It became very difficult to 'seat' the anchors using just the breaker bar and standard wrench. The anchors would not pull up flush with the concrete floor. I've added the pictured 'extensions' to give more leverage on the seating nut, and I think that I can crank it till it pulls flush w/ the deformed washer, but wanted to check since I'm putting quite a bit of force onto the anchors.

Is it ok to really torque the hell out of these as long as you have the bolt secured?

The corner anchor is the one I've been working on w/ the extensions till I felt like I should confirm my approach before continuing.

imag0666q.jpg


imag0667d.jpg


imag0668y.jpg


imag0669h.jpg
 
Last edited:
To avoid these ads, REGISTER NOW!

chickenhauler

Well-known member
Joined
May 31, 2011
Messages
473
Location
Pennsylvania
They don't need to be flush to be seated. I'd be more concerned with the one on the crack. You really should be away from joints or cracks like that, and I'm pretty sure the requirements are 12"
 
OP
T

turbotuner20v

Active member
Joined
Dec 8, 2011
Messages
28
They don't need to be flush to be seated. I'd be more concerned with the one on the crack. You really should be away from joints or cracks like that, and I'm pretty sure the requirements are 12"

I was advised that while not ideal, centering one bolt and leaving the other 2 on either side of the crack would be ok for my sub-4000lb vehicles. There weren't really any other mounting positions that would work for the car given the space constraints of the garage.

Is there a recommended number of turns to stop at when seating? I can keep on turning till it pulls flush w/ my extension, but I didn't want to over do it and either damage threads or shear the bolt.
 
Last edited:
OP
T

turbotuner20v

Active member
Joined
Dec 8, 2011
Messages
28
There should be torque specs in the manual? I seem to remember reading that it's 100-150 ft lb. range.

I'll double check the maxjax manual then... didn't think I saw anything during those steps and the wej-it box just had a strip of paper w/ the different size bolts they make.
 
To avoid these ads, REGISTER NOW!
OP
T

turbotuner20v

Active member
Joined
Dec 8, 2011
Messages
28

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,010
Location
Coastal Maine
You don't want them to be flush with the concrete.Except for the crack ,your install looks fine.I would redo that one with epoxy...you can't be too safe!If they are flush or even .001" above the slab the holding power could be compromised.See the MaxJax install thread for more on this issue.:beer:
 
Last edited:

Nogglefish

Well-known member
Joined
Dec 24, 2007
Messages
46
90ft-lbs and they should NOT come up flush. Chances are they are not biting if they come up flush before hitting 90ft-lbs.
 

olytdi

Well-known member
Joined
Dec 3, 2011
Messages
2,202
Location
Olympia, Washington
I had a couple of anchors on one post come-up; one flush and one above that. But, they did both bite. I ground down the one that came up (an eighth) and called Dannmar about it. I was told that as long as the anchor indeed bit, that it wouldn't be an issue. So far, lifting two ton cars hasn't been an issue and everything is stout.
 