Sizing overhead beam
Slackerzinc
Hey guys
I need help sizing a 25' overhead beam for a beam trolly/hoist on the garage.
I want 1000 pound capacity point load. Would a 8x24 beam be sufficient?
I found this beam locally for a great price. Minimal deflection wanted.
Thanks, Andrew
2CWG
SoCal
DISCLAIMER: I'd recommend having a licensed structural engineer review your installation plans and perform the necessary calculations. Overhead lifts are dangerous and individual installation requirements depend on a wide variety of factors that can't be properly evaluated online
If you're looking for some 'napkin math' for rough sizing then the following resources could help:
Ref for beam properties (choose beam type/size for MoI/MoE and such):
http://www.engineeringtoolbox.com/beams-t_58.html
Ref for deflection under load (plug the properties from the first link into the center-load calculator in the following link):
http://www.engineeringtoolbox.com/beam-stress-deflection-d_1312.html
318fekim
Seffner, Florida
It all depends on the actual amount of span between attachment points. Osha deflection allowance for said beam is fairly easy to calculate. You are allowed .00166 for every inch of open span.
BD1
north side
here, check this out, Wallace Gantry info.
http://www.wallacecranes.com/triste1.htm
W8x24 beam is 24 pounds per foot,7.93 depth,.245 web thickness,6.495 flange width, and.400 flange thickness. This is a WIDE FLANGE BEAM
S8x23 beam is 23 pounds per foot, 7.93 depth,.441 web thickness, 4.171
flange width,.425 flange thickness
This is from Ryerson steel book. You could always add a temporary screw jack from slab to bottom of beam if load is questionable.
LutzTD
Lutz, Florida
2nd that, if your worried keep a temporary post handy, Ive seen guys use way undersized beams for the span and them jam in 4X4 posts while using the hoist which was fairly infrequent. If you "need" to roll the hoist the full length then 2 posts you can swap around the load works too.
Charles (in GA)
50 mi south of Atlanta
The issue here may not be the beam itself so much as the support for the beam. The beam will be heavy and then adding the load to it, you are not going to just support this with some simple posts to the floor or rest it on the top of a stud wall. It will need some sturdy steel supports, and possibly some heavier footings in the floor.
If it really is a W8x24 then it will weigh 600 lbs. If the OP is describing the dimensions, and not the correct technical description for the beam, then he is probably describing a S24x121 which has a 8.05 inch wide top and bottom flange and stands 24.5 inches high. This beam weighs 121 lbs per foot, for a total of 3,025 lbs and merely getting the beam in place will be a feat, let alone supporting it.
Charles
Slackerzinc
8" x 24 lbs/ft is the beam. It's 25 feet long. I am supporting it with the same size beam pieces 9 ft long. Base plates, and braced on wall from side movement
BD1
north side
Charles
Looking at the wallace gantry site that I posted, if he had a S24x121 he would be good for about 10 TONS. Yea, he would have a lot of work ahead of him .
Greg-nwo
Ontario
Check out the software tool called Beam Buddy. Let's you run the numbers on different sized beams and spans etc.