breaker/wire size/plug ??

pete379

Well-known member
Joined
Dec 4, 2009
Messages
471
bought a new plasma cutter,looks like it can max draw 70 amps, on single phase 240v. I want to add a dedicated circuit,and plug. any recommendations ?

thanks, pete
 
To avoid these ads, REGISTER NOW!

W-Cummins

Well-known member
Joined
Jan 9, 2006
Messages
1,641
Location
Iowa
If you need a 70 amp rated plug your probably looking at a pin and socket plug set $$$ if you can use a 60 amp you can get a nema 15-60p setup

William....
 

klhitman

Well-known member
Joined
Sep 17, 2010
Messages
1,016
Location
pewee valley
i have a wire sizing chart on my computer at work. i will try to post it when i go in on Monday.

does the cutter already have a whip on it or do you need to make one. SO cable of that size will be pricy!!! you could get it at any welding supply house. i just bought some 8/4 wire for a job i and and it was like 3 bucks a foot.
 
To avoid these ads, REGISTER NOW!

BFBOB

Well-known member
Joined
Sep 20, 2011
Messages
5,073
You might want to get a book about the NEC. Not the NEC itself; that can be paralyzingly incomprehensible even to pros (like me, albeit a low voltage pro). Audell's has books that are more in tune with answering your questions. I'm sure there are others. Any attuned to household wiring will be guide you with this sort of project.
To second a previous poster's comments, be sure you're aware of the difference between amps of consumption and amps of output. The wiring and breakers you install to supply the welder must at least equal its consumption. Its output is irrelevant.
 

Greatbear

Well-known member
Joined
Jan 17, 2008
Messages
1,702
Location
Columbia/Fulton, MD
They Hypertherm 85 draws 58 amps at 240 volts. You can use the NEMA 15-60P/R plug/receptacle with no problems.

Whatcha cutting up? Battleships? ;)
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
You can use a 6-50 P/R and most likely put it on a 8/60 circuit, a 60 because the breaker is cheap. It would run on a 50, if a guy is coming on this forum chances are he won't use this machine to its potential, its a pretty respectable unit, a couple steps up from most hobby garages, never need the maximum allowable breaker or utilize the duty cycle.
I am sure, 8/3 cord is what it calls for, if they allow for max breaker over 60 it should be 8.
 
Last edited:
OP
P

pete379

Well-known member
Joined
Dec 4, 2009
Messages
471
You can use a 6-50 P/R and most likely put it on a 8/60 circuit, a 60 because the breaker is cheap. It would run on a 50, if a guy is coming on this forum chances are he won't use this machine to its potential, its a pretty respectable unit, a couple steps up from most hobby garages, never need the maximum allowable breaker or utilize the duty cycle.
I am sure, 8/3 cord is what it calls for, if they allow for max breaker over 60 it should be 8.

so the 6 ga. wire i've got is heavy enough? :)

thanks, pete
 

Thruxton

Well-known member
Joined
Dec 30, 2010
Messages
767
Location
Virginia
My advice: RTFM! I'll bet there is a breaker recommendation from the mfr in it, and that's what I would use. A quick look at the Hypertherm site and the manual for their Powermax85 shows recommended fuse sizes, for example.
 