Dr.HairyOlds
Active member
So i just picked up a Quincy QE-10 compressor. It's 240V 3 phase 10 hp motor that draws 28 amps according to the tag. I had planned on buying a 30 amp, 3 pole breaker for it but it came with the fuse panel it was wired with.
My questions is: Do I need a breaker or do I wire the fuse panel direct?
What would a direct connection in a box look like? If anyone can identify the different legs that would be great.
Another question: Assuming I use the fuse panel, it has 100A RK5 time delay fuses in it. That is how the last guy was running it. Is this correct? Should/can I swap the fuses out for a lower amperage to better protect the compressor?
My questions is: Do I need a breaker or do I wire the fuse panel direct?
What would a direct connection in a box look like? If anyone can identify the different legs that would be great.
Another question: Assuming I use the fuse panel, it has 100A RK5 time delay fuses in it. That is how the last guy was running it. Is this correct? Should/can I swap the fuses out for a lower amperage to better protect the compressor?