picts of your in-floor heat set ups.

socapots

Well-known member
Joined
Jan 3, 2011
Messages
544
Location
Canada
Re: picts of your in floor heat set ups.

Here is my system. The main reason I am posting this is to show that you don't have to spend thousands and thousands of dollars to have in floor heat. Some people have more money in copper fittings than I do into my whole system. So try not to laugh or criticize too much, my in floor is as simple as it gets, as cheap as it gets, and works really really well.

1st pic shows my wood boiler, which I designed and built myself. It works well. Heating my 1500 sq ft house only, it consumes about 5 cords of wood/winter which is pretty damn decent here in MI. With the shop tacked on I am averaging about 8 cords.

The shop is 200 ft away from the boiler, and pex was laid in a trench and then sprayfoamed over.

1000 sq ft, 2 "zones", 16" on center runs, with faucet style valves on each one to help with zone control, although both are wide open and I see no need to change it.

The rest is simple. A 24 volt transformer sends voltage to a digital thermostat on the wall which turns a 24 volt relay on and off, which switches the pump on and off. No heat exchangers are used, boilerwater goes through the floor. A mixing valve has been added to reduce water temp entering the floor from 180 to about 90 degrees.

The bucket is used to purge air out of the system, as my shop is uphill from the boiler bleeding the air out was a challenge.

This is the first year I have been running it and it works great.

Now back to your fancy beautiful polished copper systems with gauges and do-dads galore.

Thats petty good.
how often do you have to feed the fire?
 
To avoid these ads, REGISTER NOW!

VairKing

Well-known member
Joined
Jan 12, 2011
Messages
64
Location
Grand Rapids, MI
Re: picts of your in floor heat set ups.

You didn't mention anything about your insulation package, but I'm guessing that you took no shortcuts.

KO

Yes shop is insulated, fiberglass batts in the walls and cellulose in the ceiling. There is no insulation under my slab though, as I poured a cement cap on top of the existing cement floor to hold my heating lines.
 

Attachments

  • mexico 136 [800x600].jpg
    mexico 136 [800x600].jpg
    91.7 KB · Views: 620
  • mexico 139 [800x600].jpg
    mexico 139 [800x600].jpg
    98.3 KB · Views: 537

whitey42wlc

Member
Joined
Aug 21, 2011
Messages
6
Re: picts of your in floor heat set ups.

Here are a few snaps of my set up. The name of the game was to have it as simple as possible. This propane Noritz is 199 000 btu and is heating a 6000'
pole barn in Ontario. R40 attic, R28 walls, 2" foam slab insulatuion.
We are still under construction so don't bust me on having it run on an extension cord ! Grundfos 3 spd pump pumping 24- 220 loops 1/2 oxypex.
Stat calls and a Taco valve opens routing the flow through the heater.
Took a lot to get the slab up to temp in December but I am amazed at the even heat. Keeping the shop at 60 degres and leaving the fans off.
Even on our coldest days the heater runs maybe two to three times a day.
What a learning curve. A 60-65 degree shop is PLENTY WARM.
The floors are not warm as I had expected. Fans off, the furnace almost never fires. Propane consumption is 2 100lb bottles every 8-10 days.
thats about 16 litres per day or about $10-12/day. At first I thought expensive but when you consider the shop is three times the size of an average home, it is great. If I could heat a 2000' home for $4.00 a day
I would be calling the newspaper ! I love my in floor heat !
 

Attachments

  • radiant1.jpg
    radiant1.jpg
    138.4 KB · Views: 851
  • radiant2.jpg
    radiant2.jpg
    138.9 KB · Views: 730

1grnlwn

Well-known member
Joined
Jan 19, 2012
Messages
186
Location
Central Illinois
Re: picts of your in floor heat set ups.

Well we are just getting started, here is what we got so far. I got some diamond plate but doubt if I use it to frame my system. LOL But i do think I will take some more time to neaten up the system a little. So I may be worthy. My heat source is a Taylor 1000 OWB. And we will be heating 2500 sf.
 

Attachments

  • IMG_6375.jpg
    IMG_6375.jpg
    140.5 KB · Views: 477
  • IMG_6376.jpg
    IMG_6376.jpg
    150.8 KB · Views: 557
OP
E

E.rodz

Well-known member
Joined
Nov 11, 2009
Messages
2,434
Location
st.paul MN.
Re: picts of your in floor heat set ups.

Thanks everyone for posting. I hope this thread inspires and helps thats what its all about !! keep the posts coming.
 

BadgerBoilerMN

Well-known member
Joined
Aug 4, 2011
Messages
837
Location
Minneapolis
Re: picts of your in floor heat set ups.

Pump "position" (I think you mean orientation) has nothing to do with air in a radiant flloor heating system.
 
