At what point are a contactors contacts worn out? This is from a Square D Nema 3 contactor.
 

Attachments

  • 021.jpg
    021.jpg
    149.5 KB · Views: 55
  • 010.jpg
    010.jpg
    139.1 KB · Views: 41
  • 029.jpg
    029.jpg
    138.9 KB · Views: 37
Last edited:
To avoid these ads, REGISTER NOW!

W-Cummins

Well-known member
Joined
Jan 9, 2006
Messages
1,642
Location
Iowa
At what point are a contactors contacts worn out? This is from a Square D Nema 3 contactor.


Technically when the contactor metal is eroded/worn away, ie. down to the copper substrate.

The other unasked question is,
when should they be replaced??

That of course depends on the application. In a high load ( run at or near the rated capacity of the contactor), high cycle environment ( hundred to thousands of contacts per day), and/or a critical application ( device down causes loss of $$ or even life), and given that you tore it down already you would be remiss if you didn't replace them. Conversely if your running this on your compressor, or your going to use it in your phase convertor, as Aceman said " keep running it" as it will probably out last you!

William.....
 
To avoid these ads, REGISTER NOW!

Super Mech

Well-known member
Joined
Feb 19, 2011
Messages
1,806
Location
Bronx,NY
I had the contacts stick on my 3 phase Ingersoll Rand compressor on Friday. I tried in vain to locate a new magnetic starter with no luck. I called Grainger and they could not interchange the Siemens number. I was in their catalog that they sell the contacts separately. Man those suckers are expensive. I cleaned up the contacts with some emery paper and will try to nurse it along until I can find the exact replacement starter so I don't have to buy a starter/safety together.
 
OP
9

930dreamer

Super Moderator
Staff member
Joined
Oct 7, 2009
Messages
23,094
Location
Amarillo,TX and Stinnett,TX
I'm hoping this will be used to start a 30 hp converter, it will have an easy life with me. $162.90 at Southland electric for contacts.
 
Last edited:

W-Cummins

Well-known member
Joined
Jan 9, 2006
Messages
1,642
Location
Iowa
I'm hoping this will be used to start a 30 hp converter, it will have an easy life with me. $162.90 at Southland electric for contacts.

I figured that you were going to run it on the new convertor. With a few cycles per day it will out last you no problem!

I have a few SQd contactors in use and they aren't too bad. The top of the line stuff is still the A&B NEMA stuff. I don't even look at the contacts anymore when I grab a used one out of my stock pile, it's not worth my time to even look to see if they are good. They are rated at about 1/2 a million to over 1 million cycles depending on load. The only down side to them is the heaters are about $15.00 each and most of them I have were probably setup for 240V, and have the wrong heaters for my use in them.

William....
 