Fresh insulation rant

jmarkwolf

Well-known member
Joined
Jan 15, 2013
Messages
1,817
Location
Southeast Michigan
I am nearly complete with my 28ft x 30ft two story garage.

While trying to find the proper insulation for the ceiling of the ground floor (formed by 2x8 attic trusses), which is the floor of the 2nd story. And assuming that rolled and batt insulation must fill the wall and rafter cavity "properly" to achieve the rated R value (no compression nor air gaps), I'm finding the following dichotomy:

5 1/2" thick R21 insulation is too thick for 2x4, but not thick enough for 2x6.

6 1/4" thick R19 insulation is too thick for 2x6, but not thick enough for 2x8.

6 1/2" thick R19 insulation is too thick for 2x6, but not thick enough for 2x8.

8" thick R25 insulation is too thick for 2x8, but not thick enough for 2x10.

All the while, code dictates the R value that must be complied with, with no practical/economical way to get there?

Rather than making insulation that fits the various dimensions properly, ie 2x4, 2x6, 2x8 and 2x10 cavities, they would rather make insulation that fits nothing properly?

WTF Over!

Any insight gratefully recieved.
 
To avoid these ads, REGISTER NOW!

FarmerPete

Well-known member
Joined
Jul 24, 2013
Messages
258
Location
Lansing, MI
I believe the no air gaps refers to the sides of the insulation. Thus those sizes are perfect for the cavities you said they're not thick enough for.
 

James E

Well-known member
Joined
Jun 21, 2010
Messages
16,507
Location
Raleigh, NC
May be a stupid question on my part but what code requires you to insulate the floor between the first and second stories of your house?
 

Scott H in Wheaton

Well-known member
Joined
Mar 18, 2013
Messages
3,155
Location
Plainfield, suburb of Indianapolis
Since you are insulating a garage, not a house, and you want to put insulation between the two floors, does that mean you wish to heat and cool the first floor but not the second floor?

A slight air gap above your insulation is okay, plus you will be sealing it with some type of flooring which will give you an additional R factor.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
You're in left field with your understanding. R13 3.5" is for 2X4 walls, R21 5.5" works in 2X6 walls, any R19/R21 will work with 2X8's, and R25 8" or R30 9.5" works with 2X10's.
 

FarmerPete

Well-known member
Joined
Jul 24, 2013
Messages
258
Location
Lansing, MI
After looking at your numbers again, your main mistake is that you assume a 2x4 is 2" x 4". It's actually 1.5x3.5. A 2x6 is approximately 1.5" x 5.5".
 

k p

Well-known member
Joined
Feb 6, 2013
Messages
217
Location
Ontario, Canada
May be a stupid question on my part but what code requires you to insulate the floor between the first and second stories of your house?

Since you are insulating a garage, not a house, and you want to put insulation between the two floors, does that mean you wish to heat and cool the first floor but not the second floor?

A slight air gap above your insulation is okay, plus you will be sealing it with some type of flooring which will give you an additional R factor.

Likely he wishes to insulate between to stop the migration of hot/cold into the second floor from the opening/closing of the garage doors. Eg. In winter the top floor can be heated and kept warm even while having the garage doors open on the floor below.
 
OP
J

jmarkwolf

Well-known member
Joined
Jan 15, 2013
Messages
1,817
Location
Southeast Michigan
May be a stupid question on my part but what code requires you to insulate the floor between the first and second stories of your house?

No code to my knowledge.

But I'm heating the downstairs and leaving the upstairs unheated, hence the insulation betwixt the two.
 
OP
J

jmarkwolf

Well-known member
Joined
Jan 15, 2013
Messages
1,817
Location
Southeast Michigan
After looking at your numbers again, your main mistake is that you assume a 2x4 is 2" x 4". It's actually 1.5x3.5. A 2x6 is approximately 1.5" x 5.5".

And a 2x8 is actually 1.5" x 7.25". And as I said, 6.25" thick insulation is not thick enough to fill the cavity without 1" air gap, and 8" thick insulation will need to be compressed to fill the cavity, reducing R factor.

I followed the insulation threads on this, and other forums, but still come away less than confident with the best approach. Don't worry I'll muddle through it.

I think for this particular task, I'll use 2 layers of 3.5" x 23", removing the kraft facing from one layer. The resulting 7" will fill the cavity nicely. It just seems silly to have to go to the trouble and expense.