Last edited:

BadgerBoilerMN

Well-known member
Joined
Aug 4, 2011
Messages
837
Location
Minneapolis
Re: picts of your in floor heat set ups.

Here are a few snaps of my set up. The name of the game was to have it as simple as possible. This propane Noritz is 199 000 btu and is heating a 6000'
pole barn in Ontario. R40 attic, R28 walls, 2" foam slab insulatuion.
We are still under construction so don't bust me on having it run on an extension cord ! Grundfos 3 spd pump pumping 24- 220 loops 1/2 oxypex.
Stat calls and a Taco valve opens routing the flow through the heater.
Took a lot to get the slab up to temp in December but I am amazed at the even heat. Keeping the shop at 60 degres and leaving the fans off.
Even on our coldest days the heater runs maybe two to three times a day.
What a learning curve. A 60-65 degree shop is PLENTY WARM.
The floors are not warm as I had expected. Fans off, the furnace almost never fires. Propane consumption is 2 100lb bottles every 8-10 days.
thats about 16 litres per day or about $10-12/day. At first I thought expensive but when you consider the shop is three times the size of an average home, it is great. If I could heat a 2000' home for $4.00 a day
I would be calling the newspaper ! I love my in floor heat !

This is a nice looking system but a properly sized condensing boiler operating on outdoor reset should run continuously at a low reset temperature creating more comfort and using less fuel.
 

BadgerBoilerMN

Well-known member
Joined
Aug 4, 2011
Messages
837
Location
Minneapolis
Re: picts of your in floor heat set ups.

Here is my simple electric setup. I was going to wait to get a new NG line ran, but found a smoking deal on a Seisco electric boiler.

Line voltage thermostat controls the pump and temp sensors in the Siesco turn itself on.


DSCN2381.jpg

Nice looking work.

Since this electric boiler is at the top of the system, a low water cut-out also be at the top. Though electric boiler manufacturers show the pump down stream of the electric boiler, I prefer to pump into any low-mass boiler as pumping away will create lower pressure behind the pump. In a low water situation when the boiler flashes ot steam a boiler may burn up more readily.

Water fill is properly made at the point of no pressure change.
 

BadgerBoilerMN

Well-known member
Joined
Aug 4, 2011
Messages
837
Location
Minneapolis
Re: picts of your in floor heat set ups.

As far as getting all of the air out: I put water in through the fill valve, with the shut-off closed, and that forced out air and water through the drain valve. I kept the water flowing for quite a while to make sure most of the air was purged. The air seperator takes care of any remaining air. I'm no expert, I followed Radiantec's directions. My garage is 26 X 32 X 14. I attached a picture with the valves labeled.

You picture a 75# pressure relief valve generally used for well pressure tanks. It is unsuitable (unsafe) for radiant floor heating systems or hydronic heating systems of any kind.

You need a 30 pound relief valve reading the installation instructions and running rigid pipe to the floor.

This is potentially dangerous business.
 

BadgerBoilerMN

Well-known member
Joined
Aug 4, 2011
Messages
837
Location
Minneapolis
Re: picts of your in floor heat set ups.

Remembering that electric boilers will generally operate at 3 times the cost of natural gas I humbly submit a proper example of a condensing boiler installation.
 

Attachments

  • Contender w Radiant Manifold.jpg
    Contender w Radiant Manifold.jpg
    141.9 KB · Views: 1,212

BadgerBoilerMN

Well-known member
Joined
Aug 4, 2011
Messages
837
Location
Minneapolis
Re: picts of your in floor heat set ups.

This is a proper radiant floor over a frost protected shallow foundation, insulated with with XPS, tubeb with barrier PEX and driven with a wall-hung, condensing Munchkin/Contender boiler here in Minneapolis.

Note: oThis is one of the smallest (lowest output) condensing boilers on the market today; one pump, one zone/thermostat, one manifold with propylene glycol mixed for burst not flow.

This system operates at 98% combustion efficiency and has over 8000 operating hours without nothing but a bi-annual clean and check.
 

Attachments

  • Dr. Mellum tubing.jpg
    Dr. Mellum tubing.jpg
    145.6 KB · Views: 857

Fastback

Well-known member
Joined
Oct 5, 2010
Messages
518
Location
Indy
Re: picts of your in floor heat set ups.

This is a proper radiant floor over a frost protected shallow foundation, insulated with with XPS, tubeb with barrier PEX and driven with a wall-hung, condensing Munchkin/Contender boiler here in Minneapolis.

Note: oThis is one of the smallest (lowest output) condensing boilers on the market today; one pump, one zone/thermostat, one manifold with propylene glycol mixed for burst not flow.

This system operates at 98% combustion efficiency and has over 8000 operating hours without nothing but a bi-annual clean and check.


