20 amp recpts in your garage

Ironhorse

Well-known member
Joined
Sep 17, 2012
Messages
800
What I have found that works best are 20amp NYLON recpts. They have a lot more give and take when it comes to pluging in and out items. The cheaper ones will break or crack. Both Hubble and Levinton make them. Lowes does not carry them but Home Depot does...or you local electrial contractor supply store....
 
Last edited:
To avoid these ads, REGISTER NOW!

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,439
Location
Minneapolis
Are you in the US? Unless there are some local restrictions, the NEC allows 15 amp receptacles on 20 amp circuits, as long as there are more than two of them (and a duplex receptacle counts as two.) If you in fact have devices with 20 amp plugs on them I guess you need them, but the vast majority of appliances use regular 15 amp plugs.

I agree that the nylon receptacles are a lot more durable, but you probably could have saved some money buying the 15 amp ones.
 
OP
I

Ironhorse

Well-known member
Joined
Sep 17, 2012
Messages
800
Are you in the US? Unless there are some local restrictions, the NEC allows 15 amp receptacles on 20 amp circuits, as long as there are more than two of them (and a duplex receptacle counts as two.) If you in fact have devices with 20 amp plugs on them I guess you need them, but the vast majority of appliances use regular 15 amp plugs.

I agree that the nylon receptacles are a lot more durable, but you probably could have saved some money buying the 15 amp ones.

Yea...but they are about 1 or 2 dollars more...and if your like me and plan not to change it in the next 15 years or so...I figure for the little extra money...why not. Your correct even at my shop I have 1 20 unit that needs a 20 plug...the rest are all 15 amp plugs ( or cord caps ) but again nice to have it installed just incase you need it....kinda like an unused elevator shaft at the house great place to hide the bodys and maybe install elevator in 10 or so years...lol
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
There is nothing wrong with a better receptical but I have 100's of common 49 cent home depot ones in service, cant even remember when I replaced one from wear, some like those on my benches are really hi cycle use. Got to be in the thousands.
 

Gary S

Well-known member
Joined
Dec 27, 2008
Messages
2,972
Location
Bismarck, ND
There is nothing wrong with a better receptical but I have 100's of common 49 cent home depot ones in service, cant even remember when I replaced one from wear, some like those on my benches are really hi cycle use. Got to be in the thousands.


LIkewise for me. I buy the "bulk" package from Menards. They go on sale for $3 for a 10 pack. So, eventually, I will have to replace some of these 30 cent receptacles, but it hasn't happened in the last 15 years.
Yes, the high dollar ones might last a little longer, but I doubt it will ever be enough to pay for the expensive ones.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,439
Location
Minneapolis
I've had a couple of the cheap receptacles break. If someone jerks a plug out it can chip or crack the plastic around the socket (yes, I know people aren't supposed to do that but it happens.)
 

Hawk

Well-known member
Joined
Oct 21, 2009
Messages
1,019
Location
Kannapolis, NC
The 20 amp receptacles I used in my shop are Levitons which may be misspelled. The main reason I bought 50 of them was Restore had them at 1.00 each. Thats also why my switches are also 20 amp.
 

dirttracker18

Well-known member
Joined
Aug 10, 2009
Messages
3,191
Location
Slate River, ON
I ran 12/3 wire so that I have 20 amps available throughout my shop with every other receptacle on a different circuit.

I have yet to pop a breaker using anything. I can weld whe someone uses a heavy grinder :)
 

fflintstone

Well-known member
Joined
Jul 18, 2010
Messages
2,722
Location
MOFnowhere Mi.
What you want are loosely called “commercial” outlets, they are nylon and have a full back strap. I found these online somewhere for less than $2 each. Hubbell ones are made in china. So I bought the levitron (sp?)
 

Attachments

  • outlets.jpg
    outlets.jpg
    143.2 KB · Views: 51

fflintstone

Well-known member
Joined
Jul 18, 2010
Messages
2,722
Location
MOFnowhere Mi.
Ok now that we are all on the same page and using commercial outlets in our shop, time for the next question.

Do you mount them ground up for safety?

01out.jpg

By fflintstone at 2012-09-18


Or do you mount them normally so you can use these?

harrietcartercreativeou.jpg

By fflintstone at 2012-09-18

or this?

.
 

Attachments

  • outlet.jpg
    outlet.jpg
    21.8 KB · Views: 33
To avoid these ads, REGISTER NOW!

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
I've always used the cheap 10 packs and haven't had any problems. I would have likely bought the better nylon units if I'd have seen them on the shelf. I ran 12-2 and wrapped the wire on the screws, no back stabbing. I also made sure the wire was folded reasonably so the outlets fit flat in the boxes so they don't move around much if at all. I mounted everything right side up except for one GFCI. That GFCI that's been like that for almost a year and I just now noticed. :lol: Actually, when wiring a dual outlet with a GFCI on one side and a plug on the other, it's may be easier to wire the GFCI upside down because the load contacts are on the "top".

I fail to see how mounting the ground pin up makes things any safer. Don't leave the plug half out of the socket.
 
