Help me design the electrical layout in my garage

scarpozzi

Well-known member
Joined
Apr 25, 2013
Messages
70
Location
Tennessee
30x30 garage....I've got 2, 9x8 garage doors. I've only got 2, 36" man doors...one to go into the house and one to the back yard. I'll be pulling copper from my main 200amp breaker from the house. (which is way underutilized)


I'm going to have 2 garage door openers in the garage, a refrigerator, and a chest freezer. Across from the garage, I'll be feeding a 220v circuit for a minisplit to heat/cool the upstairs of the garage. I mention that because that may eat up some of the available amperage.

I'm thinking about doing outlets on the ceiling for plugin florecent lights and wiring them on a switch...there are no windows in the garage, except some obscure glass on the garage doors.

It's pretty easy for me to compute convenience outlet circuits inside the house...I'm just needing some ideas about what's normal when power tools may be involved.

How many outlets do I need along the garage walls? How many can I put on one circuit, reasonably? I've included a rough drawing...
 

Attachments

  • garagelayout.jpg
    garagelayout.jpg
    30.3 KB · Views: 73
To avoid these ads, REGISTER NOW!

sands35

Well-known member
Joined
May 29, 2012
Messages
936
Location
St. Joseph, MI
What are you going to do in the garage?

Basic car maintenance?
Race car build and support?
Machine Shop?
Storage?
House projects?
Wood working?

What sort of fixed equipment do you have or want to get? (machine tools, big air compressors, big wood working table saws, dust collectors, etc.)

Personally, I'd do a completely different power layout for each one.

The 100 amp panel location does start to suggest that any high amp draw stuff should be on that side - if only to have less expensive runs for the larger copper wires.

There aren't any limits on number of outlets per circuit, but you need to think about how you will use them. If you need 240 outlets or higher amp outlets too.

Example: I have a wall mounted 1.5hp dust collector - so I'm putting in a switched outlet up high on the wall with a double pole switch on it. I planned out where I want my wood working equipment so it will work with the rest of the equipment.

Generically (I do woodworking and have a track car):

I'd put a double duplex 120 every 6' around the perimeter. One circuit per wall. IMHO, there is no need to get complicated with alternate outlets on 2 circuits. No way a one man shop will trip a 20 amp 120 outlet breaker on their own running hand tools.

If you need 240, space them in the area where you think you'll need them.

A 40-50 amp 4 wire 240 around where a work bench and another near the garage doors (if you want to use a portable welder in the drive way for instance).

A 30 amp 120 up high where you think you will want a heater or AC unit (can be re set for 240 three wire easily). (or bigger if you aren't going to do hat gas or LP for a heat source). If you will want a mini-split AC unit, then a 30 amp disconnect on the outside someplace logical.

Then a 30 amp 240 where you want a compressor. 10 awg works for up to a 5hp compressor. I'd run conduit and THHN if you think you want a bigger one.

Car lift? 30 amp box in the ceiling for a whip to hook up the lift.
 
Last edited:

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I'll add to put the outlets high on the wall, at least 49" to bottom of cover plate from floor. You mentioned copper feed from the house. You should consider aluminum for a cost savings if the run is long. I also suggest the garage door openers be on their own circuit. And all outlets in the garage need to be GFCI, even ones on the ceiling.

Edit: I'd also put the frig and freezer on one circuit if the garage is their permanent home.
 
Last edited:
OP
S

scarpozzi

Well-known member
Joined
Apr 25, 2013
Messages
70
Location
Tennessee
This is just going to be a residential garage with some tools and homebrew supplies. My beer making is all done via propane. My chest freezer is a kegerator.... So I'll have that and another beer fridge and some power tools.

I just want to make sure I have outlets where I need them and wasn't sure if most people ran x number of outlets on a standard garage circuit....but your "one man garage" made a good point.

I don't plan on putting in a fixed compressor. My pancake compressor has served me well for the past 10 years and I just never needed more volume than its 6lb tank. I wasn't planning on putting in an AC unit in the garage, but I might change my mind since I'm putting in a mini split upstairs, I might just get a multi-zone unit and run a fan in the garage when I want it.

Thanks for the suggestions.
 
OP
S

scarpozzi

Well-known member
Joined
Apr 25, 2013
Messages
70
Location
Tennessee
I'll add to put the outlets high on the wall, at least 49" to bottom of cover plate from floor. You mentioned copper feed from the house. You should consider aluminum for a cost savings if the run is long. I also suggest the garage door openers be on their own circuit. And all outlets in the garage need to be GFCI, even ones on the ceiling.

