B-vent Clearance from Combustibles

nwav8tor

Well-known member
Joined
Feb 21, 2012
Messages
239
Location
Spokane, WA
The B-vent I'm using for my NG heater garage install requires 1 inch clearance from combustibles. While I knoiw this applies to the hole in the roof (wood sheeting covered with asphalt shingles), does it also apply to the hole in the garage ceiling sheetrock? In other words, is sheetroock considered to be a combustible? I'd like to keep the hole in the sheetrock as small as possible.

Paul
 
To avoid these ads, REGISTER NOW!
OP
N

nwav8tor

Well-known member
Joined
Feb 21, 2012
Messages
239
Location
Spokane, WA
Yeah, I forgot about the paper on the drywall. I already have the trim ring and while it is big enough to cover either size hole, you can be sure it ISN'T one of those fancy $100 ones!!

I cut the "first" hole in the drywall right at the pipe's 4-1/2" diameter so I could wedge the vent in place, plumb it up and mark where it hit the roof so I could position the roof hole in the correct spot. That worked well.

I'm off to enlarge the drywall hole now...

Thanks,
Paul
 

Steevo

Well-known member
Joined
Aug 18, 2009
Messages
8,738
Location
43.49600, -112.04300
If you plan to insulate the attic, you also need to put a box or sleeve around the pipe up to a point just above the insulation. I used a section of 8" tin vent pipe, with b-vent ceiling caps at both ends, one from below the sheetrock, and one on top of the 18" of pipe. You don't want insulation sitting up against the b-vent.

You can just barely make out the sleeve in this pic:
i-ZHD8rw5-L.jpg


And here it is buried in insulation:

i-WXP7bk8-L.jpg
 
Last edited:
OP
N

nwav8tor

Well-known member
Joined
Feb 21, 2012
Messages
239
Location
Spokane, WA
Steevo,

I already have an extra piece of larger single-wall pipe just for that purpose. It'll rest on top of the firestop/support just above the sheetrock and run almost to the roof since my vent is only about 18" out from the side wall/eave. Photos to follow after the install is complete.

Paul
 

jumpingryan

Well-known member
Joined
Jan 17, 2009
Messages
89
Location
Ontario, Canada
On my previous garage, I used a "fire break" to penetrate the drywall. While you have it on the ground, you will see it is square with a round hole with tabs that extend to the drywall. The tabs give you the 1 inch clearance. Go to home depot, and buy ductwork that snaps together to screw or rivet to the tabs....

The ductwork will be square... And make it the height above your le el of expected insulation. You can then fashion a cover if you like to prevent over zealous blown in installers from filling that square hole accidentally.

Cut a square hole in the drywall, and secure your firebreak with insulation protector. Then install your b vent through the hole... Hook up the furnace or heater.. Test, and then put in the blown in insulation.

Easy stuff!

R
 
OP
N

nwav8tor

Well-known member
Joined
Feb 21, 2012
Messages
239
Location
Spokane, WA
Here's my B-vent install in the garage attic. I went with batt insulation in the areas that would've been hard to reach using blown in insulation.

CIMG2285-1.jpg



A close- up of the firestop/support and associated framing

CIMG2287.jpg



The 6" pipe I had was just a bit shy of providing 1" clearance from the insulation (needed 6.5" diameter) so I cut some fiberboard pieces and mounted them to the firestop frame. Now I'll have 2-1/2" clearance...

CIMG2289.jpg



Almost final product attic view. Just need to secure upper corners of insulation blocker pieces.

CIMG2291.jpg



Pipe in garage just waiting for elbow and heater to be mated to it...

CIMG2293.jpg
 
Last edited:

Stee6043

Well-known member
Joined
Jun 7, 2012
Messages
143
Location
West Michigan
If you plan to insulate the attic, you also need to put a box or sleeve around the pipe up to a point just above the insulation. I used a section of 8" tin vent pipe, with b-vent ceiling caps at both ends, one from below the sheetrock, and one on top of the 18" of pipe. You don't want insulation sitting up against the b-vent.

You can just barely make out the sleeve in this pic:
i-ZHD8rw5-L.jpg


And here it is buried in insulation:

i-WXP7bk8-L.jpg

Not to hijack this thread - but why didn't you go straight up through the roof above your ceiling penetration? Looks like you could have a saved a bunch on smoke pipe?? There must be a good reason...I'm curious.
 
To avoid these ads, REGISTER NOW!
OP
N

nwav8tor

Well-known member
Joined
Feb 21, 2012
Messages
239
Location
Spokane, WA
I asked Steevo the same question a while back in a different thread. I believe he wanted the stack to exit the roof closer to the peak due to termination height requirements...

Paul
 

Steevo

Well-known member
Joined
Aug 18, 2009
Messages
8,738
Location
43.49600, -112.04300
I asked Steevo the same question a while back in a different thread. I believe he wanted the stack to exit the roof closer to the peak due to termination height requirements...

Paul

Bingo.
Near the peak, it only has to go above the roof a short ways to be above the peak. I didn't want 24" of pipe sticking out in free air, looking like a fishing cabin.
It is a small price to pay for the nicer appearance.
 
OP
N

nwav8tor

Well-known member
Joined
Feb 21, 2012
Messages
239
Location
Spokane, WA
Isn't that thimble for wall penetrations in horizontal runs, not ceilings and roofs? For my vertical run, I used a combination fire stop and support above the ceiling sheetrock. The sheetrock is only 5/8" thick. I don't think thimbles are made for such small thicknesses...

Paul
 

mrobins297aaa

Well-known member
Joined
Sep 20, 2010
Messages
3,283
Location
south east michigan
Bingo.
Near the peak, it only has to go above the roof a short ways to be above the peak. I didn't want 24" of pipe sticking out in free air, looking like a fishing cabin.
It is a small price to pay for the nicer appearance.

not so, to qualify for a fishing cabin it also needs to be leaning on about a 30 deg angle.........lol
 

csp

Well-known member
Joined
Mar 23, 2010
Messages
5,719
Location
Franktown, CO
No, the thimbles aren't just for wall penetrations. Think about insulation in a ceiling or a garage with an attic space that has a floor.
 
OP
N

nwav8tor

Well-known member
Joined
Feb 21, 2012
Messages
239
Location
Spokane, WA
... Think about insulation in a ceiling or a garage with an attic space that has a floor.

I hadn't thought of that situation, but I'm thinking about it now :eek:

I could see where a thimble would be ideal for such an install...

Paul
 