I have 3/4 PVC Conduit berried from Subpanel to Poles for Yard Lites/Power.
3 Runs. 175', 155', 65'.
If i go to Lowes, Do i get 12ga THHN Stranded or Unstranded ?
Thank You
 
To avoid these ads, REGISTER NOW!

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
I have 3/4 PVC Conduit berried from Subpanel to Poles for Yard Lites/Power.
3 Runs. 175', 155', 65'.
If i go to Lowes, Do i get 12ga THHN Stranded or Unstranded ?
Thank You

Up to you. Both have the same basic electrical characteristics.

Stranded is more flexible and easier to terminate, especially into backwire devices. 12ga solid is okay to terminate though, not as nice as 14 but not too bad.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,164
Location
Minneapolis
You actually need THWN wire for wet areas, but since it's almost always labeled THHN/THWN these days that's sort of a technicality. Either stranded or solid will work.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,071
Location
Modesto, CA
The one thing no one has asked: are u adding this run onto an existing circuit or connecting it to a new breaker/circuit? If you will be splicing this into an existing circuit, the size of wire to use will depend on the breaker size. Don't use #14 on a 20a breaker!

As far as stranded vs. solid- solid is easier to terminate under screw terminals and stranded is easier to pull, bend, etc.
 

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
The one thing no one has asked: are u adding this run onto an existing circuit or connecting it to a new breaker/circuit? If you will be splicing this into an existing circuit, the size of wire to use will depend on the breaker size. Don't use #14 on a 20a breaker!

As far as stranded vs. solid- solid is easier to terminate under screw terminals and stranded is easier to pull, bend, etc.

We didn't ask because he said he was running #12. Yard lights/power receptacles are limited to 20A circuits, and voltage drop didn't seem like a big issue :)

You're right, with the side wire terminals its better to pigtail the stranded to make a good connection which defeats part of the purpose. But if you are buying backwire outlets that have the pressure plate, it makes a quick, easy and IMO the best possible connection on both wire types.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,071
Location
Modesto, CA
We didn't ask because he said he was running #12. Yard lights/power receptacles are limited to 20A circuits, and voltage drop didn't seem like a big issue :)

You're right, with the side wire terminals its better to pigtail the stranded to make a good connection which defeats part of the purpose. But if you are buying backwire outlets that have the pressure plate, it makes a quick, easy and IMO the best possible connection on both wire types.

Yes, the OP said #12 but YOU mentioned #14!
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,071
Location
Modesto, CA
As I already said- it depends on what you will be plugging into those recep. Just lights? Then I wouldn't worry bout VD because the lights won't pull enough amperage to cause VD.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Ok. Then I should use #10

For those distances #10 is the minimum you'd want to run. As an example #10Cu at 200' with 120V 15A load will have a voltage drop of about 7 volts.

If you are having outlets I assume you plan to use them for something.
 