Edit: I'd also put the frig and freezer on one circuit if the garage is their permanent home.

This is an attached garage, so the copper run is probably 40-50 ft under the crawlspace (or in the attic) I don't want to run aluminum inside...If it were detached, it wouldn't even be a question.

I'm nervous about picking 1 location for the fridge/freezer to live. It's like trying to decide where to put a sofa....I know my wife is going to try to weigh in on the location after it's set. :D
 

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
Welcome to GJ. You'll get best advice when plenty of information is provided.

Electrical codes vary some by Country and State so your location is important. Some cities also have more restrictive codes for garages.

Now would be good time to Update GJ Profile with Country / State / City.

Good luck planning out your garage. If shop is in cold environment and you plan on hanging heater, don't forget to plan an outlet near the hanging heater.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Why? Today's aluminum is not the same from the 70's. If you are worried about its safety, it is safe. I would dare to say you may have aluminum in your house such as the cable feeding your stove or feeding electric strips in a furnace or heat pump. Depending on your setup the service entrance cable from the meter box to the main breaker panel is most likely aluminum. The copper is great if you want it, but the aluminum will be about a third to a fourth of the cost of copper. I'm not trying to talk you out of using copper, just want you to have the facts.

This is an attached garage, so the copper run is probably 40-50 ft under the crawlspace (or in the attic) I don't want to run aluminum inside...If it were detached, it wouldn't even be a question.

I'm nervous about picking 1 location for the fridge/freezer to live. It's like trying to decide where to put a sofa....I know my wife is going to try to weigh in on the location after it's set. :D
 
Last edited:
OP
S

scarpozzi

Well-known member
Joined
Apr 25, 2013
Messages
70
Location
Tennessee
Welcome to GJ. You'll get best advice when plenty of information is provided.

Electrical codes vary some by Country and State so your location is important. Some cities also have more restrictive codes for garages.

Now would be good time to Update GJ Profile with Country / State / City.

Good luck planning out your garage. If shop is in cold environment and you plan on hanging heater, don't forget to plan an outlet near the hanging heater.

The code here is 2006 IBC...not too strict. I had pex run in my slab for radiant heat, so I may be running plumbing for that in the future....but am trying to decide if it makes more sense to go solar or not. More research to decide what the cost benefit will be and how to size a system. I'm not trying to really heat the space...just break chill. My doors are R-12.75.

We typically get 1-2 months of cold weather and it's typically in 4-5 day bursts of sub freezing temps.
 
To avoid these ads, REGISTER NOW!

sands35

Well-known member
Joined
May 29, 2012
Messages
936
Location
St. Joseph, MI
TN? TVA Hydro power? For heating your garage for a few months, I'd just use a tankless electric unit. Cheap to buy and you get cheep electrical power. You'll need to read up a bit, that is a ~40-50 amp 240 circuit.

Unless you want to go through the challenge of a solar unit.

IMHO, it would be a fun DIY project - if I had the time.

===

Putting the outlets at 49" off the floor at the bottom so they will clear sheet goods is a good idea.
 
Last edited:
OP
S

scarpozzi

Well-known member
Joined
Apr 25, 2013
Messages
70
Location
Tennessee
Electric here is cheaper than some places, but my garage project is adding about 1900 square feet of space onto my house (garage included). I know my bills will rise once I get that heated/cooled.

I planned to go with an electric mini-boiler that would be mounted 5 feet below the panel in a crawlspace. (maybe not directly below it) The solar though was yes....a project.

I was reading up on evacuated tubes and how efficient they are. 25-30 tubes can generate water so hot it will melt pex. If I were to go that route,

I might end up using some kind of heat exchanger to better regulate the temp of the liquid in my radiant heat system. What makes that attractive is how easy I could mount a system like that on my roof and run the piping down to the crawlspace....The South/West facing roof that gets sun all day is on the back-side of a gable...and there's a stairwell right under that part of the roof.

In any case, those are projects for next year. Because of the short run, I can decide to run that circuit next year whenever without tearing up my walls.
 

sands35

Well-known member
Joined
May 29, 2012
Messages
936
Location
St. Joseph, MI
I might end up using some kind of heat exchanger to better regulate the temp of the liquid in my radiant heat system. What makes that attractive is how easy I could mount a system like that on my roof and run the piping down to the crawlspace....The South/West facing roof that gets sun all day is on the back-side of a gable...and there's a stairwell right under that part of the roof.