This is definately my "go to" forum when I need to navigate "uncharted" territory!
 
Last edited:
OP
J

jmarkwolf

Well-known member
Joined
Jan 15, 2013
Messages
1,817
Location
Southeast Michigan
Fine, then spray foam the entire cavity.Problem solved

Got it quoted yesterday. $1200 for spray-in cellulose, for just the 1st floor ceiling. And the drywall has to be in place before he can do it. Cha ching.

...or $275 for 1 layer of 6-1/2" fiberglass rolls of R19. Can do the drywall later.

...or $385 for two layers of 3-1/2" fiberglass rolls totalling R26. Nearly 40% improvement over R19. Can do the drywall later.

Answering my own question. Thanks for being the sounding board.
 
Last edited:

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
I had the same issue with the ceiling joists in the upstairs of the 2 story addition of my house. 2x8 just like you....but a vaulted ceiling. We used 2 layers of R19 with the second layer not having the craft facing.
 

signcrafter

Well-known member
Joined
May 9, 2012
Messages
12,361
Got it quoted yesterday. $1200 for spray-in cellulose, for just the 1st floor ceiling. And the drywall has to be in place before he can do it. Cha ching.

...or $275 for 1 layer of 6-1/2" fiberglass rolls of R19. Can do the drywall later.

...or $385 for two layers of 3-1/2" fiberglass rolls totalling R26. Nearly 40% improvement over R19. Can do the drywall later.

Answering my own question. Thanks for being the sounding board.

1200 for spray in cellulose? I didn't read how much you're going to need but based on your price for batt insulation I would say that is pretty high. You can buy the bags of cellulose from home depot and they will let you use the blower for free to do it yourself.

But the poster you quoted was telling you to use spray foam, different then cellulose. Spray foam gets sprayed in the cavity before drywall and will fill the whole cavity. Then scrape flat with the joists before you hang drywall.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,617
Location
Long Island
...or $275 for 1 layer of 6-1/2" fiberglass rolls of R19. Can do the drywall later.

...or $385 for two layers of 3-1/2" fiberglass rolls totalling R26. Nearly 40% improvement over R19. Can do the drywall later.

Huh?!? NO, you cannot add R values like that.
Two layers of R13 is NOT equal to R26. The R value is calculated for a wall system, not just the insulation. Using two batts that add up to the same size as one gets you the same thing as the one thicker batt. The additional compression increases the density, which increases the R value, but probably not more than R20. Not worth the effort over the single R19 batt that belongs in the space.
 

signcrafter

Well-known member
Joined
May 9, 2012
Messages
12,361
Huh?!? NO, you cannot add R values like that.
Two layers of R13 is NOT equal to R26. The R value is calculated for a wall system, not just the insulation. Using two batts that add up to the same size as one gets you the same thing as the one thicker batt. The additional compression increases the density, which increases the R value, but probably not more than R20. Not worth the effort over the single R19 batt that belongs in the space.

What do you mean by "compression"? If you compress insulation you actually decrease the R value. That is why you don't stuff R19 made for 2x6s in a 2x4 cavity.
 
To avoid these ads, REGISTER NOW!

gpflepsen

Well-known member
Joined
Sep 5, 2013
Messages
105
Location
NE
It's amazing how the extra space acts like a ventilation duct when insulating vaulted rafters with material that is 1" too thin...
 
OP
J

jmarkwolf

Well-known member
Joined
Jan 15, 2013
Messages
1,817
Location
Southeast Michigan
Huh?!? NO, you cannot add R values like that.
Two layers of R13 is NOT equal to R26. The R value is calculated for a wall system, not just the insulation. Using two batts that add up to the same size as one gets you the same thing as the one thicker batt. The additional compression increases the density, which increases the R value, but probably not more than R20. Not worth the effort over the single R19 batt that belongs in the space.

If that's true, then I would agree, but two 3-1/2" thicknesses will fill my 7" cavity pretty nicely without any compression nor gaps.

As for totalling up thicknesses to increase R value, it was merely intuitive, but I will defer to those more knowledgable.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,617
Location
Long Island
What do you mean by "compression"? If you compress insulation you actually decrease the R value. That is why you don't stuff R19 made for 2x6s in a 2x4 cavity.

Correct, and incorrect. Compressing fiberglass from it's factory loft decreases the overall R value, but INCREASES the R per inch.
So an R19 batt stuffed into a 2x4 cavity will not yield R19 any more, but will yield more than the R13 batt that correctly fits the space. Probably somewhere between R14 and R15.

