlins (I am calling them) or maybe they are web trusses built midspan of the rafters which in this photo I just beefed them up before I figure out what to do because they were pulling apart etc. I got it to tighten up by lifting up on the bottom of it with a jack a little bit and then added the brackets and the vertical 2x4 and the plywood gusset.
By beam I meant post. Like from the floor to that cut 2x4" instead its load is just transferring through the toe nails into that other 2x4 which is then toe nailed into a bottom chord or rafter tie. Stupid
The room in the back was added on after it was built so this wall was the original exterior wall of the house.
Any help much appreciated.
bobbuilder440
see if those make better sense and i will watch the video for sure thanks
bobbuilder440
Such an AWESOME video. Those dudes drive nails so incredibly fast and effective. cool that they had fun editing back then too to make it look like they never check for plumb or level just wam bam thank you ma am. But still awesome. Yeah so basically a purlin but a purlin without a load bearing wall under it and there never was one. So effectively useless on under sized ceiling joists rafter ties. I could remove the existing purlin and run a beam and then support the rafters mid span that way. But how would I get a beam 20ft long? would I need an LVL or somethign else. and I would need 2x top and bottom. Or could I do like they do and side nail them together but that is because they are sitting on a load bearing wall so they aren't supporting the weight themselves just transferring it down. So yeah I am still confused.
Did they try to build the purlin like a web truss so that none of the weight actually is on the bottom chord and somehow it works like a beam and transfers the load all the way to the other top plates? is that the idea?
bobbuilder440
is it trying to be a web truss? do those supposed to pass load only to the two opposing walls and not sag in the middle at all?
bobbuilder440
I am thinking if I built these on the rafters that have nothing on them (they are just rafters) no truss built that that could beef it up. Like build this on all the eones that are empty
MovingAlong
I think you're starting to figure out the existing "design" and the challenges. Now you just need to add an engineer to the process to answer those specifics on sizing the solutions. :thumbup:
As motivation - remember, the last guy didn't use one. ;)
bobbuilder440
Cost of an engineer to try to come up with something and go through all those hoops = probably $2000 minimum here? I would imagine. Versus I can upsize all the lumber I want, buy all the best hardware I want, and couldn't possibly make it any worse (I know people will debate that). but quite literally whatever last person did it (with engineers drawing up the plans these were track homes and inspectors) was garbage. So when people say run to an engineer on a very simple garage roof it makes me think you also don't have any idea what you're talking about. Which is okay, just why waste the time to tell me that. I know engineers exist, I know they would come up with something for this, I know that is the more correct route. But sistering on even 2x6's onto the 2x4 rafters from ridge board to top plate would only strengthen it. adding collar ties would only strengthen it. Adding more rafter ties would only strengthen it. Building other trusses to match the one in there (which I dont even think are trusses really) would only strenghen it. I am not going in there with a sawzall and starting to cut everything down. I understand that a temporary support wall or something needs to be there when removing load bearing pieces. Thanks
bobbuilder440
At same time I am just trying to post a fun problem to people ON A FORUM meant for people to ask questions to see if anyone has dealt with something similar and can offer some tips and problem solve. It isn't meant to be a hey I am a genius look at me. I like learning however, and that is what forums and online spots are supposed to be about
driftpin
Judging from your pictures and responses, you just need to hire someone.
You're SO right. Thanks Bert
bobbuilder 440 said:
"So when people say run to an engineer on a very simple garage roof it makes me think you also don't have any idea what you're talking about."
Ah Bob, are you trying to intentionally piss-off people, and ignore the 'hive's advice,' when multiple people give their worthwhile observations to your particular problems? Because with remarks like that, people will write-off your obstinacy to doing things where you are not using subject matter experts in construction methods and techniques based upon physics principles, materials qualities and formal engineering training.
If you need a curriculum vitae for every contributor then ask for it. Don't be surprised if no one steps-up to help you.
