200 amp service wire sizing

toyotadriver

Well-known member
Joined
Dec 30, 2010
Messages
1,586
Around here, the most common wire size and type that you see for 240 volt service is aluminum 4/0 4/0 2/0 or occasionally you'll see aluminum 4/0 4/0 2/0 2/0.

What is the recommended wire sizes for 200 amp service and why?

Thanks.
 
To avoid these ads, REGISTER NOW!

chickenhauler

Well-known member
Joined
May 31, 2011
Messages
473
Location
Pennsylvania
I used 3/0 copper for mine. Pricey, but I don't like aluminum wire on or in my house. A lot depends on your electric company. Mine only required 3 lines, and then #6 ground at the service breaker.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I used 3/0 copper for mine. Pricey, but I don't like aluminum wire on or in my house. A lot depends on your electric company. Mine only required 3 lines, and then #6 ground at the service breaker.

There's nothing wrong with aluminum wire feeding your home.

There are a gazillion homes in the US wired with 4/0 4/0 2/0 AL. But if spending more money on copper helps you sleep at night.....
 

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
There's nothing wrong with aluminum wire feeding your home.

There are a gazillion homes in the US wired with 4/0 4/0 2/0 AL. But if spending more money on copper helps you sleep at night.....

Agreed. The terminations of aluminum SE in the main panel have proven basically bulletproof. All the issues were with switch/receptacle connections. Everyone uses aluminum feeders around here.
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
are you actually speaking to service entrance conductors? Or a feeder?
 
OP
T

toyotadriver

Well-known member
Joined
Dec 30, 2010
Messages
1,586
There's nothing wrong with aluminum wire feeding your home.

There are a gazillion homes in the US wired with 4/0 4/0 2/0 AL. But if spending more money on copper helps you sleep at night.....




My house, built in 2008, has 4/0, 4/0, 2/0 aluminum wire 200 amp service.
 
To avoid these ads, REGISTER NOW!

mtne

Well-known member
Joined
Dec 3, 2007
Messages
113
Location
Denver
2011NEC - Table 310.15(B)(7) Service or Feeder rating - 200A - 2/0 copper or 4/0 aluminum

Why? 'Cause it's the code. And you only want three wires for the service entrance.... hot, hot, noodle.........
 

v8garage

Well-known member
Joined
Jun 27, 2007
Messages
901
Location
Texas
Around here, the most common wire size and type that you see for 240 volt service is aluminum 4/0 4/0 2/0 or occasionally you'll see aluminum 4/0 4/0 2/0 2/0.

What is the recommended wire sizes for 200 amp service and why?

Thanks.

Where is "around here"?
V/8
 

mtne

Well-known member
Joined
Dec 3, 2007
Messages
113
Location
Denver
Where is "around here"?
V/8

Good point.......... No idea what code is outside of the USA..... and it can vary depending on where you are which edition is accepted and then it always falls to the AHJ to say what goes.

Shouldn't be too much, or any variance with services tho....
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,779
Around here, the most common wire size and type that you see for 240 volt service is aluminum 4/0 4/0 2/0 or occasionally you'll see aluminum 4/0 4/0 2/0 2/0.

What is the recommended wire sizes for 200 amp service and why?

Thanks.

That depends what the SE is for... Anything other then a dwelling & it's not correct.
 