scottzilla

Well-known member
Joined
Mar 27, 2009
Messages
200
You can see a bubble forming under my shingles and if you look closely there is a wavy secton of shingles running up the roof.

IMAG1199.jpg


The black streak to the left is what's commonly referred to as roof algae.

The bubble does not seem to get worse when it rains and there doesn't seem to be any water intrusion (I cannot see the bubble from the inside because the spot is behind an attic knee wall).
Here's another pic.
IMAG1198.jpg


Anyone know what causes this? Roof is 12 years old.
 
To avoid these ads, REGISTER NOW!

srmofo

Well-known member
Joined
Oct 15, 2009
Messages
6,161
Location
SW ohio
is the roof vented properly?

is is the shingles popping up like that or is the decking underneath it popping up?
 
To avoid these ads, REGISTER NOW!

Mister Moose

Well-known member
Joined
May 24, 2012
Messages
131
Maybe stating the obvious, but why not get out a ladder and take a look under the bulged shingle?
 

kbs2244

Well-known member
Joined
Nov 11, 2006
Messages
14,065
From here it looks like delaminating plywood.
Most likely due to not enough venting installed when they put in the knee wall.
 

signcrafter

Well-known member
Joined
May 9, 2012
Messages
12,641
Based on what you said, "behind a knee wall so you can't see behind it", I would go with improper venting which led to sheathing delaminating. How is the space behind your knee wall ventalated? Soffit vents, ridge vents, roof vents, gable vents? The best way to vent something like that is soffit vents to allow air into the space behind the knee wall, then use foam baffles stapled to the underside of roof sheathing where(I'm assuming here) that the interior is drywalled up to the "attic" space above the ceiling and then that space vented using ridge vent. If you don't have good venting in the space behind the knee wall and have been having hot weather like most of the country it can cause major problems like this. That space is like an oven with the sun shining on dark shingles all day reaching temps well over a hundred plus. Try and find out how that area is vented. If this is the case and the interior is finished it can be an expensive fix. The easy fix would be to try and cut some vents in the roof or the gable ends. But that probably wouldn't be the right way to fix it depending on a bunch of things.
 

SARG

Well-known member
Joined
Jan 25, 2011
Messages
1,004
Location
Northeast
Replaced several sheets of "buckled" plywood last year & it looked just like your picture.

The sheathing had become wet because of a stove vent that had become loose and vented moisture into the area.
 

Gary S

Well-known member
Joined
Dec 27, 2008
Messages
2,972
Location
Bismarck, ND
Replaced several sheets of "buckled" plywood last year & it looked just like your picture.

The sheathing had become wet because of a stove vent that had become loose and vented moisture into the area.


Quite possible ^..

The first thing I would do is go up there and step on the bulge. Does it feel like just the shingles, or is some part of the roof causing it? I'd almost bet on the roof.

Plywood has a bad habit of doing things like this when the layers decide to delaminate, or when you get some moisture in it. If you have plywood there, it is a good suspece.

I much prefer OSB for roofs and walls because it is usually more stable in the long run.
 