In any case, those are projects for next year. Because of the short run, I can decide to run that circuit next year whenever without tearing up my walls.
That sounds like a cool idea.

You can run conduit for cheep into the area where you may put in the solar stuff. It will save the cost of putting in wires now. Conduit is pretty cheep at around ~$1-2 a 10' stick.
 

2ManyProjects

Well-known member
Joined
Jul 18, 2013
Messages
757
30x30 garage....I've got 2, 9x8 garage doors. I've only got 2, 36" man doors...one to go into the house and one to the back yard. I'll be pulling copper from my main 200amp breaker from the house. (which is way underutilized)

I'll echo "pattenp"'s comments that aluminum 2-2-2-4 MHF would be more cost-effective than copper for that feeder. It's also good for ~90A (or at least it is in a detached garage scenario; not sure if attached is different, but I doubt it's significantly so), which from the sounds of things would be more than adequate for your purposes.

I'm going to have 2 garage door openers in the garage, a refrigerator, and a chest freezer. Across from the garage, I'll be feeding a 220v circuit for a minisplit to heat/cool the upstairs of the garage. I mention that because that may eat up some of the available amperage.

They will, but nothing outrageous. Of the items you mention, the largest load would undoubtedly be the mini-split system; but even a relatively large one (such as, just to throw a dart, http://www.homedepot.com/p/GREE-Pre...-208-230V-GWH36LB-D3DNA3E/203536863?N=1z11reb) will typically chew up less than 20A when it's running (tho' you'll surely want to put it on a 30A circuit to account for start-up loads & such).

The thing to remember is, the refer, freezer and HVAC system are all effectively "24/7" loads -- i.e., you don't (directly) control when they will be running and/or starting up. So, sooner or later, you WILL encounter the "perfect storm" of several/all of them trying to start up concurrently, Hence, they should be on separate circuits if at all possible (the refer & freezer can probably share a 20A 120V circuit).

I'm thinking about doing outlets on the ceiling for plugin florecent lights and wiring them on a switch...there are no windows in the garage, except some obscure glass on the garage doors.

That's one way to do it, and it's a fairly popular approach. But I really don't see the need for all those plug-in connections, each of which is a potential trouble spot down the road (think contact corrosion, weakening retention springs, etc.); plus there's the "ugly clutter" of all those hanging cord loops. Beyond that, see http://www.garagejournal.com/forum/showpost.php?p=3387494&postcount=5&b=4 for my general thoughts on lighting.

It's pretty easy for me to compute convenience outlet circuits inside the house...I'm just needing some ideas about what's normal when power tools may be involved.

How many outlets do I need along the garage walls? How many can I put on one circuit, reasonably? I've included a rough drawing...

From the bulk of your comments, it doesn't sound like you're planning on getting all that "serious" about power tools & such. It's mostly the big stationary machines (table & miter saws, dust-collection systems, really big air compressors, certain other machine tools, vehicle lifts, etc.) that you really need to specifically plan for. But my impression is, you're not going to have many/any of those. Still, a 30A/240V outlet or two for such things as a portable welder might not be a bad idea.

Anything you can hold in your hand and stow in a portable case when you're done will surely draw less than 15A @ 120V (usually MUCH less). So again, not much of a concern from an overall load point of view. I agree on the double-duplexes (four sockets, total) every several feet approach; every six feet might be slightly closer spacing than really needed, but it certainly won't hurt anything. And the recommendation to keep them at least 49-50 inches off the floor is a good one for several reasons.

However, unlike "sands35", I would put at least two 20A/120V circuits on each wall (tho' given the "mostly one man shop" assumption, you could near-certainly use the SAME two circuits for all three walls. Within each of those two-gang boxes, I'd have each of the duplexes fed from alternate circuits. If you are CERTAIN this will always and forever be ONLY a "one man shop", this is not strictly "necessary"; but there are several good reasons to do it anyway, and the marginal cost is minimal in the overall scheme of things. Also, before leaving this sub-topic: The initial run from the breaker panel to the first pair of duplexes can be done with a single 12/3 NM-B cable; but I would run independent 12/2 for each circuit anyway. Beyond my general distaste for shared Neutrals in 120V circuits, this side-steps the need for common-trip breakers on those circuits, and may well make future troubleshooting and/or expansion simpler & easier. And again, the marginal cost difference is trivial.

