I see a lot of ways to wire a three way light circuit. I like the one below because it makes sense in my head. I just want to make sure it meets current NEC code.
But if the boxes are metallic there does not need to be a grounding jumper to the switches.There should be a ground wire going to the switches. but other than that it looks right.
But if the boxes are metallic there does not need to be a grounding jumper to the switches.
NEC 404.9(B)
Your theory is correct, the device would ground the box.I am not an electrician by trade so I have been curious about this. Makes perfect sense. Does it also work, per code, that you can run the ground to the switch and then have it ground the metallic box? I have in the past grounded both the box and the switch but know electrically when installed that both are of the same potential when together
Your theory is correct, the device would ground the box.
However 250.148(B) prohibits this practice. the following is a direct quote from the NEC.
It is required for receptacles. They have different grounding requirements than switches.... and i thought with metallic boxes a ground jumper to the device was required or at least if you are using an RS cover or Industrial cover.