The point is that fiberglass insulation is fluffed as much as practicable at the factory to make it the least expensive to install. Fluff it any more and you get too much airflow between the fibers and the R value drops dramatically. Compress it, and you need to use a lot more fiberglass to get the job done, so it gets prohibitively expensive (and then there would be more effort to get the sheetrock flat).

So is isn't worth getting thicker batts and compressing them to insulate better. If you wanted more R per inch, you should just switch to something other than fiberglass.
 
Last edited:

RedBKM

Well-known member
Joined
Dec 2, 2012
Messages
236
Location
Central Virginia
I would look into rock wool aka stone wool, mineral wool etc. It has multiple advantages over fiberglass.

Lowes carries a brand called Roxul and it is so much easier to install. Try it and you will wonder why anybody would buy fiberglass for anything.
 

#1SomeGuy

Banned
Joined
Dec 4, 2012
Messages
511
Location
Canada
I would look into rock wool aka stone wool, mineral wool etc. It has multiple advantages over fiberglass.

Lowes carries a brand called Roxul and it is so much easier to install. Try it and you will wonder why anybody would buy fiberglass for anything.
+10000000000

Did my basement with Roxul...it's R14 for 2x4 framing (more than pink fiberglass), doesn't cost much more, is quite fire resistant, easier to handle and doesn't itch, doesn't hold water (so getting it wet doesn't destroy it's R value), doesn't mold either. Better product in every single way.
 

FarmerPete

Well-known member
Joined
Jul 24, 2013
Messages
258
Location
Lansing, MI
I just bought some to insulate a spot in my attached garage wall. I like that it's higher R value and fire resistant. The Lowes I went to had a guy with a demo table. He had a torch setup to show that it wont catch fire. Very neat stuff. Significantly more expensive than fiberglass though.
 

#1SomeGuy

Banned
Joined
Dec 4, 2012
Messages
511
Location
Canada
It's about double here as well (same package cost but twice the square footage in a package), but for R12 (pink) vs R14 (roxul) it kind of skews things a smidge. The doesn't cost much more is when you compare pink to roxul to spray foam. If pink cost $1, roxul would cost $2 and spray foam would cost $8. I got a quote of $2500 to spray foam my basement (Installed), but it only cost me about $500-600 for roxul + vapor barrier (DIY)
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
Whatever you do, don't peel the paper off insulation. Buy unfaced batts and lay them on top of the installed insulation if you are installing craft face down. Around here we don't use faced insulation in floors. Just hold it in place with wire until the ceiling is installed. Or if the ceiling is coming in soon, just leave it in compression between the joists. In the case of no ceiling, we just depend on the wire.
 

RedBKM

Well-known member
Joined
Dec 2, 2012
Messages
236
Location
Central Virginia
I just bought some to insulate a spot in my attached garage wall. I like that it's higher R value and fire resistant. The Lowes I went to had a guy with a demo table. He had a torch setup to show that it wont catch fire. Very neat stuff. Significantly more expensive than fiberglass though.

I had some drops left over that I tossed on a campfire just for fun. Nothing happened and it eventually smothered the fire.

Lowe's has a special knife now for cutting the stuff. It looks like something you would see advertised on TV at 3AM but it works great.
 

Jim_No_Garage

Well-known member
Joined
Jan 15, 2011
Messages
3,316
Location
Millington NJ
There is a cheap Farberware steak knife tucked into the walls of my family room. I was using it to cut Roxul and never saw it again. :dunno:

Roxul is VERY DUSTY compared the the new Itch Free FG batts.

I have 2x6 ceiling joists so I ran faced R21 in the bays and unfaced R30 cross-wise.

I need to roll out a layer of r30 across the rest of the attic - should have done it 15 years ago. I HATE blown in cellulose - we had some walls done and the air leaks in unrenovated spaces bring leak cellulose into the bedroom. Dusty . . .

Jim .
 
OP
J

jmarkwolf

Well-known member
Joined
Jan 15, 2013
Messages
1,817
Location
Southeast Michigan
Worst thread ever. Talk about wasted brain power.

Then don't follow it. Move on.

I was able to correct some misconceptions I had on a subject that I had no previous experience in, while building my new garage, by "conferring" with the kind folks on this forum.

Thank you to those helpful posters.
 