Finally, I would probably also run one more 20A 120V circuit to wherever your workbench will be located. That area will become a magnet for all sorts of plug-in gadgets, so best to have some added capacity there. One or two double-gang boxes with two duplexes in each will probably suffice, as you can also use mounted outlet strips for various minor loads like the battery chargers for your hand tools, the stereo, etc.

I don't plan on putting in a fixed compressor. My pancake compressor has served me well for the past 10 years and I just never needed more volume than its 6lb tank.

You might want to re-think this.

I understand that your day-to-day needs are probably rather minimal. But nonetheless, once you pipe the garage for air (which is not difficult or grossly expensive), the convenience & usefulness of pneumatic tools becomes REALLY seductive. Also, a permanently installed compressor can (at least usually) also be a somewhat "remotely located" compressor, however that term might apply in any particular situation (in your case, perhaps in the crawl space, or in a closet under the stairs, or...?). The acoustic isolation this can provide will seem like a Godsend when you don't have the racket of even that pancake unit just over your shoulder. And thus, pneumatic tools become still more attractive.

You certainly don't need a King Kong compressor in order to remotely install it. For that matter, even a wheeled "portable" compressor can be "permanently" mounted by simply parking it in a suitable (ventilated) closet or similar, and running a short length of hose to the inlet for the air distribution lines (which would originate there); and it can still be "portable" if/when needed. That said, doing this with a little (10-year-old, yet) pancake unit is probably pushing your luck. Were I in your shoes, I'd probably target something similar to this:

DeWALT 1.6 HP Workshop Compressor D55168, 200 PSI, 15 Gallon
http://www.homedepot.com/p/DEWALT-1...-Compressor-D55168/100497924#customer_reviews
D55168_1.jpg


up to MAYBE this (which is probably a bit on the overkill side, for you):

Campbell Hausfeld Portable Air Compressor VT6275, 240V, 3.2HP, 60 Gal
http://www.globalindustrial.com/p/p...-tools/vt6275-air-compressor-32hp-240v-60-gal
CBH_VT6275.jpg


The point is, if you think about this now, before construction is complete, you can easily and inexpensively at least make provision for it.

I wasn't planning on putting in an AC unit in the garage, but I might change my mind since I'm putting in a mini split upstairs, I might just get a multi-zone unit and run a fan in the garage when I want it.

Do you have a suitable spot, preferably relatively high on an exterior wall, to through-wall mount a so-called "Window" air conditioner? Maybe you should think about framing in such a spot now, even if you don't plan to use it right away. This would also be the time to install a 240V circuit & outlet for it, while the walls are open and everything is easy to get to. Again, this is one of those things which is easy & relatively cheap to do now, as opposed to later.

This is an attached garage, so the copper run is probably 40-50 ft under the crawlspace (or in the attic) I don't want to run aluminum inside...If it were detached, it wouldn't even be a question.

I won't fault you for preferring copper; but it WILL be more expensive. As long as you're OK with that, go for it. ;)

I'm nervous about picking 1 location for the fridge/freezer to live. It's like trying to decide where to put a sofa....I know my wife is going to try to weigh in on the location after it's set. :D

For obvious reasons, it would be best to nail that down NOW. Explicitly seek your wife's input on this. Maybe even defer to her preference (or at least make it seem that way). Then, if/when she later decides a different spot would be "better", you can legitimately point out that she picked the current location, and that she'll just have to live with it.

[The BBS software is nattering at me that the message is too long. So I'm breaking it here. Continued in next message...]

 
Last edited:

2ManyProjects

Well-known member
Joined
Jul 18, 2013
Messages
757
[...Continued from previous message.]

I had pex run in my slab for radiant heat,

EXCELLENT move! I hope you also put plenty of rigid foam insulation UNDER the slab, and did a proper thermal break at the perimeter.

so I may be running plumbing for that in the future....but am trying to decide if it makes more sense to go solar or not. More research to decide what the cost benefit will be and how to size a system. I'm not trying to really heat the space...just break chill. My doors are R-12.75.

I've been doing some thinking along these lines as well; but I've not as yet had an opportunity to put it into practice (or the time to do as much research as I'd like, for that matter). One approach which seems very attractive for stand-alone floor heating in semi-isolated areas like garages is to use a smallish (and probably electric-powered, for simplicity) tank-type domestic water heater and a separate circulator pump. The water heater will keep a moderate (perhaps 6-20 gallons; more research needed to nail this down precisely) cache of pre-heated water ready to go whenever the circulator pump calls for it. That circulator pump would in turn be controlled by an on-wall thermostat in the heated space. This approach SHOULD help alleviate the rather long warm-up delays caused the high thermal mass of the slab; so you can keep the t-stat set relatively low when the space is unoccupied, yet still make it comfortable without waiting a day and a half (yes, I'm exaggerating) when you do want to use the space. If anyone has first-hand experience with such a setup, I'd love to hear how it worked out.

