I've just purchased a new home, taking possession on Sept 21st, and one of my first projects will be running a sub to the attached garage.
The Main panel is in the basement, fed from an underground service entrance.
It's a 200A GE PowerMark Gold, 32 Space - 40 Circuit. with about 14 spaces currently in use (mostly 15 amp lighting & outlets, 2x 20A to kitchen counter outlets and a couple double pole for AC, clothes drier and an unused range plug, since we have a gas range)
It's the panel with the Main Breaker that looks like 2 double pole breakers with a tie bar.
Looks like this guy:
I will install a 15A double pole for the compressor which will live in the basement next to the panel and be plumbed to the garage, and a 80A double pole to feed a subpanel in the garage
So to get to my garage, I have a straight shot about 12' across the (unfinished) basement ceiling, through the rim joist into the garage and straight up about 5' to where I want to locate the sub panel.
Including feeding around to the main disconnect, etc, looking at a maximum 20' run.
I want everything in the garage in conduit. So my understanding is that because I can't run NM in conduit, and I can't run individual conductors exposed, I will need to run conduit from the main panel all the way to the sub, in order to run individual conductors. Correct?
Due to the complexity of curves to get out of the main panel and across the ceiling in the basement, I'm considering flexible conduit from the main panel, then convert to ridgid (EMT or PVC) with a 90 degree fitting where I enter the garage at the rim joist.
I intend to install a 80A breaker in the main panel with four (3x 4AWG / 1x 8AWG ground) individual conductors feeding a main disconnect subpanel.
Since it's an attached garage, I do not need additional ground rods. Just 2 hots to their respective buss bars, Neutral to the neutral buss bar, ground to the ground buss and remove the bonding screw.
Anything important I'm missing here?
Thanks in advance.
The Main panel is in the basement, fed from an underground service entrance.
It's a 200A GE PowerMark Gold, 32 Space - 40 Circuit. with about 14 spaces currently in use (mostly 15 amp lighting & outlets, 2x 20A to kitchen counter outlets and a couple double pole for AC, clothes drier and an unused range plug, since we have a gas range)
It's the panel with the Main Breaker that looks like 2 double pole breakers with a tie bar.
Looks like this guy:
I will install a 15A double pole for the compressor which will live in the basement next to the panel and be plumbed to the garage, and a 80A double pole to feed a subpanel in the garage
So to get to my garage, I have a straight shot about 12' across the (unfinished) basement ceiling, through the rim joist into the garage and straight up about 5' to where I want to locate the sub panel.
Including feeding around to the main disconnect, etc, looking at a maximum 20' run.
I want everything in the garage in conduit. So my understanding is that because I can't run NM in conduit, and I can't run individual conductors exposed, I will need to run conduit from the main panel all the way to the sub, in order to run individual conductors. Correct?
Due to the complexity of curves to get out of the main panel and across the ceiling in the basement, I'm considering flexible conduit from the main panel, then convert to ridgid (EMT or PVC) with a 90 degree fitting where I enter the garage at the rim joist.
I intend to install a 80A breaker in the main panel with four (3x 4AWG / 1x 8AWG ground) individual conductors feeding a main disconnect subpanel.
Since it's an attached garage, I do not need additional ground rods. Just 2 hots to their respective buss bars, Neutral to the neutral buss bar, ground to the ground buss and remove the bonding screw.
Anything important I'm missing here?
Thanks in advance.