Last edited:

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
There is no correct way to mount a receptacle, anyone who says up or down is the correct way is WRONG.
 

Dick in Wisconsin

Well-known member
Joined
Mar 3, 2012
Messages
3,048
Location
Shawano, Wisconsin
There is no correct way to mount a receptacle, anyone who says up or down is the correct way is WRONG.

When I lived in NYC in the early 2000's I was riding the subway one day in Manhattan. They guy next me had an electrician's text book. Started taking to him. He was studying to be an electrician and take the NYS or NYC electrician's test. I asked about which side up for outlets. He said, "book and code says ground".

I've installed my ground down so far.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
I used nylon faced 15 amp receptacles for my house. I seem to recall that they were a couple of dollars cheaper than the 20 amp ones, and if you look close, the 15 amp has the innards of a 20 amp installed in it, just the different face plate on the front. Nylon Levitons have a flat face with no indentation around the slots. In the shop I used the exact same receptacle, sans the nylon face, on one side of the shop, the other side, I used a very similar quality Cooper (Eagle) brand receptacles.

Installing receptacles ground pin up, or ground pin down, is largely personal preference and if you have receptacles to be used for fridges with the 90 degree plug, or computer cables or power supply cables that not only lay flat to the wall, but exit the receptacle at a 45 degree angle from vertical, you might want to install them so your cords lay or hang properly.

NEC DOES NOT address the up or down installation of receptacles. In my log house, mine are mounted sideways. Previous owners had installed them willy nilly, whichever way the wind was blowing that day (owner constructed house, whole 'nuther story) so I replaced the cheap 49 cent receptacles that the lamp plugs kept falling out of, with the Leviton Nylon faced, back wired receptacles, and put them all with the ground pin on the left, which just happened to put the neutral on top, but that doesn't really matter, they are all the same now, so I know which way to hold the two prong "polarized" plugs when I plug them in.

Charles
 
Last edited:

GirlnAgarage

Well-known member
Joined
Jan 21, 2011
Messages
4,675
Location
Texas
The brick plugs of the things I need plugged in have the ground down. So that's how I put my outlets.
 

fflintstone

Well-known member
Joined
Jul 18, 2010
Messages
2,722
Location
MOFnowhere Mi.
I fail to see how mounting the ground pin up makes things any safer. Don't leave the plug half out of the socket.

You, me and everyone else with half a brain will always push the plug all the way in.

but I bet we all know “someone” who will yank on a cord 3 or 4 times to make sure they have all the cord available to them despite having 10 feet of slack at their feet. Then that 1/8” x 1 ½” x 8’ strip of steel that is propped up against the wall, gets knocked over by the dog who was startled by all the cord yanking…….

:shocking:
 

Steevo

Well-known member
Joined
Aug 18, 2009
Messages
8,738
Location
43.49600, -112.04300
I used all 20A gray nylon commercial grade captive-screw receptacles in my shop build, and I installed them all right-side-up.
 
Last edited:

Outlawmws

Well-known member
Joined
Aug 9, 2011
Messages
39,565
Location
The Badlands
Yeah, I'm going to put the ground pin UP so this type of plug always has to UP the wall instead of down to the ground where a little thing called gravity wants it to be...


attachment.php


:lol_hitti


You, me and everyone else with half a brain will always push the plug all the way in.

but I bet we all know “someone” who will yank on a cord 3 or 4 times to make sure they have all the cord available to them despite having 10 feet of slack at their feet. Then that 1/8” x 1 ½” x 8’ strip of steel that is propped up against the wall, gets knocked over by the dog who was startled by all the cord yanking…….

:shocking:

As for this "possibility" (Particularly since the bar you speak of is hardly likely to hit the plugs dead level...), What do you think the purpose of a CB and/or a GFIC is for? In the one in ten million to one (or more) odds of that happening,you get a "pop" and the power is off. I'm probably more likely to win the lottery than have that happen. (Maybe I'd better go buy some tickets! :pimpflash )

:evil:
 

Attachments

  • plugs.jpg
    plugs.jpg
    46.4 KB · Views: 72
OP
I

Ironhorse

Well-known member
Joined
Sep 17, 2012
Messages
800
or this?

.[/QUOTE]

If it is a 20 amp do that mean there winking? lol I am now hiding this too many sharpie's around and to much time..lol
 

rodm1

Well-known member
Joined
Feb 17, 2008
Messages
2,275
Installing receptacles ground pin up, or ground pin down, is largely personal preference and if you have receptacles to be used for fridges with the 90 degree plug, or computer cables or power supply cables that not only lay flat to the wall, but exit the receptacle at a 45 degree angle from vertical, you might want to install them so your cords lay or hang properly.

Charles


I agree, This is the only reason it would matter and the way I've decided is the proper way for me.
 

djjsr

Well-known member
Joined
Sep 4, 2006
Messages
4,797
Location
In the cornfields
You could mount them horizontally. Then you would have to decide if the ground goes to the left or right.

404022540.jpg



Or if you just can't decide, there are outlets that swivel.

404022539.jpg


:D
 