So the electrician came to my house today to do some garage wiring. Based on what I have read here, I'm wondering if he did things correctly.
I had him add more outlets in the garage and wire a 50a out for my welder and run wire for my compressor.
The question is on the compressor wiring. It is 48 feet of surface mounted conduit on a block wall. At any rate, he ran 12 awg wire. My compressor is an older quincy 325 from 1957. I have a baldor l1430t The data plate says that it is 20.6 fla. and he put it on a 20 amp breaker. I would have asked him why he left but I had to go to work.
I think that circuit is undersized for what I need. What do the experts think? and if different what should I ask that he change it to?
So the electrician came to my house today to do some garage wiring. Based on what I have read here, I'm wondering if he did things correctly.
I had him add more outlets in the garage and wire a 50a out for my welder and run wire for my compressor.
The question is on the compressor wiring. It is 48 feet of surface mounted conduit on a block wall. At any rate, he ran 12 awg wire. My compressor is an older quincy 325 from 1957. I have a baldor l1430t The data plate says that it is 20.6 fla. and he put it on a 20 amp breaker. I would have asked him why he left but I had to go to work.