First off - I'm somewhat of a rookie when it comes to electrical work and while I've done my homework I don't know all of the general rule-of-thumb guidlines that may seem obvious to some. I know 'just enough to be dangerous' as my grandfather would say!
I need to to a feed-through a box for my compressor ciruicit. I'm running 8-2 NM-B into the box which will have a 30A outlet. The wire then continues on to another box and outlet at the end of the run.
The inspector says I can't double-tap the 30A outlet that I have in the box. He says I'll need to pig-tail to the outlet. I may have to add a second double-duplex box above the outlet to house the splice and then run the pigtail to the actual outlet box due to space restrictions.
In any case I'm having trouble finding a suitable connector to do this 3-way splice w/ 8gauge wire. I can find 2-way splices all day long but nothing for a 3-way. What are my options for completing this splice?
Thanks,
Tanner