'Nuther Sub Panel - 60A this time, CU or AL?

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
After some great advice here, I have decided to run a 60A Sub panel off of my 100A Panel in the Garage... At what point is CU vs AL decision made? I know stupid way of putting the question...Basically when I ran my 100A sub to the garage, I had no heartburn using AL because pricing was VASTLY different...for a 60A sub, looking at #6 CU
I could get some #6 CU THHN or #3 AL

I just had 40' of 2" EMT, plus a box of fittings donated to me, so I'll use that with the THHN.

Length of run is oh...50' at most.
 
To avoid these ads, REGISTER NOW!

skamp

Well-known member
Joined
Jul 20, 2007
Messages
644
Location
Cypress, TX
After some great advice here, I have decided to run a 60A Sub panel off of my 100A Panel in the Garage... At what point is CU vs AL decision made? I know stupid way of putting the question...Basically when I ran my 100A sub to the garage, I had no heartburn using AL because pricing was VASTLY different...for a 60A sub, looking at #6 CU
I could get some #6 CU THHN or #3 AL

I just had 40' of 2" EMT, plus a box of fittings donated to me, so I'll use that with the THHN.

Length of run is oh...50' at most.

I think EMT for an underground run is a mistake. Schedule 80 PVC is cheap and no chance of rust, etc. Also AL for the run is fine. No need to spend the extra money on CU. Just make sure you use the paste on the teminals if using AL.

Steve
 
OP
S

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
I think EMT for an underground run is a mistake. Schedule 80 PVC is cheap and no chance of rust, etc. Also AL for the run is fine. No need to spend the extra money on CU. Just make sure you use the paste on the teminals if using AL.

Steve

No, its all indoors...just come up the wall from my existing 100a sub, across the trusses and down into the rear of the garage.
 

madosta

Well-known member
Joined
Sep 4, 2012
Messages
807
Location
Michigan
Whew, glad the EMT is inside. I would pull 3 #6 CU and a #10 Green CU if it were mine.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Dave, it's just a matter of $$$ whether to use copper or aluminum. Do you really need conduit for this run? 2" is rather large. If the conduit isn't needed, use SER to feed the 60A sub-panel.

#4 Al is good for 60A


*
 
Last edited:
OP
S

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
Dave, it's just a matter of $$$ whether to use copper or aluminum. Do you really need conduit for this run? 2" is rather large. If the conduit isn't needed, use SER to feed the 60A sub-panel.

#4 Al is good for 60A


*

Conduit isnt needed per se, no dangers in the way...it was given to me, so I figured why not use it. I could easily bring it back and say thanks anyways.. I felt 2" was too big too, but the price was right...
So either #4 AL SER or #6 CU...I assume they make a SER in CU?
 