Wiring in the shop. Running 12/3 romex to GFCI receptacles. Two receptacles per box, on separate circuits. Do I run jumper wires off the correct neutral to the correct terminal? or? 


Wiring in the shop. Running 12/3 romex to GFCI receptacles. Two receptacles per box, on separate circuits. Do I run jumper wires off the correct neutral to the correct terminal? or?![]()
Wiring in the shop. Running 12/3 romex to GFCI receptacles. Two receptacles per box, on separate circuits.
Neutral can be shared bwtween the GFCIs on the line side but NOT on the load side. This means you will HAVE to run two 12/2 Romex cables from the GFCIs to each and every outlet downstream!
Planning on GFCI's being the first receptacle on each run.
Looks like i'll be running 12/2 downstream.
Thanks
Have thought about that.GFCI breaker is an option
Yep, thanksmake sure to install a 2 pole breaker if using 12-3 to the first recepts.