Which Boiler do I need?
silvermonte
iowa
Heres the back story, self built place. 80'x50' post frame building, 2500 of it is garage and 1500 of it is house, the place is tall enough for a second floor but for now its just a single floor. The concrete slab is just poured on grade, has r20 pink board insulation all the way around the slab 3' down and r10 under the concrete. The walls are r29 and the attic is r60 and Im located in east central Iowa. The garage has 2 zones and the house has its own zone, id like to plan ahead and have the option for a 4th zone for the second floor when that becomes a reality.
Editing for more information- 1/2" pex and i tried really hard to make all the lines as close to 290', the one that is off the most is just 10' shorter compared to the others. There are 2 zones in the garage with 5 runs apiece, and the house has 5 runs for the 3 zones. If a 4th zone went in for the second floor it would probably only have 4 runs at most. The house has 2 1/2 baths in it.
Heres where I would like some help. Are there better options for the money then the items listed? I have propane and electric is just silly expensive where im at so thats not an option really.
boiler- https://www.menards.com/main/plumbi...ler/rmcbh-l199i/p-1642874299838873-c-8519.htm
Panels- https://www.menards.com/main/plumbi...ete-system/6959775/p-1471978652594-c-8521.htm
kj_mustang
Harrisonburg, VA
Boiler spec write up is not very thorough. Since it is a Combi boiler you really need to know the max DHW flow rate and how much DHW flow you and the house occupants potentially will be using at the same time.
PoorUB
Fargo, ND
How many feet of tubing? Roughly 30 BTU per foot, so no sense in putting i a larger boiler than the tubing can handle.
Need to do a manual J calc.
Yes and no. The manual J might come out higher than the floor tubing can use. If the building needs 100,000 BTU, but he has only 50,000 BTU of tubing a larger boiler is a waste.
silvermonte
iowa
I have roughly 4350' of 1/2" tubing in the floor between the 3 zones.
PoorUB
Fargo, ND
4350 feet x 30 BTU gets you 130,000 BTU. So for the existing you need 130,000 BTU. Then add any anticipated additions, or the second floor in your case. Also you 50x80 comes to 4,000 sqft. Most of the time, for floor tubing in normal situations we always ended up with I foot of tubing per 1 sqft of floor, 4250 feet is a bit more, but pretty close to the 1 ft per 1 sqft. So if the anticipated second floor is 1,000 sqft, you will need another 30,000 BTU. In reality you probably don't need that much heat for the space. the 199,000 boiler is not out of line, 150,000 would probably do it.
Are you looking for a combi boiler, for domestic hot water too? If you are then you will want to size it for your domestic hot water requirements.
silvermonte
iowa
That particular boiler is a combi boiler, which I wanted for domestic use also, if its feasible. I have room for a standard water heater, but why use one if I can get away with a combi boiler and call it a day. Im out of my element with this stuff which is why Im asking for suggestions. The house would be 2 1/2 bathrooms and a 4 bedroom house. I dont know what a standard amount for domestic water would use.
fitter30
Peace Valley,mo
1/2" pex, roughly 290' apiece and 15 runs total , 2 zones in the garage and one in the house that are 5 runs apiece.
147,900 btu's total
each zone 49,300 btu's
Flow through each loop 1 gpm
Head .03X300= .9' then add 2' for piping around the boiler.
In the house any wood floor coverings or vinyl check with flooring manufacturer for temp limit for water temp most 80-85°. Boiler glycol 30% minimum 50% max. 30Glycol manufacturers list total freeze protection and slush. Slush might have to go to web site or call customer service.
jlv03
SE IA
If you have the space in your utility room, I would put some thought into an 80 gallon heat pump water heater (HPWH). Then either skip the combi boiler or use the combi to back up/complement the HPWH.
silvermonte
iowa
What is the advantage of that heat pump so I can look into them? Im not aware of them.
jlv03
SE IA
Biggest advantage of the heat pump water heater is low cost to operate. As a side benefit it cools and dehumidifies the space in which it is located.
Sumboodie
AK
I have a combi.
You should put a small water heater in line. There's quite a delay between opening a kitchen or bathroom spigot and having hot water. And that happens everytime. Can't close the water and open 30 secs later and expect hot water.
Takes a good 30-45 seconds for it to fire and make hit water and the water pipe to clear. Not quite as bad if it's already heating for the floors.
Even just a under sink 2-3 gallon tank would be fine as a buffer tank.
As far as boiler size, again, DO A MANUAL J. That's the correct way to know.
Sumboodie
AK
I
147,900 btu's total
If that was true, any house in the south would ruined floors. 80* is a "nice day" haha
caleb383
That is a pretty big space to heat, so zoning it properly from the start is definitely the right move. Skipping electric and propane makes total sense given the local costs, though balancing those long line lengths for the radiant panels will take some careful planning.
Sumboodie
AK
Should have been done before the tubing was installed...
But, you know.
I doubt mine was.
It's 1250 sq ft on 3 loops. The pex is run with not much planning, least that I can figure. It's not even O2 barrier pex.
It heats though. Got lucky I guess. (I bought it 10 years after built)
silvermonte
iowa
But, you know.
I started looking into that and it was over my head. I just kinda winged it and copied off of videos I watched that had a place that was similar to my place. I learned enough to get the tubing laid out to get them as close to the same length as possible and drew up a few plans until i had it right. Admittedly not the smartest way to do things.
silvermonte
iowa
I started doing some reading , pretty neat stuff. I pay 27 cents a kw/h so I worry about the running cost of one of them.
PoorUB
Fargo, ND
That would be fine for domestic hot water, but it wouldn't be close to enough for the floor heat. The recovery on a HPWH is very low. It works fine for people that don't use much water, or use hot water often so it has time to regenerate.
As for floor heat the floor pump ran the tank would get cold and go over to electric back up. I helped install a set up for a customer and he had to water source heat pumps heating hot water for floor heat. They were 5 HP each and staged. It was a larger house and in the middle of our North Dakota winters one unit ran 24/7 and the other would run half the time.
jlv03
SE IA
Apologies, I should have clarified a bit, I meant a HPWH just for domestic hot water. Use a boiler for the floor heat, just give it a break during the off season.
fitter30
Peace Valley,mo
I
There a difference when you have a 70° space and 85° floor temp. RH falls as temp rises. Dries out the wood.
kc.warmyourfloor.com/is-radiant-heat-safe-under-wood-flooring/
Please note: Some wood floor manufacturers specify that their flooring should not be subjected to temperatures over 82° to 84°F, be sure to check with your flooring dealer or manufacturer and set the floor heating thermostat limit temperature appropriately.
Sumboodie
AK
My previous house would run the floor water up to 130*. That's a common setting used around here.
Now actual floor temp was maybe 90-100*
It needs to be nearing 100* to feel "warm"
PoorUB
Fargo, ND
We have electric floor heat in our bathroom, the floor temp 'stat is set at 82F and feels warm on our feet.