250.50, 250.52 and 250.53 cover the grounding and would be damn long if I cut and pasted it.........
The shorthand is that there are 1-8 means of grounding. Any of them present at a structure must be bonded together to make the ground system. If none are present, one of the 4-8 shall be installed and used. Defacto that means a ground rod as it's cheap and easy. 250.53 goes on to require a supplemental electrode for single grounding electrode unless the resistance to earth is 25ohm's or less. So cheap and easy, you set another ground rod cause most little shops don't have the appropriate testing equipment.
Yes this is all 2011 code, the areas I work in all adopt current code, usually within 6 months.............. it's the minimum and they often add stuff above and beyond.
The new arc fault signage **** is out of hand...........
The shorthand is that there are 1-8 means of grounding. Any of them present at a structure must be bonded together to make the ground system. If none are present, one of the 4-8 shall be installed and used. Defacto that means a ground rod as it's cheap and easy. 250.53 goes on to require a supplemental electrode for single grounding electrode unless the resistance to earth is 25ohm's or less. So cheap and easy, you set another ground rod cause most little shops don't have the appropriate testing equipment.