Twist plug wiring

ebamba

Active member
Joined
Jan 29, 2012
Messages
39
I need to replace a standard 220V plug with a NEMA L6-20P on a newly acquired, second-hand, older model, Husky Pro, two stage, 80 gallon air compressor. I'm probably over thinking this, but does it matter which terminal on the plug I attatch the white and black wires to? one terminal is maked "X" and the other "Y". Obviously the ground (Green) wire goes to the the terminal marked G with a green dot painted next to it.

Also, any idea where I can get a copy of the User's Manual?

Thanks in advance,
Ed
 
To avoid these ads, REGISTER NOW!
OP
E

ebamba

Active member
Joined
Jan 29, 2012
Messages
39
Thanks for the quick reply. That's what I thought, but doesn't hurt to ask.
 
OP
E

ebamba

Active member
Joined
Jan 29, 2012
Messages
39
Thanks for the link. It does state that a 30A Minimum Branch Circut is required. Strange because the label on the motor states the voltage of 230 and the amps of 16.5.

Your thoughts?
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
That manual may not pertain exactly to the model you have. If the motor says 16.5A then you can get by with a 20A circuit. Technically 16A it suppose to be the max continuous load on a 20A circuit but I don't think .5A over is anything to worry about.
 
OP
E

ebamba

Active member
Joined
Jan 29, 2012
Messages
39
Saves me from having to call on the Electrician who installed it. Thanks for your help.
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
If you check your voltage you may find you have 240V or more so that would mean the motor will be actually pulling less than 16A.
 

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
Cord ends don't have a very high HP rating, it's usually better to hardwire it.

I was just gonna make a post about this topic...hardwire or plug...and products to use either way. My Puma compressor has a motor rating right around the OP's...want to say it was 16a as well (220v).

I am ready to install whatever I decide to use for a termination for my compressor...Up until now I was gonna use an L6-30R but I dont think they make an angled L6-30P...so rather then have that sticking out of the wall asking to get hit and mangled, I thought about a hardwire solution.

What do is the technical term for the "Junction box" with the big lockable shut off handle?

**Edit...looks like this is the ticket?
http://www.homedepot.com/p/GE-60-Amp-240-Volt-Fusible-Indoor-General-Duty-Safety-Switch-TG3222/202978653
 
Last edited:

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
What do is the technical term for the "Junction box" with the big lockable shut off handle?

**Edit...looks like this is the ticket?
http://www.homedepot.com/p/GE-60-Amp-240-Volt-Fusible-Indoor-General-Duty-Safety-Switch-TG3222/202978653

You want a nonfused disconnect, or safety switch.

If you size your breaker right, you don't need a fused disconnect, it's just more parts to buy and one more thing to go wrong.

Don't forget to buy a ground lug. Most disconnects don't have them unless you specifically ask for a neutral kit.

Also, verify the HP rating of the disconnect meets or exceeds your compressor HP.
 
Last edited:

Steevo

Well-known member
Joined
Aug 18, 2009
Messages
8,738
Location
43.49600, -112.04300
. . .

If you size your breaker right, you don't need a fused disconnect, it's just more parts to buy and one more thing to go wrong. . . .

.

Is it considered OK to use the breaker to turn power to the compressor on and off daily? I thought the disconnect was also meant to avoid using the breaker as an on/off switch?
 

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
You want a nonfused disconnect, or safety switch.

If you size your breaker right, you don't need a fused disconnect, it's just more parts to buy and one more thing to go wrong.

Don't forget to buy a ground lug. Most disconnects don't have them unless you specifically ask for a neutral kit.

Also, verify the HP rating of the disconnect meets or exceeds your compressor HP.

So something like this:
http://www.homedepot.com/p/Square-D-by-Schneider-Electric-QO-60-Amp-Not-Fusible-AC-Disconnect-Switch-Does-Not-Provide-Overcurrent-Protection-QO200TRCP/202353314?N=arcd

I'll probably get it at the electrical supply house for the simple reason of prices are usually the same and service is 600x better...so I'll ask for the neutral/ground lug kit.

The compressor motor is similar to the OP's...Motor tag says something along the lines of 16A and came wired (from Pressure switch to motor) using 12GA. I'd like to wire this disconnect for future use so I got 8ga wire.
 