Umm, I dont know if u've ever worked on or hooked up 3-phase motors but some of the info in the PDF u linked to is wrong. I work on 3-phase motors everyday at work. We have thousands of 3-phase pumps in the field, most with their windings wired in delta configuration for 480v service and the rest wired in wye configuration for 240v service, none of which have a neutral run to them. Hell, half of our pump main service panels are fed by 3-wire service and dont even have a neutral at the meter socket! A 3-phase motor does NOT need a neutral! Just yesterday i worked on a dual voltage motor, and wired the winding leads in wye(aka star) configuration for low voltage 240v operation. But i didnt run a neutral to the motor- just 3 hots and a ground!
I dont need to do any research because i work on this suff everyday! U may want to google the subject yourself! I googled it myself even though i knew the answer and heres one thread for your reading pleasure:
http://www.electriciantalk.com/f2/do-3-phase-motors-require-neutral-3892/
I would note too, that that PDF is from the UK. They MIGHT do things differently there and run a neutral to a 3-phase motor, dont see why they would cause its not needed. But u never know.
The main point is, a properly running 3-phase motor should be pretty close to a balanced load and any imbalance is balanced between the 3 phase legs.
A neutral is used and needed for single phase loads, of which a 3-phase motor is NOT!