Changing to a larger Amp breaker

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
23,025
Location
Amarillo,TX and Stinnett,TX
I have an 125Amp service in my shop. I have a phase converter running from a 50 amp circuit, I want to replace it with a larger breaker and wire. What's the largest breaker I can use?
 
To avoid these ads, REGISTER NOW!

spongerich

Well-known member
Joined
Apr 17, 2010
Messages
2,339
Location
Monroe, NY
What's the max amperage of the phase converter? As long as you use appropriately sized wire, you should be able to go as high as that. If your branch circuit is more than a few feet from your panel. be prepared to spend a shitload of money on the wire. I ran a 220/50 from my service panel out to my barn and I think I ended up spending $300 on wire.
 

danski0224

Well-known member
Joined
Jan 29, 2005
Messages
13,700
Location
Near Naperville, IL
Probably something like 80% of the main panel breaker rating, which is 100A if your panel is 125A.

I am not an electrician or code enforcement officer.

$.02
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
I have an 125Amp service in my shop. I have a phase converter running from a 50 amp circuit, I want to replace it with a larger breaker and wire. What's the largest breaker I can use?

Nothing to stop you from putting in anything you want. If you match the breaker and wire size, that pretty well takes care of it. Do you have a 125 amp main? What is the size of the breaker protecting the the shop service.

Charles
 
To avoid these ads, REGISTER NOW!
OP
9

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
23,025
Location
Amarillo,TX and Stinnett,TX
The issue I was having was one of my converters was blowing the fuse. I ended up replacing the disconnect with a larger 50 amp one. I need to check the voltage on each leg and adjust with run caps. All is well now, thanks.
 