switched outlet

Garage5.9

Well-known member
Joined
Jan 26, 2011
Messages
2,508
Location
Maui,Hawaii
Im looking to put a switch inline with a outlet i plan on putting on the side of my garage. The outlet will be for my 120v craftsman 30gallon compressor. Im tired of always flipping the switch on and off and running a extension cord. My only concern is will i be overloading the switch running a compressor ? I'm talking a regular light switch
 
To avoid these ads, REGISTER NOW!

nehog

Well-known member
Joined
Jan 2, 2010
Messages
7,935
Location
Jaffrey, NH
IIRC they do make switches designed for higher currents... (Heck, I've got wall switches designed for three phase!)

A 'regular' household switch would perhaps last a week or two before it failed, likely causing a fire!

Personally, I'd use a contactor (relay), but I have a bunch of them sitting on the shelf as well... That would avoid the voltage drop issues with the extra wiring to the switch, and limit the requirement for a high current switch (which, BTW, won't be cheap!) I did this with my high power metal halide lighting, switches that control a relay set in a control box. Made wiring much easier, too...
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
You need what looks like a light switch, but is much heavier built, and rated at 20 amps (or 30 amps) and is marked on it as "motor rated".

HERE is a motor rated 20 amp Leviton double pole switch. It should have an actual horsepower marked on the switch, usually on the metal strap. You do not need to use both sets of contacts, just run in the screws on the unused set of terminals.

Charles
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,487
Location
SE MI
You need what looks like a light switch, but is much heavier built, and rated at 20 amps (or 30 amps) and is marked on it as "motor rated".

HERE is a motor rated 20 amp Leviton double pole switch.
Don't confuse the poor guy with a double pole switch for a 120V circuit !

For a 120V circuit he needs a single pole, single throw Leviton CSB1-20. It is rated at 20A and 1 HP. Hopefully the OP has 12 gauge wiring !
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Don't confuse the poor guy with a double pole switch for a 120V circuit !

For a 120V circuit he needs a single pole, single throw Leviton CSB1-20. It is rated at 20A and 1 HP. Hopefully the OP has 12 gauge wiring !

I could not find a example of a single pole motor rated switch quickly. You are correct however, no need for the double pole if you can find the single pole. The key is having the horsepower rating on the switch.

Charles
 
To avoid these ads, REGISTER NOW!

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,487
Location
SE MI
Thanks guys , Should i look for a 20 amp rated outlet too or what ?
To answer that question I need to ask 2 questions
  1. What size breaker is on that circuit ?
  2. What size wire is used from the breaker panel to the switch and outlet ?
 
OP
G

Garage5.9

Well-known member
Joined
Jan 26, 2011
Messages
2,508
Location
Maui,Hawaii
To answer that question I need to ask 2 questions
  1. What size breaker is on that circuit ?
  2. What size wire is used from the breaker panel to the switch and outlet ?

I was thinking of adding another dedicated circuit just for this. Is 12g wire enough or should i go with 10 ?
 