knobby97
Member
This is my first post on this forum and I have to say that there is definitely info here that has helped me with my latest project, but I wanted to get some opinions on my work/plan thus far to make sure everything is good to go.
Brief history:
Detached shop in SC that is a 100' run from the house's 200A main load center. 110v was already run to the shop when I bought the house via a 20A breaker out of the main panel. I do a lot of jeep and other off road fab, which requires my miller 211 MIG, miller 375 plasma, miller diversion 180 TIG, and a 35 gal 110v air compressor. So the 110v setup wouldn't support all of my gear, so I decided to upgrade the wiring to 220v and install a 6 slot sub panel in the shop.
Layout:
The shop has 3 florescent lights inside, two exterior halogen lights, and 3 duplex outlets currently installed.
Plan:
Install 30A 220v plug for welders, dedicated 20A 110v outlet for air compressor, puts exterior lights on one 20A breaker, and run the 3 current outlets and add another off of another 20A breaker.
I picked up 3 x 114' of 6 AWG THWN (black, red, white) and 114' of 10 AWG THWN for the ground. This is all going in 1" PVC conduit with the misc pull boxes, etc. This will run from a 50A double pole breaker in the main panel.
If I understood everything I read on the forum thus far I would run the red and black hots to the 50A breaker, white to neutral bar, and green to the ground bar (which is bonded) in the main panel. This would feed the homeline sub panel (which is main lug only) which will be non bonded and have the separate ground and neutral bars. As stated above the box will have a 30A double pole breaker which will feed the 220v plug via 6-2 NM-B, and the 3 other 20A breakers will use 12 AWG NM-B.
Questions:
I have the 8' copper grounding rod that I have no installed yet, but was wondering if I needed to use the bare copper conductor to link the rod to the ground bar or can I use more 10 AWG green wire? Also is one rod enough, or no I need to install 2 bars 6' or more apart?
Could I run more than the planned 50A to the sub panel via the 100' of 6 AWG wire?
Does everything check out, or do I need to adjust anything?
I did have a funny discovery when removing the 110v wire and 3/4" conduit earlier today. First, the 12 AWG that was run from the main panel, through the conduit, to the shop was regular household NM-B and the conduit was filled with water and mud. Second, something had crushed the 3/4" conduit in one place. So I was glad that I hadn't tried to run the new wiring through the old conduit, as there is no way it would have made it through the kinked spot nor the dirt and other funk.
Brief history:
Detached shop in SC that is a 100' run from the house's 200A main load center. 110v was already run to the shop when I bought the house via a 20A breaker out of the main panel. I do a lot of jeep and other off road fab, which requires my miller 211 MIG, miller 375 plasma, miller diversion 180 TIG, and a 35 gal 110v air compressor. So the 110v setup wouldn't support all of my gear, so I decided to upgrade the wiring to 220v and install a 6 slot sub panel in the shop.
Layout:
The shop has 3 florescent lights inside, two exterior halogen lights, and 3 duplex outlets currently installed.
Plan:
Install 30A 220v plug for welders, dedicated 20A 110v outlet for air compressor, puts exterior lights on one 20A breaker, and run the 3 current outlets and add another off of another 20A breaker.
I picked up 3 x 114' of 6 AWG THWN (black, red, white) and 114' of 10 AWG THWN for the ground. This is all going in 1" PVC conduit with the misc pull boxes, etc. This will run from a 50A double pole breaker in the main panel.
If I understood everything I read on the forum thus far I would run the red and black hots to the 50A breaker, white to neutral bar, and green to the ground bar (which is bonded) in the main panel. This would feed the homeline sub panel (which is main lug only) which will be non bonded and have the separate ground and neutral bars. As stated above the box will have a 30A double pole breaker which will feed the 220v plug via 6-2 NM-B, and the 3 other 20A breakers will use 12 AWG NM-B.
Questions:
I have the 8' copper grounding rod that I have no installed yet, but was wondering if I needed to use the bare copper conductor to link the rod to the ground bar or can I use more 10 AWG green wire? Also is one rod enough, or no I need to install 2 bars 6' or more apart?
Could I run more than the planned 50A to the sub panel via the 100' of 6 AWG wire?
Does everything check out, or do I need to adjust anything?
I did have a funny discovery when removing the 110v wire and 3/4" conduit earlier today. First, the 12 AWG that was run from the main panel, through the conduit, to the shop was regular household NM-B and the conduit was filled with water and mud. Second, something had crushed the 3/4" conduit in one place. So I was glad that I hadn't tried to run the new wiring through the old conduit, as there is no way it would have made it through the kinked spot nor the dirt and other funk.