Number of circuits?

Karl Fields

Well-known member
Joined
May 29, 2012
Messages
75
Starting on the wiring of my 36x48 garage. Lights are all in and now on to 120v receptacles!

Question is I am not sure how many circuits to allocate for this. The walls are on the 48' sides while the 36' ends are almost all doors. I am thinking of running two 20A circuits down one wall and alternating the receptacles between the two circuits. Probably 8 to 10 receptacles on the wall.

Then doing the same with two more 20A circuits on the opposing 48' wall. A couple of receptacles on the end walls tied into one of the above circuits.

Good plan? Flawed plan? Suggestions?
 
To avoid these ads, REGISTER NOW!

porschedude996TT

Well-known member
Joined
Oct 28, 2007
Messages
2,384
Location
Santa Maria, California
I think you have a good plan. It all depends on what you are doing and how many people will be working.

I have two 120 volt receptacle circuits in my 30' x 40'. It has been good for some time but I ran into a problem the other day. My Miller MIG welder is rated at 20amp. So is the receptacle breaker. If I short out the wire coming from the welder gun, it will trip the breaker or if I weld too long it does it as well.

First I thought it was because I have the surround sound and TV on and had the welder plugged into the same circuit. I moved it to the other side of the shop which is a different circuit and it was better.

When I planned the shop I wired in a 240v 30 amp receptacle with a neutral. This way I could make a pig-tail with a 20 amp receptacle and be able to put a better than 20amp load on it. By wiring it for both voltages I am able to eliminate the tripping breaker.

I have 13 duplex receptacles on each of the two 20amp circuits. These are convenience outlets…

I also oversized the wire (#10) to reduce any voltage drop.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
To have alternate outlets down the same wall to be on separate circuits you may want to consider running a multiwire branch circuit using one run of 12/3 vs running 2 runs of 12/2. The two circuits will need to be on 2 single pole breakers with a handle tie or a standard double pole breaker. This should save you a little money on wire.
 

Highbeam

Well-known member
Joined
Feb 15, 2011
Messages
2,292
Location
Mt Rainier foothills, WA
To have alternate outlets down the same wall to be on separate circuits you may want to consider running a multiwire branch circuit using one run of 12/3 vs running 2 runs of 12/2. The two circuits will need to be on 2 single pole breakers with a handle tie or a standard double pole breaker. This should save you a little money on wire.

Doesn't that, MWBC, make GFCI protection difficult? How do you do it?
 
To avoid these ads, REGISTER NOW!

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
That's a good point about the GFCI. Putting a GFCI outlet in the first outlet on a MWBC is problematic. You could use GFI breakers but there goes any savings on the wire. Forget my MWBC suggestion.
 

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
When I was "Sketching" my wiring diagram in my head I thought about doing the alternating thing...between wire costs & speaking with various electricians about it, came to the conclusion its one of those things that sounds great but out in the real world isnt so hot.
Make it easy on yourself, just use more circuits with less outlets...Put bigger stuff like compressors/welders/etc on dedicated outlets and dont lose sleep over it.
 

tylernt

Well-known member
Joined
Jan 24, 2013
Messages
182
Location
Idaho, US
When I planned the shop I wired in a 240v 30 amp receptacle with a neutral. This way I could make a pig-tail with a 20 amp receptacle and be able to put a better than 20amp load on it.
20A receptacle on 30A breaker... even with 10ga wire, is that legal?
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Nope, 20A outlet on a 30A circuit is not to code. porschedude996TT didn't say the circuit was on a 30A breaker, but you'd think it is since he has a 30A outlet on it.

20A receptacle on 30A breaker... even with 10ga wire, is that legal?
 