copper 1/0 thw

z385488

Well-known member
Joined
Jun 3, 2011
Messages
119
Location
Columbus, GA
Does anybody know if you can use copper 1/0 thw for the service entrance from the disconnect to the main panel for a 200 amp service? It is rated for 600 volts and wrapped with a oil resistant insulation. My location is Columbus, GA.
 
To avoid these ads, REGISTER NOW!

Gooch

Well-known member
Joined
May 30, 2009
Messages
676
Location
Petersberg, IA
Does anybody know if you can use copper 1/0 thw for the service entrance from the disconnect to the main panel for a 200 amp service? It is rated for 600 volts and wrapped with a oil resistant insulation. My location is Columbus, GA.


no, 1/0 is only good for 175A, needs a minimum 2/0 copper or 4/0 Aluminum.

This is assuming single phase residence service.
 
To avoid these ads, REGISTER NOW!

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
If the lugs can handle it, namely listed for 2 conductors, 1/0 is the minimum size allowed to paralell conductors but it does have to meet the criteria spelled out in the NEC.
 