3 phase wiring problem

jabberwoki

Well-known member
Joined
May 1, 2009
Messages
6,510
Location
puyallup wa usa
So i bought a Phoenix phase converter of c/l a while back and the magnetic switch had a broken tang on it so i replaced it.
I got it all wired up and hit the switch and i can hear the motor start up but the magnetic contact switch jumps in and out?
Any clues?
 

Attachments

  • Jan09_0001.jpg
    Jan09_0001.jpg
    92.4 KB · Views: 87
To avoid these ads, REGISTER NOW!

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,932
Location
oregon
Are you using the generated leg of the 3p to hold in the relay? I've had problems with contactors in machines that had the generated leg going to the control circuit.

lg
no neat sig line
 
OP
J

jabberwoki

Well-known member
Joined
May 1, 2009
Messages
6,510
Location
puyallup wa usa
I`m am no sparky mate how about i post up a pic of the whole box. Like i said all i`ve done is change the switch and connect up the 3 phase legs to the places the diagram said to.
 

Attachments

  • Jan09_0003.jpg
    Jan09_0003.jpg
    50.7 KB · Views: 63
  • Jan09_0004.jpg
    Jan09_0004.jpg
    44 KB · Views: 56
  • Jan09_0005.jpg
    Jan09_0005.jpg
    48.8 KB · Views: 50
  • Jan09_0006.jpg
    Jan09_0006.jpg
    49.2 KB · Views: 43
  • Jan09_0001.jpg
    Jan09_0001.jpg
    92.4 KB · Views: 40
Last edited:

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,932
Location
oregon
Do you have a schematic of the box you can post up? I looked at the web site and could not find one.

lg
no neat sig line
 
OP
J

jabberwoki

Well-known member
Joined
May 1, 2009
Messages
6,510
Location
puyallup wa usa
No and the company will not give one out all they say is to send it back to them?
I think that's ****** service my self.
The wires from the idler motor are wires in to the connection that the outlets are wired to it`s the bottom left pic the green,white ,red & black with red being the ground to the box.
As far as i know all the feeds to the contractor are from the capacitors then on the other side back to the single phase 480 in feed top row far right.
 
Last edited:
To avoid these ads, REGISTER NOW!

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
23,114
Location
Amarillo,TX and Stinnett,TX
No and the company will not give one out all they say is to send it back to them?
I think that's ****** service my self.
The wires from the idler motor are wires in to the connection that the outlets are wired to it`s the bottom left pic the green,white ,red & black with red being the ground to the box.
As far as i know all the feeds to the contractor are from the capacitors then on the other side back to the single phase 480 in feed top row far right.

Is this being fed from 480V? If so the cap in pic #5 shows 250v limit? I might be reading this wrong?
 

bobadame

Well-known member
Joined
Dec 26, 2007
Messages
1,124
Sounds like too much capacitance. Is the load compatible with the converter?
 
OP
J

jabberwoki

Well-known member
Joined
May 1, 2009
Messages
6,510
Location
puyallup wa usa
Its a 10 hp converter for a 5 hp grinder.
I talked to the tech (finally got through) and he told me to check the voltage at the contact switch.
But i don`t have a volt meter for 480 volts so i`ll harass a mate tomorrow and borrow his.
 
Last edited: