120/240VAC for mill and lathe

danroy323

Active member
Joined
Feb 3, 2011
Messages
38
Location
Quebec City Canada
I'm about to start the wiring of my garage. I have a metal lathe and Bridgeport mill. Both are setup to run on 240VAC single phase. At my father's garage they were plugged with 6-50 plugs (welder plug) on 30A circuits. I have lights and digital readout(well, I wish I had the DRO... but I have the lights!!) on them that run on 120VAC so I need a 120V receptacle as well. I was thinking of using a NEMA 14-30 plug and receptacle (clothes dryer plug). That way I would have a neutral wire as well and I could wire a 120V receptacle right on the machines, reducing wiring clutter between machine and wall. Is this a legal way of doing things?

Thanks,
Dan
 
To avoid these ads, REGISTER NOW!

TWX

Well-known member
Joined
Apr 1, 2010
Messages
817
Location
Phoenix
When I was researching this same thing before going with 14-50 for my compressor I learned that dryers used to be hot-hot-neutral so that they could run 120V or 240V depending on the system in the dryer. Now many dryers are four-wire, to add the ground.

I'm pretty sure the main reason why the 14-50 setup was chosen was specific for your application.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,763
How large are the motors? 30A is too large to tap off for lights w/o fusing it down, but a 20A 4wire 125/250V rated locking (NEMA config. # eludes me) receptacle/plug is EZ to get.
 

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
How large are the motors? 30A is too large to tap off for lights w/o fusing it down, but a 20A 4wire 125/250V rated locking (NEMA config. # eludes me) receptacle/plug is EZ to get.

I honestly wouldn't have a problem with it. Light fixtures are fed from 30A circuits all the time. 240.5(B)2 lets you use 14 awg taps from a 30 amp lighting circuit, not that I consider this a light fixture, but just as an example.
 
To avoid these ads, REGISTER NOW!
OP
D

danroy323

Active member
Joined
Feb 3, 2011
Messages
38
Location
Quebec City Canada
Thanks guys for the answers.

The machines aren't near me so I can't check for sure but I'd say 1 or 1 1/2hp.

The only thing I see is that I'd have 30amps at the 120V outlets. Just need to be careful and limit the use of these outlets to the work lights and digital readout.

Dan
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
FWIW - when I run my lathe and mill feeds, I run a dedicated feed for each. Running a separate #12 for a 110V accessory outlet doesn't cost much of anything unless you have to go buy a 250' spool. I like to be able to power down the machines and still have accessory power close by.

If you want to self-limit the outlet use, put twist lock plugs and sockets on the 110V power outlets
 
OP
D

danroy323

Active member
Joined
Feb 3, 2011
Messages
38
Location
Quebec City Canada
I was thinking about it, if my machines are 1 1/2hp or less I should be ok with 20 amps circuits. 20amps in the 120V receptacle would be better.
 