Mike Honcho
Well-known member
Is there a maximum distance that the ground rods can be away from a subpanel? And can they be covered in concrete once installed or do they have to be accesible. Thanks in advance.
Chris
Chris
For human safety, the ground should not be more than twenty feet away. For transistor safety, even ten feet is too far.Is there a maximum distance that the ground rods can be away from a subpanel?
I think I'd can them out meaning placing a sleeve around them. You can put a clean out cap in a threaded fitting to cover. Be sure the rods have good earth contact but you could spread out 4 or so inches of gravel around the rod top and out a bit to ensure water doesn't collect in your 'can.'
I just don't like things that are buried and you can't see when a connection is involved.
If conduit is metallic, then a ground wire has increased impedances; becomes non-conductive to surges.... and i "canned" the ground rods and ran a stick of conduit between them so i can run the wire at a later date.
For human safety, the ground should not be more than twenty feet away. For transistor safety, even ten feet is too far.
As others noted, clamps should be available for inspection. Furthermore, concrete in contact with copper wire can break down that copper.
Earthing for human safety need only meet code. Earthing to protect transistors demands many installation rules that exceed code requirements.
BTW, these rules are even more critical on the main panel.
QUOTE]
where did this information come from? is there a white paper or study on it?
Mostly from over 100 years of science and experience. Much can be gleemed from IEEE papers. Earthing for human safety is defined by code. Earthing for transistor safety involved concepts often not even known by electricians. For example, code addresses wire thickness for lower resistance. Earthing for other functions involves shorter length (not thickness) for lower mpedance.where did this information come from? is there a white paper or study on it?
All "modems" (cable, U-Verse, DSL, etc) have an isolation transformer inside.Biggest thing that I gained when I went back and poured over the code was for the phones. I am not real bright so I ask my engineer type,,, why does it take out the modem and not other devices,, he says,, the other phones are 2 wire, the computer is grounded to the electric,, duh.
If this pour isn't done yet there needs to be a uffer from the rods in the foundation. It is something I would absolutely take a picture or 2 of before cement went down in case someone gets a hair up their azz after the fact.
where did this information come from? is there a white paper or study on it?
If conduit is metallic, then a ground wire has increased impedances; becomes non-conductive to surges.
Best earth ground is an Ufer ground. That is wire embedded in concrete. However concrete will 'eat' copper with age. Meaning you probably want copper that is twice as thick (maybe 6 AWG sizes larger).
Being able to inspect the earthing connection is desireable. But also learn about best earth grounds - Ufer grounds. One demonstrated how he did this in: http://scott-inc.com/html/ufer.htm
Another relevant discussion here:
http://lists.contesting.com/archives//html/Towertalk/1999-09/msg00141.html
And here:
http://www.mikeholt.com/mojonewsarchive/GB-HTML/HTML/UferGroundPsi~20030930.htm
so after all this, the garage is considered attached. is it worth while to run a wire to the ground rods, or is it against code since it is attached?
Posted was a relevant concept:Grounding electrodes arent needed for an attached structure because theres already groundig electrodes(or should be) at the main service panel...not against code but not needed and waste of money.
A ballpark guideline says if structures are separated more than 20 feet, then each should be single point grounded where an interconnecting wire enters both structures. An example of earthing that must exceed code requirements.Earthing for human safety need only meet code. Earthing to protect transistors demands many installation rules that exceed code requirements.
Basic electrical knowledge demonstrates a ground wire, sufficient to meet code, can also be insufficient for surge protection.What country are u from? Where do u come up with your statements?
Noticed the reference to "pounding" ground rods. Though soil conditions vary, you can put a 10ft ground rod in the ground without breaking a sweat using a glass of water. No hammer required.
I have very hard clay soil and it would be exhausting to drive one with a hammer, but this way is fast and easy.
I found a cat 307 mini ex to be really handy for for pushing rods through the frost in minot nd years ago when I worked up there!Hammer drill works wonders on a ground rod.
Charles

I welded a spark plug socket to an air chisel and used that on my air hammer to drive the ground rods.