is there any code as to how many outlets you can have downstream off the load terminals of gfci?
You can put a pigtail to feed the GFCI outlet.Then continue your outlets with out GFCI protection if you wish.Hope this helps!
If you are buying 20 amp receptacles (non-GFCI) thinking they are better, think again. The internals of a Leviton 15 amp Pro Grade and a 20 amp Pro Grade of the same type/part number series, is identical. The only difference being the face plate attached to the receptacle during manufacture, and the price in the store.
Charles
If you are buying 20 amp receptacles (non-GFCI) thinking they are better, think again. The internals of a Leviton 15 amp Pro Grade and a 20 amp Pro Grade of the same type/part number series, is identical. The only difference being the face plate attached to the receptacle during manufacture, and the price in the store.
Charles

I have a fairly new 15 amp GFCI in a kitchen counter outlet. The load side has 3 additional 15 amp outlets. These are located within about 15 feet of run, in the next room.
The GFCI outlet and the next outlet in the run work fine. But whenever any item is plugged into outlet 2 or outlet 3, the GFCI immediately trips.
Using a standard GFCI tester, GFCI outlet and the next outlet in the run test out correctly. And when the fault button is pressed, the GFCI outlet and the next outlet in the run trip the GFCI - as they should.
Outlets 2 and 3 in the run - the ones that immediately trip the GFCI whenever any load is plugged in - also indicate that they're correctly wired. However, when the fault button is pressed on the GFCI tester when its plugged into either outlet 2 or outlet 3, the GFCI will not trip
So I'm a bit stumped. How can the tester indicate correct wiring while the fault button won't trip the GFCI on either of these two outlets, but anything else plugged into either outlet immediately trips the GFCI ?
Do outlets 2 and 3 work when the GFCI is tripped? If you haven't checked, do so, it may be that they are wired to the line side rather than the load side of the GFCI and are not protected by it.
If you didn't wire it, there is no telling what some flunky electricians helper did.
Charles
If you are buying 20 amp receptacles (non-GFCI) thinking they are better, think again. The internals of a Leviton 15 amp Pro Grade and a 20 amp Pro Grade of the same type/part number series, is identical. The only difference being the face plate attached to the receptacle during manufacture, and the price in the store.
Charles

I bet youre getting sick of repeating this over and over again just like I'm getting tired of explaining the difference between a GROUND rod and a GROUND wire(EGC) and why u cant connect an outlet EGC to a ground rod and say the outlet is properly grounded....uggg![]()