I'm not 100% certain on these electrical things. But I recently purchased a used Champion compressor and want to purchase a new mag starter for it. It has a 5 hp Dayton motor on it, which draws 23.5 amps, single phase.
It looks to me that a NEMA class 1 mag starter is required. Is this correct? Anything wrong with getting one bigger than my application? As in a NEMA 2 or will it have adverse affects? Which brands are good? I am scoping a few Square D units.
Also, I keep reading about these heaters installed on the starters, these are rated to the amperage on the motor? So I need to make sure I get a mag starter that still has parts available or are pretty much all these heaters interchangeable?
All help is appreciated. Thanks
It looks to me that a NEMA class 1 mag starter is required. Is this correct? Anything wrong with getting one bigger than my application? As in a NEMA 2 or will it have adverse affects? Which brands are good? I am scoping a few Square D units.
Also, I keep reading about these heaters installed on the starters, these are rated to the amperage on the motor? So I need to make sure I get a mag starter that still has parts available or are pretty much all these heaters interchangeable?
All help is appreciated. Thanks
. I do understand relay Logic because we use it all the time in our business. I was just concerned it was a NEC code I was not familiar with on 5 hp motors. I can see a Mag start on a 7.5 HP or more motor being a code requirement but not on a 5hp motor. I'm not saying it would be a bad idea though as an option if someone wanted to set it up that way.....
. Very well explaned and thanks OccupantRJ. It will help a lot of people