It looks like you stapled the pex directly to the foam board, I don't like that idea as individual studies have shown that suspending the pex higher up in the slab improves heat distribution.
 

Fastback

Well-known member
Joined
Oct 5, 2010
Messages
518
Location
Indy
Re: picts of your in floor heat set ups.

Remembering that electric boilers will generally operate at 3 times the cost of natural gas I humbly submit a proper example of a condensing boiler installation.


Really, I don't think so, that pump is pushing into the sprirovent, they even point out how that is not the ideal design.
 

70pcuda

Well-known member
Joined
Jan 15, 2006
Messages
76
Location
OHIO
Re: picts of your in floor heat set ups.

Here's my system. Hope to have it up and running later this week.
 

Attachments

  • radiant.jpg
    radiant.jpg
    75.4 KB · Views: 1,102
OP
E

E.rodz

Well-known member
Joined
Nov 11, 2009
Messages
2,434
Location
st.paul MN.
Re: picts of your in floor heat set ups.

:thumbup:
Here's my system. Hope to have it up and running later this week.

simple looking system. before you fill it up I would move your air vent to the highest part of the system or you will never get the air out of it and you will cavitate the pump. I am not an expert by ay way but this really stands out as a problem. Just trying to help.. by the way you will love the heat all said and done.!:thumbup:
 

hercules633

Well-known member
Joined
Jan 12, 2012
Messages
52
Re: picts of your in floor heat set ups.

70PCUDA- do you have any dollar amount figures on your system, minus the pex tubing? what size and brand is your boiler/on demand? how many sq feet you heating? looks great
 
To avoid these ads, REGISTER NOW!

70pcuda

Well-known member
Joined
Jan 15, 2006
Messages
76
Location
OHIO
Re: picts of your in floor heat set ups.

I don't, but could probably add up all my receipts.

going to heat 3456 sq foot

Thanks
 

jack stand

Well-known member
Joined
Feb 29, 2012
Messages
3,335
Location
Lakes Region Maine
Re: picts of your in floor heat set ups.

A couple of years ago.
 

Attachments

  • DSC02349.JPG
    DSC02349.JPG
    73.8 KB · Views: 626
  • DSC02355.JPG
    DSC02355.JPG
    86.6 KB · Views: 675
  • DSC02375.JPG
    DSC02375.JPG
    78 KB · Views: 605
  • DSC02402.JPG
    DSC02402.JPG
    79.2 KB · Views: 575

70pcuda

Well-known member
Joined
Jan 15, 2006
Messages
76
Location
OHIO
Re: picts of your in floor heat set ups.

70PCUDA- do you have any dollar amount figures on your system, minus the pex tubing?

I bought everything you see on the wall for right around $1500.
The PEX tubing was $1355
The Natural Gas, 150K btu Dayton forced air heater was a $200 craigslist purchase. Been using it to knock the chill off while working on the Radiant system.

So everything you see there was around $3055. Took a lot of shopping around and waiting for deals. :thumbup:

Takagi TK-4 on demand 199K BTU. The shop is 3456 sq ft.

Anyone know how long I can expect it to take to heat the floor up on initial startup? Overnight? days?
 
OP
E

E.rodz

Well-known member
Joined
Nov 11, 2009
Messages
2,434
Location
st.paul MN.
Re: picts of your in floor heat set ups.

I bought everything you see on the wall for right around $1500.
The PEX tubing was $1355
The Natural Gas, 150K btu Dayton forced air heater was a $200 craigslist purchase. Been using it to knock the chill off while working on the Radiant system.

So everything you see there was around $3055. Took a lot of shopping around and waiting for deals. :thumbup:

Takagi TK-4 on demand 199K BTU. The shop is 3456 sq ft.

Anyone know how long I can expect it to take to heat the floor up on initial startup? Overnight? days?

lets see the final picts. and how does it work? you can't keep us in suspense for that long.
 

70pcuda

Well-known member
Joined
Jan 15, 2006
Messages
76
Location
OHIO
Re: picts of your in floor heat set ups.

The final system looks just like the previous picture I posted, except I added a vent to the highest part of the system to get all the air out. (and it worked)

I fired the system up and the next day it was 60 degrees and hasn't really got much colder since. So I won't really know how it performs until next winter.
 

maxspeed96ct

Well-known member
Joined
Apr 6, 2012
Messages
379
Re: picts of your in floor heat set ups.

Are you guys in cold weather areas like new england running a glycol / antifreeze mixture in your slab radiant ?
 

jack stand

Well-known member
Joined
Feb 29, 2012
Messages
3,335
Location
Lakes Region Maine
Re: picts of your in floor heat set ups.

Are you guys in cold weather areas like new england running a glycol / antifreeze mixture in your slab radiant ?

