230 question

uncletater

Well-known member
Joined
Oct 6, 2011
Messages
500
Location
China Grove, NC
I was shopping for a compressor and was talking to the sales person. I was looking at Northern tool at the Puma and the IR.

The Sales person stated that the compressor should be wired within 10 feet of the panel.

Is this true. If so I am screwed because my panel is about 25 feet away from where I want to set the comperssor.

I have yet to wire the 230 yet so my options are open. I am sure my electician will know what to do. I just wanted some opinions before I discuss it with him.

Thoughts?
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
There is no problem with it being 25' from your panel. The 10' is bull. Just use the correct size wire.
 

frankush

Well-known member
Joined
Oct 23, 2011
Messages
1,156
Location
IL
The install manual will tell you if you need to upsize the wire. Go to the manufacturer's website and see if an install manual for the models you are looking at can be downloaded.
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
Depends on the distance and size of the motor. My 3.2HP upright is 50' from the panel as the wire runs, 12-2 is all that is required to feed the 240VAC motor.
 
OP
U

uncletater

Well-known member
Joined
Oct 6, 2011
Messages
500
Location
China Grove, NC
I am looking at a 3hp single stage upright. I have a lot of 12/2 left over from the outlets. I do have 10/3 that I thought could be used for the 230 runs.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
I am looking at a 3hp single stage upright. I have a lot of 12/2 left over from the outlets. I do have 10/3 that I thought could be used for the 230 runs.
What does the size of the wire have to do with the voltage? And WHY do you need 3-wire? Isn't this a 240V motor load only?

Run the appropriate size wire for the circuit size, NOT the voltage.
Run the appropriate configuration (2-wire, 3-wire) according to the voltage (120v, 240v, 120/240v).
 

lessersivad

Well-known member
Joined
Aug 28, 2011
Messages
282
Location
Morenci, MI
What does the size of the wire have to do with the voltage? And WHY do you need 3-wire? Isn't this a 240V motor load only?

Run the appropriate size wire for the circuit size, NOT the voltage.
Run the appropriate configuration (2-wire, 3-wire) according to the voltage (120v, 240v, 120/240v).

Gosh, I guess voltage drop may have something to do with the 1st question.

Along with a possibilty later on that a larger compressor/load MAY come into play.

Also, while 3 wires may not be neccessary, some people actually do run a ground to a 240 volt application.

Just my 2¢.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
Gosh, I guess voltage drop may have something to do with the 1st question.
My point was he said he had 12/2 from some receptacles he wired, and that he had 10/3 for the "230". As if #10 were somehow required for a 230V circuit. I don't get how so many people think larger wire is automatically required for a 240V circuit.
I HIGHLY doubt voltage drop was a consideration in this case.



Along with a possibilty later on that a larger compressor/load MAY come into play.
Maybe, but I doubt it.



Also, while 3 wires may not be neccessary, some people actually do run a ground to a 240 volt application.
I don't get it. A ground is ALWAYS required, regardless of the voltage. I was referring to "3-wire", as in 10/3.
This is another DIY/homeowner wives tale. Automatically thinking 3-wire is needed for a 240V circuit. Maybe because they think only black and red can be used. Who knows?
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
I am looking at a 3hp single stage upright. I have a lot of 12/2 left over from the outlets. I do have 10/3 that I thought could be used for the 230 runs.

So it's like mine, in which case 12-2 will do fine based on the distance you stated in post #1. If you think you'll upgrade later to something like a 5 or 7.5 HP model, no problem using #10. I have 4 240V runs, only one uses #10. That is the 5kW heater, which pulls 20A. The compressor only pulls about 10A running.
 
To avoid these ads, REGISTER NOW!
OP
U

uncletater

Well-known member
Joined
Oct 6, 2011
Messages
500
Location
China Grove, NC
thanks for the answers.

Yes I was thinking of voltage drop may have been an issue.

Yes I thought that you would need to ground 230 (hence the 3 wire)

As you can tell I do not mess with electrical. That is why I asked.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Just a FYI, but when referring to wire such as NM-b (Romex), 12/2 is 2 plus a ground and 12/3 is 3 plus a ground. The ground wire is not included in the count. When talking about cord the ground is included in the conductor count.
 
OP
U

uncletater

Well-known member
Joined
Oct 6, 2011
Messages
500
Location
China Grove, NC
Sorry I didn't phrase that correctly.

I assumed with the 230 I would need two hots(blacks or black and red) one neutral (white) and a ground.

This is why I picked up the three wire
 

Engineer61

Well-known member
Joined
Oct 26, 2012
Messages
225
Location
Colorado
You do need to ground 230, it's the neutral line that you don't need. You only need the neutral line if you want to run something that's 115v off of the compressor switch; fan, hour meter etc. which you would hookup to the hot line that is controlled ny the switch, and the neutral line. The compressor runs between the two hot lines (230v), and 115v is between either of the two hot lines and the neutral line, and the ground line of course is hooked to the compressor's ground.
 
OP
U

uncletater

Well-known member
Joined
Oct 6, 2011
Messages
500
Location
China Grove, NC
You do need to ground 230, it's the neutral line that you don't need. You only need the neutral line if you want to run something that's 115v off of the compressor switch; fan, hour meter etc. which you would hookup to the hot line that is controlled ny the switch, and the neutral line. The compressor runs between the two hot lines (230v), and 115v is between either of the two hot lines and the neutral line, and the ground line of course is hooked to the compressor's ground.

thanks this is good information.
 

lessersivad

Well-known member
Joined
Aug 28, 2011
Messages
282
Location
Morenci, MI
Speedy,

You wrote;
"I don't get it. A ground is ALWAYS required, regardless of the voltage. I was referring to "3-wire", as in 10/3.
This is another DIY/homeowner wives tale. Automatically thinking 3-wire is needed for a 240V circuit. Maybe because they think only black and red can be used. Who knows? "

Yup, you're right, a ground is required and I had a MAJOR brain fart when I wrote previously in regards to the "10/3".

I know what 10/3 is but for some stupid reason I was thinking of only 3 wires, NOT 3 + ground.

So I made a rather BIG mistake with my response concerning the 10/3.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,604
Location
SE MI
Just a FYI, but when referring to wire such as NM-b (Romex), 12/2 is 2 plus a ground and 12/3 is 3 plus a ground. The ground wire is not included in the count. When talking about cord the ground is included in the conductor count.

Absolutely accurate !


HOWEVER, when you are referring to "portable cordage" (the stuff they make "extension cords" out of) 12-2 does NOT have a 3rd (ground) conductor. 12-3 cordage DOES have 3 conductors.

12-3 cordage (SOW, SJOOW, SJT) can be used to make either a 120V or a 240V only extension cord. Most "modern" 240V "appliances" require 4 wires.
 