Is this wire sized right?

StaggeringGoat

Well-known member
Joined
Jul 1, 2011
Messages
758
Location
Oregon
My new shop condo has a small 3600w instant water heater for the sink like this one:
http://www.grainger.com/Grainger/CHRONOMITE-LABS-Water-Heater-6DXT2

Specs are 120v, 30A, 3600W. It's hooked to a 30A breaker using #10 romex in a pretty long run. That just barely works...but I thought you weren't allowed to use 100% of the wire rating 100% of the time? In other words the max draw on a 30A breaker should be only 24 amps....shouldn't it? (80%)

Is this heater installed correctly? I haven't got the power turned on yet so I can't tell you how well it actually works or not.
 
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
point of use instant water heaters arent considered continuous loads. The manual for yours says 30 amp circuit so youre fine as far as circuit ampacity. How long is 'pretty long' ? I would have used a 240v model...only 15 amps..
 