Flourescent/GFI problem

szyg6h

Well-known member
Joined
Feb 13, 2012
Messages
85
Location
Seabeck, WA
I have an overhead flourecent light that when I turn it on, turn it off, sometimes, not consistent, it kicks off a GFI that is on a totally different breaker and circuit. That GFI circuit is just for bench outlets. ....and again a totally different breaker and circuit. The flourecent circuit checks proper for polarity, grounding, etc with the little 3 prong device that plugs into a grounded circuit.
The fixture probably came from HD, Lowes, ACE- don't remember.
Any ideas?
Maybe a capacitor could be wired into it? ....but what capacitor specs?


:dunno:
 
To avoid these ads, REGISTER NOW!

jpinca

Well-known member
Joined
Sep 23, 2011
Messages
225
Location
NorCal
Are the two circuits proximate, especially running together for any length?
 

jpinca

Well-known member
Joined
Sep 23, 2011
Messages
225
Location
NorCal
yes they are.

You could be experiencing inductive-coupled EMI caused by a overshoot/undershoot transient from the light.

While it would be a fun science project to figure it out exactly, you may be time ahead trying a new GFI- especially another brand. Otherwise you can start by separating the cables.
 
OP
S

szyg6h

Well-known member
Joined
Feb 13, 2012
Messages
85
Location
Seabeck, WA
You could be experiencing inductive-coupled EMI caused by a overshoot/undershoot transient from the light.

While it would be a fun science project to figure it out exactly, you may be time ahead trying a new GFI- especially another brand. Otherwise you can start by separating the cables.

the EMI transient is exactly what I have been thinking.

Went to Home Depot this afternoon and talked to a guy I respect for his electrician knowledge- have had good conversations with him before.

And, yeah, I could make a science project out of it. HD electrician suggested just replacing the old "fat" tube fixture, with the new T8, cold start, different starting device. I did. So far so good with many on/off cycles. Plugged in the old fixture, into a circuit next to the switch for the problem light, and it tripped the GFI.

Thanks to all for the suggestions.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,765
Flourescent lamp ballasts do leak a small amount current to the case,perhaps the leakage was enough to trip the GFCI, worked on a office building years ago that none of the 2X4 recessed troffers were grounded, each suite had 8 fixtures & touching the ceiling grid & a gas line while working in the ceiling I would get bit, the reason was some non-code compliant work when they were built in 1979, but anytime I worked were there was a large # of ungrounded fixtures, always got a tingle, but have not seen any info on the current electronic ballasts & their leakage, if any...
 

Shocker

Well-known member
Joined
Nov 23, 2008
Messages
2,015
Location
Olympia, WA
T8 or T12 fixture?

T12 ballasts seem to leak a lot more current as they age. T8 ballasts seem to be better.
 
OP
S

szyg6h

Well-known member
Joined
Feb 13, 2012
Messages
85
Location
Seabeck, WA
T8 or T12 fixture?

T12 ballasts seem to leak a lot more current as they age. T8 ballasts seem to be better.

It was the T12.
Very interesting. Heard at HD that the T12 is history soon. Also heard that the T8 is (did he say) electronic and that is why they start at lower temps.
 

jbberns

Well-known member
Joined
Jan 1, 2012
Messages
105
The fixture is on a separate breaker and it was causing the GFI to trip?
 
OP
S

szyg6h

Well-known member
Joined
Feb 13, 2012
Messages
85
Location
Seabeck, WA
...and this is a 2 year old GFI, and this has been going on for a year or more.

With the new T8 fixture, still no porblems. But I plug in the old fixture to an outlet, GFI trips.

I see no constant Voltage leak when on, but I see spark when I plug it in. Transient jolt....
 