We typically get 1-2 months of cold weather and it's typically in 4-5 day bursts of sub freezing temps.

As touched on above, part and parcel of water-based radiant heating is the relatively high thermal mass of the slab. While that might be viewed as a curse under some circumstances (particularly if there's lots of intermittent use of the space), it's also a blessing in others. Once you get it warm, it tends to stay warm for a long time with relatively little energy input. This makes it eminently suitable for the application you describe, particularly if you're only (or at least "mostly") just trying to avoid freezing.

Electric here is cheaper than some places, but my garage project is adding about 1900 square feet of space onto my house (garage included). I know my bills will rise once I get that heated/cooled.

I planned to go with an electric mini-boiler that would be mounted 5 feet below the panel in a crawlspace. (maybe not directly below it) The solar though was yes....a project.

Obviously, heating more space costs more than heating less space, regardless of the energy source. But if your local electric rates really are on the "reasonable" side, and can be expected to generally stay that way, then solar will be less attractive by comparison. You not only have to figure on a longer time before you reach the theoretical "break even" point, you also have to consider the additional costs of maintenance & repairs over that time frame. If the break-even point is far enough out, you MIGHT even have to replace the whole system (due to it simply being worn out) before (or too soon after) that break-even point.

I was reading up on evacuated tubes and how efficient they are. 25-30 tubes can generate water so hot it will melt pex. If I were to go that route,

And that is one more reason using solar might not be your best bet. The additional manifolding, plumbing, mixing valves, etc., needed to regulate the water temperature to "safe" levels will all add cost & complication, not to mention dilute overall reliability.

I might end up using some kind of heat exchanger to better regulate the temp of the liquid in my radiant heat system. What makes that attractive is how easy I could mount a system like that on my roof and run the piping down to the crawlspace....The South/West facing roof that gets sun all day is on the back-side of a gable...and there's a stairwell right under that part of the roof.

Your call. And I DO understand the attraction of doing something like this "just because". Just try to consider ALL the factors before making a final decision.

In any case, those are projects for next year. Because of the short run, I can decide to run that circuit next year whenever without tearing up my walls.

Indeed. The important things NOW are those which will become disproportionately more difficult and/or expensive later. Wire is cheap. Paying someone to fish wires through already closed/insulated walls is NOT cheap. Doing that fishing yourself can often be an exercise in masochism.

 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I didn't suggest any type wire other than aluminum. He would not use MHF because it's only an interior run. SER is the best thing to use, be it copper or aluminum.

I'll echo "pattenp"'s comments that aluminum 2-2-2-4 MHF would be more cost-effective than copper for that feeder. It's also good for ~90A (or at least it is in a detached garage scenario; not sure if attached is different, but I doubt it's significantly so), which from the sounds of things would be more than adequate for your purposes.
 

mrjaw14

Well-known member
Joined
May 22, 2012
Messages
1,958
Location
Nashville, TN
My advise is to over-size the wire. #14 shouldn't be there at all. go with #12 and above. Most things in a garage have motors, and motors are hungry when they start up. I have a 120v 33gal craftsman comprssor in my garage that I went ahead and ran #10 for, even though the run was about 15-20'. That way if I ever need to go to 240 for a larger compressor I can just push one more #10 in the conduit and be done.

Also consider hardwiring your lights to save from having a GFCI on them and save the money on plugs.

If you have a radio or TV keep in mind that flourescent lights, motors, etc throw trash on the circuit, so unless you like a fuzzy radio, have more than one circuit available to plug things into just to keep things isolated.

My garage is detached, so I ran AL cable. I got the cable, the box, and all the outlets in my garage for the same price as just the copper wire would have been. I had to increase the awg on the cable, and use a 90A instead of a 100A breaker, and use no-lox on the ends, but other than that the AL was great.
 

2ManyProjects

Well-known member
Joined
Jul 18, 2013
Messages
757
I didn't suggest any type wire other than aluminum. He would not use MHF because it's only an interior run. SER is the best thing to use, be it copper or aluminum.

You are correct. That was my oversight, amid all the other "stuff" I was attempting to cover in that post. Didn't mean to put words in your mouth.

 