My son has an issue at his shop in ohio.He is feeding a sub panel and there is an existing 1 1/4" conduit that he can either use,or if he cant, he will have to tear out 16' of his deck to bury a new pipe. he will be running 3 - 2's and a # 6 ground.Is that going to be allowed in the 1 1/4" pipe?
 
To avoid these ads, REGISTER NOW!

Gooch

Well-known member
Joined
May 30, 2009
Messages
676
Location
Petersberg, IA
My son has an issue at his shop in ohio.He is feeding a sub panel and there is an existing 1 1/4" conduit that he can either use,or if he cant, he will have to tear out 16' of his deck to bury a new pipe. he will be running 3 - 2's and a # 6 ground.Is that going to be allowed in the 1 1/4" pipe?


should work just fine. assuming Sch. 40 PVC and THHN conductors.
 
OP
T

trbomax

Well-known member
Joined
Mar 21, 2010
Messages
2,556
Location
starvation lake,mi.
Its going to be inspected and his concern is that they will not allow those conducters in that size pipe. I told him to use 1 1/2", and he would but he doesnt want to tear out the deck to dig the trench. He put the 1 1/4" in when he built the deck because he knew that he was going to run this elec in the future.
 

Gooch

Well-known member
Joined
May 30, 2009
Messages
676
Location
Petersberg, IA
Its going to be inspected and his concern is that they will not allow those conducters in that size pipe. I told him to use 1 1/2", and he would but he doesnt want to tear out the deck to dig the trench. He put the 1 1/4" in when he built the deck because he knew that he was going to run this elec in the future.

you can put 5-#2 THHN's in a 1.25" pipe. what he wants to do will pass inspection.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
If all he's feeding is a 100 subpanel, three #3's and a #8 ground are all thats required unless he's upsizing for voltage drop.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,783
If all he's feeding is a 100 subpanel, three #3's and a #8 ground are all thats required unless he's upsizing for voltage drop.

Upsizing ungrounded conductors kicks in the requirements of 250.122(B).

Here is a copy & paste of it from the 2008 NEC.

(B) Increased in Size. Where ungrounded conductors are
increased in size, equipment grounding conductors, where
installed, shall be increased in size proportionately according
to the circular mil area of the ungrounded conductors.

Just tossing that tidbit in.
 

fefarms

Well-known member
Joined
Jan 25, 2007
Messages
186
you can put 5-#2 THHN's in a 1.25" pipe. what he wants to do will pass inspection.

THHN will not pass in buried conduit. He needs THWN-2 or other wet service rated wire. Some types (such as THW) are larger in diameter and might not meet the conduit fill limits.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,783
THHN will not pass in buried conduit. He needs THWN-2 or other wet service rated wire. Some types (such as THW) are larger in diameter and might not meet the conduit fill limits.

Most THHN is dual rated as THWN, but it is good to verify before buying
 

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
when was the last time anyone saw (new) thhn that wasnt thwn? i dont think they make just straight thhn anymore....
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
when was the last time anyone saw (new) thhn that wasnt thwn? i dont think they make just straight thhn anymore....

I've never seen any that wasn't dual rated. But it seems like someone always has to point it out on here....:headscrat
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,783
when was the last time anyone saw (new) thhn that wasnt thwn? i dont think they make just straight thhn anymore....

I have only seen it once & there is no telling how old it was.
 