So I'm reading some conflicting info on the Ampacity of 8ga CU wire...

Long story short...I need 5' of wire to wire in a 50A Range Plug....8-3 wire gonna be fine?
 
To avoid these ads, REGISTER NOW!

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,765
Location
Long Island
It depends on what you're doing with said plug. If this is a dedicated circuit for a welder, it will probably be fine. If it is a circuit for a range, that's a no-go.
 
OP
S

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
All of my 50amp welded plugs are 6ga cu. Why not just use #6?

No reason not to use #6...

As for its use. I wired up my existing garage with a 14-50R...made myself a converter to go from 14-50 to 6-50 when I weld (Refused to pay 70 bucks for the Genuine Miller one)... I also can hook my Generator up to it, and my compressor, etc.. (Along the way I've made a few convertor/extension cords) even to the point of being able to hook up my 20a 220v Pressure Washer up to it.
This weekend I'm gonna want to use my compressor IN the garage, so I'm gonna wire up an outlet under my panel...down the road I dont even expect using this outlet, but it will be nice to have just in case.

I could easily use #6, I've got all kinds of #6 CU wire at home.

Why did I go 14-50R in the first place? Because thats whats on the front of a Miller Trailblazer/Bobcat...so I've got plenty of experience with it and its cheap & easy to deal with and sorta industry standard...
 

Jose G

Well-known member
Joined
Aug 1, 2012
Messages
46
Location
Canada, Quebec
8ga will withstand about 40-45A without problem. easy to find wire that size (6ga isnt easy to find)...but its not rated to 50A in any way. if you plan of using a 180A welder... 8ga will be more than enough. but still... not 50A ready.
 
OP
S

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
6ga it is then!
Biggest problem is wiring the 2 gang box...big stiff wire, normal box..working it all in isnt fun. I know I used choice words on my last one....
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,245
Location
Modesto, CA
Dave-

The reason ur getting conflicting specs is because there is different insulation temperature grades of wire. For example, while the conductors in Romex/NM has 90C deg rated insulation, it is limited to a 60C deg ampacity by NEC code. Also, because of 240.4d, anything #1 and smaller(if I remember right- don't have my book in front of me) is sized based on 60C deg rating.

If you are talking about #8 Romex, it is limited to 40a, #6 Romex is 50a. Now, if u were to use #8 THHN wire, it has a higher ampacity(I believe 55a @ 75C deg- again don't have my book in front of me). So if u wanna use #8 wire for 50 amps, use individual THHN wire and u will be fine!
 
OP
S

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
Dave-

The reason ur getting conflicting specs is because there is different insulation temperature grades of wire. For example, while the conductors in Romex/NM has 90C deg rated insulation, it is limited to a 60C deg ampacity by NEC code. Also, because of 240.4d, anything #1 and smaller(if I remember right- don't have my book in front of me) is sized based on 60C deg rating.

If you are talking about #8 Romex, it is limited to 40a, #6 Romex is 50a. Now, if u were to use #8 THHN wire, it has a higher ampacity(I believe 55a @ 75C deg- again don't have my book in front of me). So if u wanna use #8 wire for 50 amps, use individual THHN wire and u will be fine!

Gotcha..so that means I could do #8 THHN, inside a conduit with a ground and voila. IF I go this way, what ground wire should i use..I assume Bare #10 is adequate? Because this is literally straight 18" below the breaker box, conduit is doable easily.

Of course i went thru my scrap pile, and I've got a 3' piece of 6ga Romex...not enough. unless a take a piece off my 30' section...just gotta debate the $$ side of buying some #8 vs using what I got.

Thanks!
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
8ga will withstand about 40-45A without problem. easy to find wire that size (6ga isnt easy to find)...but its not rated to 50A in any way. if you plan of using a 180A welder... 8ga will be more than enough. but still... not 50A ready.
WHAT are you talking about??? You are guessing at all of this.
And #6 is SUPER easy to find everywhere.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
Dave-

The reason ur getting conflicting specs is because there is different insulation temperature grades of wire. For example, while the conductors in Romex/NM has 90C deg rated insulation, it is limited to a 60C deg ampacity by NEC code. Also, because of 240.4d, anything #1 and smaller(if I remember right- don't have my book in front of me) is sized based on 60C deg rating.

If you are talking about #8 Romex, it is limited to 40a, #6 Romex is 50a. Now, if u were to use #8 THHN wire, it has a higher ampacity(I believe 55a @ 75C deg- again don't have my book in front of me). So if u wanna use #8 wire for 50 amps, use individual THHN wire and u will be fine!
THIS is the correct answer.

Bottom line:
#8NM cable = 40A
#8THHN in conduit = 50A
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,245
Location
Modesto, CA
WHAT are you talking about??? You are guessing at all of this.
And #6 is SUPER easy to find everywhere.

I was gonna correct him, but I'm too tired to bicker! And yeah, just saw all different forms of #6 @ Homo depot the other day- #6NM, #6 THHN, #6 bare, etc. etc.!
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Dave-

The reason ur getting conflicting specs is because there is different insulation temperature grades of wire. For example, while the conductors in Romex/NM has 90C deg rated insulation, it is limited to a 60C deg ampacity by NEC code. Also, because of 240.4d, anything #1 and smaller(if I remember right- don't have my book in front of me) is sized based on 60C deg rating.

If you are talking about #8 Romex, it is limited to 40a, #6 Romex is 50a. Now, if u were to use #8 THHN wire, it has a higher ampacity(I believe 55a @ 75C deg- again don't have my book in front of me). So if u wanna use #8 wire for 50 amps, use individual THHN wire and u will be fine!

Wrong NEC section. It's 110.14(c). 240.4(d) is overcurrent protection of small conductors. Also the 60C requirement on conductors #1 and smaller is somewhat meaningless because of the "Unless clause" in 110.14(c)(1) where if the device is marked otherwise. Since most devices are are marked 75C.