I don't, it reduces efficiencies. I'm not sure how much but the radiant design Co. that I used advised against it for my situation. I suppose that if you wanted to be able to "shut down" everything for an extended period in the coldest part of the winter you'll want it. With slab heat, it is important to insulate under the slab and the vertical frost wall (in my case) so I believe that it would take more than a week of cold with the heat off before I started to wory.
 

maxspeed96ct

Well-known member
Joined
Apr 6, 2012
Messages
379
Re: picts of your in floor heat set ups.

I don't, it reduces efficiencies. I'm not sure how much but the radiant design Co. that I used advised against it for my situation. I suppose that if you wanted to be able to "shut down" everything for an extended period in the coldest part of the winter you'll want it. With slab heat, it is important to insulate under the slab and the vertical frost wall (in my case) so I believe that it would take more than a week of cold with the heat off before I started to wory.

Thanks, reason im considering it is I might not run my radiant unless im in the garage doing work for cost reasons.

But Im having trouble finding a answer, some say the pex just wont freeze inside the slab some say it can. i'd like to avoid the glycol since it takes more btu's to heat and like you said kills the efficiency
 

walrus

Well-known member
Joined
Nov 12, 2008
Messages
11,679
Location
Maine
Re: picts of your in floor heat set ups.

I'm running glycol in my solar heated slab, you will lose efficiency but not that much. In my case I have a closed loop so had to have glycol as collector temps are outside temps at night
 
OP
E

E.rodz

Well-known member
Joined
Nov 11, 2009
Messages
2,434
Location
st.paul MN.
Re: picts of your in floor heat set ups.

coming up on heating season tought it might be a good idea to get this rolling for inspirational purposes.there is some great systems on this thread. Thanks everyone for posting! keep them coming.:thumbup:
 

rev177

Well-known member
Joined
Jul 29, 2012
Messages
118
Location
Lino Lakes MN
Re: picts of your in floor heat set ups.

Mine is just getting set-up now
 

Attachments

  • 281025_10151406088480299_191299016_o.jpg
    281025_10151406088480299_191299016_o.jpg
    146 KB · Views: 405

wedge40

Well-known member
Joined
Oct 31, 2009
Messages
335
Location
Bloomington, IN
Re: picts of your in floor heat set ups.

Hope to post my layout in next few weeks. Been playing with loopcad the last couple of days to get an idea on layout.

Wedge
 

bglad

Well-known member
Joined
Jul 4, 2012
Messages
103
Location
Adirondack Mtns Upstate New York
Re: picts of your in floor heat set ups.

I started out with intentions of radiant heat in a 40 x 40 but gave up when I realized the expense of the underfloor insulation. Now I plan on just doing the mancave and bath.
 

BadgerBoilerMN

Well-known member
Joined
Aug 4, 2011
Messages
837
Location
Minneapolis
Re: picts of your in floor heat set ups.

But Im having trouble finding a answer, some say the pex just wont freeze inside the slab some say it can. i'd like to avoid the glycol since it takes more btu's to heat and like you said kills the efficiency

We never use anti-freeze unless we must e.g. snow melting. The PEX will freeze and leak if filled with water an frozen.

If you don't want to heat the slab full time, you have to think of when you wil use it. Using the heat on and off during cold weather requires a anti-freeze mix that will flow in the coldest weather. If you don't want to use it at all, the a burst mix is sufficient.

If you won't use the radiant floor until next season, test with air and fill with water next year.

Anti-freeze will de-rate the output of the slab, increase fuel consumption, cost more to pump and be hard to keep in the system...fitting leaks.
 

hidollartoys

Well-known member
Joined
Jul 15, 2008
Messages
594
Location
K. C. Metro area
Re: picts of your in floor heat set ups.

Here is mine.
 

Attachments

  • Building July 2012 020.jpg
    Building July 2012 020.jpg
    141 KB · Views: 424
  • Building July 2012 028.jpg
    Building July 2012 028.jpg
    158.2 KB · Views: 474
  • Building July 2012 021.jpg
    Building July 2012 021.jpg
    141.8 KB · Views: 462

maxspeed96ct

Well-known member
Joined
Apr 6, 2012
Messages
379
Re: picts of your in floor heat set ups.

We never use anti-freeze unless we must e.g. snow melting. The PEX will freeze and leak if filled with water an frozen.

If you don't want to heat the slab full time, you have to think of when you wil use it. Using the heat on and off during cold weather requires a anti-freeze mix that will flow in the coldest weather. If you don't want to use it at all, the a burst mix is sufficient.

If you won't use the radiant floor until next season, test with air and fill with water next year.

Anti-freeze will de-rate the output of the slab, increase fuel consumption, cost more to pump and be hard to keep in the system...fitting leaks.

I plan on running the system all winter long , but only plan on keeping the garage at a steady 55-60 degrees F

I'd really rather not run glycol . Glad you agree I don't need it .
 