I am a retired licensed lifesafety inspector and plans examiner in the state of FL, and have had to spend time doing case studies of catastrophic building collapses and other tragedies involving mass casualties, to retain my credentials.
You are a recent arrival, a couple of months under your belt. It would behoove your level of understanding to see in other threads how those in supplication ask for advice, and how they react to that which is offered. People will willingly help, but not if they're insulted.
bobbuilder440
No insults intended. Just pointing out my logic, and happy to be told where I am flawed and that is how I learn. When I am just told to hire someone, then I have every right to explain why I haven't reached that conclusion yet. Could that be what I end up doing? Sure. But ultimately I don't think this is necessarily a super complex problem. I would not be making any structural changes by simply sistering on to the existing trusses or whatever you want to call them and making them stronger but keeping them as is. I am not dealing with a truss that was an engineered truss stamped by a company, I am dealing with a truss that was built by some dudes that put up houses as fast as possible with no nail guns and used as few nails as seemingly possible. Some of the rafter to rafter tie or whatever you want to call it maybe have 2 nails in them whereas modern code I believe would call for like 8-20 depending on the size of the lumber. So yeah, I still don't think it is wrong of me to say hey anyone have some ideas on how I can beef this up? If that is insulting then I apologize.
manwithtools
Lebanon, TN
Don't take this the wrong way, but if it's so simple, why ask for advice on how to do this? If you were fully competent and confident you would have already been done by now. I think you might be realizing that it's not a simple as it seems. None of us are standing there looking at reality, so it's difficult to give meaningful input without reservation. Good luck on whatever you decided to do and remember, adding more material and fasteners to a structure is not always the right answer.
firebirdparts
Kingsport, TN
There are plenty of people who could just look up in there for 5 minutes and explain it all to you for free. If you are a neighbor of mine I'd do that for you.
Regardless of what people here say, you know there are just a few trusses, mostly rafters. I only see one truss, but it looks like you see 2. Okay. There are some connections between different planes. Hip rafters, apparently, but I can see valley rafters in your pictures.
Normally, in this forum, people are trying to chop up everything, remove the rafter ties, cut a hole in something, etc. You're not. You can build onsite trusses up in there, and yes, it'll be strong. You need good connections. That is really easy to do where the truss connects to itself, but hard to do between roof system element and the top of the wall. Hard to get a fastener in there.
Raising the roof, removing the sag, is going to pull a lot of stuff apart. Applying the force is easy, but it'll pull stuff apart rather than "unbend" that ridge pole.
firebirdparts
Kingsport, TN
P.S. I would love to answer all your picture questions, but 10 other people will post, and then you'll start jabbering with them, and I never know if you even read what I wrote. It certainly does not appear that you read what I wrote the first time.
Here, I'll start. Picture 1 questions:
1. NO not a web truss. NO.
2. Appears to be unwise. Let's assume that was intended as rafter support and that it was done ineffectively by an unwise person and then if somebody talks about it again, ignore him.
bobbuilder440
Ok, thanks Fire bird. I went back and reread your earlier response before the pictures. I will try to get better pictures that are laid out more cleanly i was just using random ones I had found in my phone.
What I was thinking though is the bottom plate on the foundation there is like another 2" or 1.5" so if I added a 4x6" beam after notching out a section of the bottom plate then resting on the foundation footing (so it would stick out past the existing 2x4 studs by 1.5" or whatever. Then whatever new support purlin I could put in midspan of the trusses like what they had built out of 2x4" I could rebuild out of 2x8 or 2x6. But unsure of how I would lap the two joints in the middle if they are unsupported. It is basically not good idea to ever run a 2x6 or 8 20ft span unsupported I would imagine.
Just crazy to me that this was done to any sort of code or construction standards back then. Just goes to show you how cheap houses were back then everyone could afford one it just sorted depended on where you wanted to live. and nobody thought these homes would still be around in 50 years it would've been cheaper to just knock them down and rebuild htem