I'll get a photo of the motor tomorrow, but here's the wiring diagram in manual. I expect the motor will show 208-230 VAC. I guess I've always been wiring dryers and ovens, etc. and not motors. I guess I spent a little more on copper than I needed to. Thanks, guys.
It looks like they were expecting 10/2 nm-b cable to power a disconnect. I can't tell if they provided and wired the disconnect or if you are providing it and then connecting to the power unit.
For a 2 conductor nm-b cable, the conductor colors are black and white. The white is re-identified (by you) to indicate it is an ungrounded hot conductor. Any color except green is ok to use. Let's say you made it red. The black and red wire connect to your 2 pole cb. Obviously, the bare grounding conductor is terminated at both ends.
If you have 10-3 nm-b, use the black and red conductors to connect to the cb and disconnect lugs. Cap the white wire at both ends.
Per the diagram, only two wires come out of the motor. Hook them up as shown. If there are more wires from the motor or nameplate shows multiple voltages, then the nameplate is needed.
Does the power unit have the thermal overload protective device?